[?]: S7-200 ethernet communication to Wonderware

Post by reymond_craig »

Hi,

Good day, is there a way to communicate s7-200 to intouch using ethernet? If yes what other software do i need like (PC Access ? ) or no need just the cp. And if yes also does this soppurt cross connection of cable without using ethernet switch.

Thank you very much in advance.

Warm regards,
REy
bunglehead
Posts: 109
Joined: Thu Oct 19, 2006 7:00 am
Location: Russia

Post by bunglehead »

All you need is a OPC server (PC Access used for that).
You need a CP for S7-200 of course. Crossed cable will work of course.
Umencho
Posts: 508
Joined: Mon Jul 16, 2007 12:28 pm
Location: Europe

Post by Umencho »

Hello Ray,
Another decision is to use "good old" DASSIDIRECT Server (of course if you have CP). Maybe your favorite.
Look at http://61.37.246.137/TECH/html/t002006.htm or
http://fa.sammicomputer.co.kr/TECH/html/t002006.htm :wink:
Hope this will helps. :P
regards