[?]: WinCC Flex 2007 RT And S7200 communication problem

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
amit
Posts: 53
Joined: Thu Apr 23, 2009 2:12 pm
Location: India

Post by amit »

Hi,
I'm facing problem for communication between WinCC Flexible RT 2007 ( i'm using PC as HMI) and S7200. ( i'm using CPU 224 DC/DC/DC).
I have gone through various tips in this forum as well all searched treads.
But no success.

My settings in brief are as under,
1. In connections selected Interface- MPI/DP
Profile - PPI
Add - 1
Baud - 9600
PLC Add-2
2. In PLC system block - Add 2 , Baud 9600

Further i have checked with RS 232 PC-PPI cable as with USb PC-PPI cable but there is no communication. I can communicate to PLC with MW4.0.

Pl help me.

Thanks in advance.
Amit
emulefan
Posts: 27
Joined: Sat Feb 10, 2007 3:19 pm
Location: Argentina

Post by emulefan »

You need to set the PG/PC Interface to PPI advanced mode, it works for me.

Regards
amit
Posts: 53
Joined: Thu Apr 23, 2009 2:12 pm
Location: India

Post by amit »

Test with PC-PPI in advance mode and also with USb PC-PPI cable also. But still no communication.
Further somebody was telling about peripheral selection ( select S7200) while installing the Wincc Flexible. But while installing i was not prompted this option. Any Idea...
emulefan
Posts: 27
Joined: Sat Feb 10, 2007 3:19 pm
Location: Argentina

Post by emulefan »

Check this link. But in my case works only with "PPI advanced" mode activated.
http://support.automation.siemens.com/W ... n/28263099

http://support.automation.siemens.com/W ... d=&lang=en

Regards
amit
Posts: 53
Joined: Thu Apr 23, 2009 2:12 pm
Location: India

Post by amit »

Dear emulefan,
Tahnk you for the help. I hv already gone through these links but still there is no communication. Any further advice...

Amit
kvaziexpert
Posts: 1
Joined: Thu Jan 08, 2009 1:47 pm
Location: Bosnia and Herzegovina

Post by kvaziexpert »

What about OPC connection and PCAccess?
emulefan
Posts: 27
Joined: Sat Feb 10, 2007 3:19 pm
Location: Argentina

Post by emulefan »

May be you have a configuration issues in the PLC communication port, and you need to reset the PLC to the factory default (9600 bps, Address=2, etc.) and try again.
If you want to do this, use the Wipeout.exe application that comes into the Microwin CD (you need a RS232-PPI cable).
But remember, this action will erase all the contents in the PLC, including any program you have into the PLC.

Regards
amit
Posts: 53
Joined: Thu Apr 23, 2009 2:12 pm
Location: India

Post by amit »

Thank you all of you for your support. I hv finally solved the problem. As described above all settings were same in PLC and wincc flexi but i was setting PG-PC interface from Microwin so acess point was remaining microwin intade S7online. After setting PG-Pc interface to S7online-PC-PPi cable i 'm able to communicate between S7200 and Winc_flexible.

Once again my thanks to all of you.

Amit