[?]: communication between two XBTGT and M340 PLC

другие контроллеры
pawas
Posts: 2
Joined: Sat Feb 28, 2009 3:11 pm
Location: India

[?]: communication between two XBTGT and M340 PLC

Post by pawas »

hi,
can anybdy help me out to communicate two XBTGT HMI to communicate with MODICON M340 series PLC using the modbus RTU protocol.
i can able to communicate both the hmi individualy but can't able to stablish the communication between both hmi togather.
Kuzyma
Posts: 31
Joined: Tue May 12, 2009 8:32 am

Post by Kuzyma »

Hi, pawas
It's not possible to communicate two XBTGT with M340 using Modbus RTU.
In your case XBTGT acts Mater role, but in Modbus RTU network could be only ONE master. So, if you want to use two XBTGT panels with one M340 controller you should use Ethernet network (Modbus TCP protocol).
In this case your panels will be clients and your controller will be server.
pawas
Posts: 2
Joined: Sat Feb 28, 2009 3:11 pm
Location: India

Post by pawas »

thnx

but in the manual it is clearly mentioned that 32 xbtgt can be configured in one modbus RTU network where XBTGT will be act as a slave.

but with XBTGT as a slave and M340 as a master is not getting communicate.