can anybdy help me out to communicate two XBTGT HMI to communicate with MODICON M340 series PLC using the modbus RTU protocol.
i can able to communicate both the hmi individualy but can't able to stablish the communication between both hmi togather.
[?]: communication between two XBTGT and M340 PLC
-
- Posts: 2
- Joined: Sat Feb 28, 2009 3:11 pm
- Location: India
-
- Posts: 31
- Joined: Tue May 12, 2009 8:32 am
Hi, pawas
It's not possible to communicate two XBTGT with M340 using Modbus RTU.
In your case XBTGT acts Mater role, but in Modbus RTU network could be only ONE master. So, if you want to use two XBTGT panels with one M340 controller you should use Ethernet network (Modbus TCP protocol).
In this case your panels will be clients and your controller will be server.
It's not possible to communicate two XBTGT with M340 using Modbus RTU.
In your case XBTGT acts Mater role, but in Modbus RTU network could be only ONE master. So, if you want to use two XBTGT panels with one M340 controller you should use Ethernet network (Modbus TCP protocol).
In this case your panels will be clients and your controller will be server.