Just got a question from a friend, but have no experience with Beckhoff equipment at all.
There is two exactly identical machines, controlled by BC9000 PLC with a few I/O modules (both analog and discrete).
After a nearby lightning hit, Ethernet port on one of BC9000 went bad.
Everything is working fine locally, but unable to monitor it remotely anymore and unable to change settings
(there is some custom VB program that used to monitor operation and change process settings, not full-featured SCADA system).
Company who developed this project does not exist anymore, no way to get any support from authors. No any project source files available.
Now the main question - is it possible to purchase new BC9000 "head" and clone full contents of failed one to a new one, or use second machine with operational BC9000 and exactly the same project loaded as a "donor" to load a new BC9000 unit?
Both machines still in use, and swap must be done in a single weekend, once started.
No extreme hurry, but it would be good to know ASAP if there is no way to simply clone loaded code and there is need to re-create everything from scratch.
PS: Alternate way is on-site component level repair of failed BC9000, keeping programming intact, but with the same "one weekend" rule.
This looks not so realistic to me.
Does anyone looked inside BC9000 or have schematics/service manual for this beastie?
[?]: Beckhoff BC9000 cloning
-
- Posts: 38
- Joined: Fri May 02, 2008 4:41 am
- Location: Mexico
BC9000 its not a PLC it is a distributed IO, you just need to configure the "box". The real PLC program runs in your PC. you should make a back up of the file or an image of the entire HDD;
Here is an example:
http://www.infoplc.net/Descargas/Descar ... ystem.html
it tells you to open the system manager, thats on the twincat icon that is on rigth botom corner of the desktop computer near the clock
regards
Here is an example:
http://www.infoplc.net/Descargas/Descar ... ystem.html
it tells you to open the system manager, thats on the twincat icon that is on rigth botom corner of the desktop computer near the clock
regards
-