[?]: analog input signal about 5A and 100V for PLC S7-200

Post by hoangnguyen1986 »

The analog inputs of PLC S7-200 can read a signal with a range from 4-20mA or -10-+10V.
But my problem here is that i use a current transformer and a voltage transformer that mean i have an input signal about 5A and 100V.
So how can i solve this problem.
Please tell me something that you know about this one.
Thanks so much!
auto_mitch
Posts: 17
Joined: Thu Jan 08, 2009 11:28 am
Location: Europe

Post by auto_mitch »

You must use signal converter to change the 5A and 100V to 4-20mA. Dont use these signals direct to plc's analog inputs.
e.g.
http://www.hsb-electronics.de/BIMe.pdf
hoangnguyen1986
Posts: 33
Joined: Thu Mar 27, 2008 2:18 am
Location: Vietnam

Post by hoangnguyen1986 »

thanks so much.I'll try to use this one for my application!
Thanks again1
Sundar
Posts: 2
Joined: Wed Aug 19, 2009 3:14 pm
Location: India

Post by Sundar »

you can also try Pilz - S1WP signal converter
link : www.pilz.com