[?]: rsview modbus problem

Post by eng_ehab »

hi all

i have a flow computer model solarton 7951 , and i wanna to design a scada system so i used matrikon and rsview

but

when i make a connection between matrikon and the flow computer i can read all tags , but while i connect rsview with matrikon the values were unreadable and the connecton between matrikon and flow computer down and fail !!

so what's your advice !?>

thanx and sorry about poor English
winwinwin
Posts: 3
Joined: Wed Oct 14, 2009 2:15 pm
Location: Thailand

Post by winwinwin »

Flowcom communication with modbus 485 right?

if right, on software you must used Kepware server OPC to connect between RSView32 and flowcomp. (RSView32 configuration to connect with OPC server)

on hard wire , neccessories to used RS232 /RS485 converter to connect between computer and flowcomp


enjoy!