Hi,
Does anybody have a table with the addresses of the major special marks bits of S7 PLC - CPU 312?
I am looking for the bit that goes to "1" in the 1st cycle, after the order to run the program.
I tried setting SM0.1, has for the S7-200 series, but without result.
Regards,
Bruno
[?+]: "Problem" with s5/s7 software
-
- Posts: 17
- Joined: Sat Aug 23, 2008 11:43 pm
- Location: Europe
-
- Site Admin
- Posts: 1387
- Joined: Sat Aug 13, 2005 6:15 am
Re: "Problem" with s5/s7 software
no
you can made it
into OB100 make :
into OB 1,last network :
you can made it
into OB100 make :
Code: Select all
SET
S M0.0 //bit of first scan
Code: Select all
SET
R M0.0
-
- Posts: 17
- Joined: Sat Aug 23, 2008 11:43 pm
- Location: Europe
Re: "Problem" with s5/s7 software
Thank You.
Problem solved.
Regards,
Bruno
Problem solved.
Regards,
Bruno