Dear All,
Anyone have experience with connecting Micromaster 440 using PC Adapter via RS485 port?
is it possible?
Regards,
Ciwa
[?]: Connecting MM440 using PC Adapter via RS485 port?
-
- Posts: 146
- Joined: Fri Aug 25, 2006 3:50 pm
- Location: Indonesia
-
- Posts: 96
- Joined: Fri Nov 16, 2007 3:18 pm
- Location: Europe
Re: [?]: Connecting MM440 using PC Adapter via RS485 port?
If you want to connect inverter to PC it's easy. Micromasters have RS485 interface as I remember correctly there are two blue connectors 29(Data+) and 30(Data-), just attach your adapter to these connectors and use DriveMonitor.
Last edited by kriztof on Fri Nov 20, 2009 6:14 pm, edited 1 time in total.
-
- Posts: 146
- Joined: Fri Aug 25, 2006 3:50 pm
- Location: Indonesia
Re: [?]: Connecting MM440 using PC Adapter via RS485 port?
hi kriztof,
i tried but no luck. are there parameter should be set??
regards,
Ciwa
i tried but no luck. are there parameter should be set??
regards,
Ciwa
-
- Posts: 96
- Joined: Fri Nov 16, 2007 3:18 pm
- Location: Europe
Re: [?]: Connecting MM440 using PC Adapter via RS485 port?
Yes, you have to configure USS protocol parameters, use parameter range: P2009 – r2037i tried but no luck. are there parameter should be set??
Operating instruction:
http://support.automation.siemens.com/W ... ype=133300
Parameter list:
http://support.automation.siemens.com/W ... reeLang=en
-
- Posts: 146
- Joined: Fri Aug 25, 2006 3:50 pm
- Location: Indonesia
Re: [?]: Connecting MM440 using PC Adapter via RS485 port?
hi kriztof,
the parameter already set, but still no luck. I use Starter and set the PG/PC interface as PC Adapter(PPI) is this correct?
The cable schema
PC Adapter --------- MM440
DB9 ----------------- Terminal No.
7 ---------------- 9 ---- +24VDC
2 ---------------- 28 ---- 0V
8 ---------------- 29 ---- Data A
3 ---------------- 30 ---- Data B
When I try to connect the MPI & USB light are blinking but no device found.
Regards,
Ciwa
the parameter already set, but still no luck. I use Starter and set the PG/PC interface as PC Adapter(PPI) is this correct?
The cable schema
PC Adapter --------- MM440
DB9 ----------------- Terminal No.
7 ---------------- 9 ---- +24VDC
2 ---------------- 28 ---- 0V
8 ---------------- 29 ---- Data A
3 ---------------- 30 ---- Data B
When I try to connect the MPI & USB light are blinking but no device found.

Regards,
Ciwa
-
- Posts: 96
- Joined: Fri Nov 16, 2007 3:18 pm
- Location: Europe
Re: [?]: Connecting MM440 using PC Adapter via RS485 port?
I thought it's only for S7 200 connection? Do you mean Simatic PC Adapter for S7? Sorry I didn't understand you correctly.I use Starter and set the PG/PC interface as PC Adapter(PPI)
I use RS232-RS485 converter and DriveMonitor, it works with Micromaster, Simovert, Simoreg.
-
- Posts: 1
- Joined: Wed May 03, 2017 4:06 pm
Re: [?]: Connecting MM440 using PC Adapter via RS485 port?
Hi guy,ciwa wrote:hi kriztof,
the parameter already set, but still no luck. I use Starter and set the PG/PC interface as PC Adapter(PPI) is this correct?
The cable schema
PC Adapter --------- MM440
DB9 ----------------- Terminal No.
7 ---------------- 9 ---- +24VDC
2 ---------------- 28 ---- 0V
8 ---------------- 29 ---- Data A
3 ---------------- 30 ---- Data B
When I try to connect the MPI & USB light are blinking but no device found.![]()
Regards,
Ciwa
I did test successfully by connecting STARTER (PC) to Micromaster MM440 via terminal 29, 30 (RS485 port) using USB-RS232-PPI/RS485 cable, but the wiring should be follow:
PC Adapter --------- MM440
DB9 ----------------- Terminal No.
7 ---------------- 9 ---- +24VDC
2 ---------------- 28 ---- 0V
3 ---------------- 29 ---- TRX+
8 ---------------- 30 ---- TRX-