hello,
i configured hardware on RSLogix 5000, CPU with IO modules. On my desk i just have a CPU and i wont to try my program but i when i turn PLC to remote-run mode and write some value to non IO variable i get a major fault
and routines are not executed.
"(Type 03) I/O Fault
(Code 23) At least one required connection not established before going into RUN mode." Maybe somebody knows how to disable such a kind of error.
BEst REgards
[?]: Major Fault on CompactLogix L32E
-
- Posts: 23
- Joined: Tue Jun 12, 2007 8:17 am
- Location: Lithuania
-
- Posts: 8
- Joined: Tue Jan 15, 2008 8:40 pm
- Location: Europe
Re: [?]: Major Fault on CompactLogix L32E
Hello kelertas,
Try disable checkbox "Major Fault on Controller if Connection Fails While in Run Mode" in connection settings under module properties. I allways test program with configured but not connected I/O`s with this checkbox disabled.
Try disable checkbox "Major Fault on Controller if Connection Fails While in Run Mode" in connection settings under module properties. I allways test program with configured but not connected I/O`s with this checkbox disabled.
-
- Posts: 23
- Joined: Tue Jun 12, 2007 8:17 am
- Location: Lithuania
Re: [?]: Major Fault on CompactLogix L32E
thank you it works
best regards