Можно ли подключить профибас-устройство к резервированной шине без модуля Y-Link? Есть ли какие-нибудь решения?
[?]: Connection to redundant PROFIBUS network 400H
-
- Site Admin
- Posts: 1122
- Joined: Wed Sep 06, 2006 12:03 pm
- Location: CIS
[?]: Connection to redundant PROFIBUS network 400H
Is it possible to connect PROFIBUS slave to redundant PROFIBUS network without Y-Link module? Please help.
-
- Posts: 186
- Joined: Sun Feb 12, 2006 5:47 pm
- Location: Europe
Re: [?]: Connection to redundant PROFIBUS network 400H
Hi,
You have to know what nonredundant slave You want to connect to redundant network. For example ET200M have interface module which can connect to redundant network (IM153-2). Also there is possibilities to connect skave to just one CPU but this is not helpful because You don't know which CPU will be master at each time instant.
regards
You have to know what nonredundant slave You want to connect to redundant network. For example ET200M have interface module which can connect to redundant network (IM153-2). Also there is possibilities to connect skave to just one CPU but this is not helpful because You don't know which CPU will be master at each time instant.
regards
-
- Posts: 3
- Joined: Tue Dec 20, 2005 8:48 pm
- Location: Europe
Re: [?]: Connection to redundant PROFIBUS network 400H
Perhaps this is what you looking after?
https://support.automation.siemens.com/ ... aller=view
https://support.automation.siemens.com/ ... aller=view