[?]: backtransfer data from simatic panel

Questions about Siemens & Analog Siemens hardware.
Software & hardware exchanger
srithep
Posts: 10
Joined: Fri May 07, 2010 5:05 am

[?]: backtransfer data from simatic panel

Post by srithep »

I can't backtransfer data from screen panel simatic OP 177B color PN/DP by Ethernet cable.
It show Could not find the pdz file (see the picture),How to do it.
I use WinCC Flexible 2008 please instruc me.
Srithep.

<a href="http://f1.uploadfile.biz/file/?i=IMEHMEIEEZMVMH" target="_blank">Download คลิกที่นี่</a>
Download คลิกที่นี่
CoMod
Site Admin
Posts: 3992
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia

Re: [?]: backtransfer data from simatic panel

Post by CoMod »

How do you back transfer the projects of an operator panel and what should you watch out for?
3. Frequently Asked Questions
3.1 Why is the message "Could not find the pdz file" displayed?
The error message depicted below can occur during the back transfer of a project when the pdz file cannot be found on the WinCE panel or does not exist there.
If the pdz project file was also transferred to the panel, it might have been stored in the wrong place with an incorrect name.
https://support.automation.siemens.com/ ... tion_e.pdf
Backtransfer possible only if Full_Source_Project_file.pdz exist in memory card (CompactFlash/SD) :(
*.PDZ = ZIP archive of WinCC Flexible project.
In most cases, the panel does not contain the source project, because the designer did not record it there.
Russian wrote:ОбратнаяПередача исходного проекта с панели возможна только, если проект реально находится на карте памяти панели (CompactFlash/SD)
*.PDZ = ZIP архив WinCC Flexible проекта.
В большинстве случаев панель не содержит исходный проект потому, что проектировщик его туда не записал.
https://support.automation.siemens.com/ ... tion_e.pdf
srithep
Posts: 10
Joined: Fri May 07, 2010 5:05 am

Re: [?]: backtransfer data from simatic panel

Post by srithep »

Thank you,I will try.