Hi all!
As I know, S-200, S7-300, S7-1200 can communicate with Sinaut Micro SC via GPRS.
But, is it allowed to combine different PLC types (S7-200, S7-300. S7-1200) in THE SAME Sinaut Micro system?
Thanks.
[?]: S7-200/300/1200 in same SINAUT Micro SC Configuration
-
- Posts: 258
- Joined: Fri Apr 03, 2009 3:24 pm
- Location: Bosnia and Herzegovina
-
- Posts: 41
- Joined: Wed Sep 06, 2006 10:07 am
- Location: Slovenia
Re: [?]: S7-200/300/1200 in same SINAUT Micro SC Configurati
As I know, Sinaut micro is for S7-200 only. You would need to unpassword the Sinaut micro library in Microwin and rewrite protocol for communicating with modem MD740 on different platform.
-