[?]: CPU314C and FM350-2

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
amit
Posts: 53
Joined: Thu Apr 23, 2009 2:12 pm
Location: India

[?]: CPU314C and FM350-2

Post by amit »

Hello,
I'm trying a combination of CPu314C ( 6ES7314 6CF01 0AB0) and Fm 350-2 ( 6ES7350-2AH00-0AB0) .
I'm using sample project . But the CPU remains in stop and FM350-2 Sf LED lits UP.
( It remains steady and flashes alternately).
In Fm350-2 manual is is given that it can be used with standard CPU's 313, 314,315.
But it is not clear that whethrer it can be used with COMPACT CPU's.
Anybody have any idea pl share with me.

Thanks And Regards

Amit
Coyote
Posts: 41
Joined: Wed Sep 06, 2006 10:07 am
Location: Slovenia

Re: CPU314C and FM350-2

Post by Coyote »

First of all check the diagnostic buffer of PLC (CPU-> PLC -> Module information) for an answer what is the cause.
amit
Posts: 53
Joined: Thu Apr 23, 2009 2:12 pm
Location: India

Re: [?]: CPU314C and FM350-2

Post by amit »

Checked. It says that I/o acess error or Module type mismatch. Checked and confirmed module type nos.
dls.dls
Posts: 17
Joined: Wed Feb 28, 2007 11:57 am
Location: France

Re: [?]: CPU314C and FM350-2

Post by dls.dls »

Hello,
Do you have always your problem?

You must be shure that the Cpu and the FM350-2 are "power on" in the same time,
They must have the same power circuit.
amit
Posts: 53
Joined: Thu Apr 23, 2009 2:12 pm
Location: India

Re: [?]: CPU314C and FM350-2

Post by amit »

Yes... I'm always trying new things so come across problems....
Anyway power circuit ( 24VDC) is same for CPU and FM350-2.

Amit
Trafo
Posts: 28
Joined: Sat Oct 09, 2010 11:39 am
Location: SLOVENIJA

Re: [?]: CPU314C and FM350-2

Post by Trafo »

CPU314C and FM350 should work fine. In Hardwer configuration you should define correct configuration. This is very important. If you see "I/o acess error or Module type mismatch", than your configuration is fault.