I have trouble with the following system:
system1:
0/1769-L32E
1/1769-SDN/B
2/1769-IQ32/A
3/1769-OB32/A
4/1769-IF4
5/1769-OF2
connect to system2:
0/
I am going to use ethernet or RS232 to connect to this system but I do not know which type of kepware should be chosen and how tag are created.
I am in hurry.
Thanks for your help.
[?]: kepware link tag with compactlogix 1769-L32E
-
- Posts: 37
- Joined: Wed Jul 21, 2010 2:30 pm
-
- Posts: 37
- Joined: Wed Jul 21, 2010 2:30 pm
Re: kepware link tag with compactlogix 1769-L32E
soory I miss
system 2 is:
0/1794-ADN
1/1794-OB16
2/1794-OÁ6
3/ 1794-OB16
system 2 is:
0/1794-ADN
1/1794-OB16
2/1794-OÁ6
3/ 1794-OB16
-
- Posts: 406
- Joined: Mon Mar 31, 2008 11:29 am
- Location: Ryazan, Russia
Re: [?]: kepware link tag with compactlogix 1769-L32E
IMHO you have only 1 system, but it include 2 I/O racks. Your second rack is the remoute ControlNet subsystem. May be you need to configurate aliases for ControlNet tags in processor tags libriary?
-
- Posts: 37
- Joined: Wed Jul 21, 2010 2:30 pm
Re: [?]: kepware link tag with compactlogix 1769-L32E
thanks for response.
But I mean that I am going to use kepware to link tag with this system by ethernet or rs 232
But I mean that I am going to use kepware to link tag with this system by ethernet or rs 232
-
- Posts: 406
- Joined: Mon Mar 31, 2008 11:29 am
- Location: Ryazan, Russia
Re: [?]: kepware link tag with compactlogix 1769-L32E
If you has your system "as is", first of all you must be sure that the processor's communication ports are enable.
ControlNet obviously your system is configured, but otherwise there is no certainty.
ControlNet obviously your system is configured, but otherwise there is no certainty.
-
- Posts: 8
- Joined: Fri Mar 26, 2010 1:07 am
Re: [?]: kepware link tag with compactlogix 1769-L32E
First have your System (Local Rack + Remote DeviceNet Node) wired correctly, then use RSNetWorx for DeviceNet to Schedule the DeviceNet, set up your scan list for your 1769-SDN. Once you set the run bit for the scanner module to 1, your I/O from the DeviceNet will update at the Network update time. Use Kepware then to look at Controller Scope Tags. Or if you have Rslinx Professional setup OPC shortcut.
To get your system working: you need 1) RSlogix 5000; 2) RSNetworx for DeviceNet
To get your system working: you need 1) RSlogix 5000; 2) RSNetworx for DeviceNet