[?]: S5 135 PLC problem
Dear Experts,
i have a S5 135U/155U cpu 928b
If I power up the system the Run led is off .QVZ & BASP led is on.
Digital Input led is ON but All digital output led is off
i connect step5 with cpu. upload my backup program (s5d). no problem to upload,but still same error.
Here is the photo--
CPU
http://i54.tinypic.com/i6e2ih.jpg
Digital input and output card.JPG
http://i53.tinypic.com/211sz2c.jpg
Error
http://i55.tinypic.com/k53eja.jpg
Error
http://i54.tinypic.com/2lng3dv.jpg
My Zennon SCADA is working fine.
Now, Please, tell me, is it a hardware fault??
and how could i find out the faulty card?
Thanks in Advance
ISteak
i have a S5 135U/155U cpu 928b
If I power up the system the Run led is off .QVZ & BASP led is on.
Digital Input led is ON but All digital output led is off
i connect step5 with cpu. upload my backup program (s5d). no problem to upload,but still same error.
Here is the photo--
CPU
http://i54.tinypic.com/i6e2ih.jpg
Digital input and output card.JPG
http://i53.tinypic.com/211sz2c.jpg
Error
http://i55.tinypic.com/k53eja.jpg
Error
http://i54.tinypic.com/2lng3dv.jpg
My Zennon SCADA is working fine.
Now, Please, tell me, is it a hardware fault??
and how could i find out the faulty card?
Thanks in Advance
ISteak
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: S5 PLC problem
After your DO there is an 4 Channel module (WFxxx or IPxxx?).
Your pictures shows an PEU (periphery not clear) and stops at OB23 with a Stopcommand.
So I think this module is your problem!
Take a look at FB57!
Your pictures shows an PEU (periphery not clear) and stops at OB23 with a Stopcommand.
So I think this module is your problem!
Take a look at FB57!
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: S5 PLC problem
please explain more
i am new on it
thanks
i am new on it
thanks
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
PEU means in your program is coded a direct access to the peripherie like L PEW or T PAW (german mnemonik).
Your 1st error picture shows an stop comand as the cause of your problem (cause of interrupt STP).
The place is OB23 on relative adress 08h (REL-SAC). Your last FB before stop was the FB57. I guess this one handels your module.
Your 2nd error picture shows a PEU (peripherie unclear) and a QVZ (acknowledgement delay).
The reason for these two errors is an module which communicate over the peripherie like your IP or WF or else.
Not DI or DO, here you would have an ADF (adress failure) at restart.
If you don't understand anything of i discribed, sorry for that. It is not so easy with the S5 if you don't have any experience.
Your 1st error picture shows an stop comand as the cause of your problem (cause of interrupt STP).
The place is OB23 on relative adress 08h (REL-SAC). Your last FB before stop was the FB57. I guess this one handels your module.
Your 2nd error picture shows a PEU (peripherie unclear) and a QVZ (acknowledgement delay).
The reason for these two errors is an module which communicate over the peripherie like your IP or WF or else.
Not DI or DO, here you would have an ADF (adress failure) at restart.
If you don't understand anything of i discribed, sorry for that. It is not so easy with the S5 if you don't have any experience.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
from my s5d program
it has 316 blocks
if i transfer all block to PLC Stop, BASP, QVZ Led is ON
and all output led is off but input led is on
if i delete OB13 & OB20 block from PLC then, Stop & QVZ led is off. Run & BASP LED is ON
(see attached s5d on zip)
i already try cold warm reset
now can you tell me how can i solve my problem??
which card is faulty digital input card or digital output card or...........??
i checked 24v in output it is all right but why there is no led on in digital output?
if 1 digital output card is faulty then every digital output card will stop working??
PLEASE TELL ME HOW CAN I SOLVE MY PROBLEM??
THANKS
ISTEAK
it has 316 blocks
if i transfer all block to PLC Stop, BASP, QVZ Led is ON
and all output led is off but input led is on
if i delete OB13 & OB20 block from PLC then, Stop & QVZ led is off. Run & BASP LED is ON
(see attached s5d on zip)
i already try cold warm reset
now can you tell me how can i solve my problem??
which card is faulty digital input card or digital output card or...........??
i checked 24v in output it is all right but why there is no led on in digital output?
if 1 digital output card is faulty then every digital output card will stop working??
PLEASE TELL ME HOW CAN I SOLVE MY PROBLEM??
THANKS
ISTEAK
-
- Posts: 4
- Joined: Sun Jul 13, 2008 9:15 pm
- Location: Czech Republic
Re: [?]: S5 135 PLC problem
If I remember, you should go to the FB47 in CPU, then show addresses (F1 or Shift F1 key) and look at address E213 or previous line. I think, there will be an access to some periphery. And this periphery is your problem. Good luck.
-
- Posts: 4
- Joined: Sun Jul 13, 2008 9:15 pm
- Location: Czech Republic
Re: [?]: S5 135 PLC problem
But... Send a snap of all rack with CPU.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
Jaja wrote:If I remember, you should go to the FB47 in CPU, then show addresses (F1 or Shift F1 key) and look at address E213 or previous line. I think, there will be an access to some periphery. And this periphery is your problem. Good luck.
i am new on it how could i detect or identify the faulty card by periphery
PLEASE I AM NEW ON S5........
is this a hardware defect?? which one possibly? here is the images....
and tell me a way to solve it.....
CPU
http://i54.tinypic.com/i6e2ih.jpg
Digital input and output card.JPG
http://i53.tinypic.com/211sz2c.jpg
Error
http://i55.tinypic.com/k53eja.jpg
Error
http://i54.tinypic.com/2lng3dv.jpg
-
- Posts: 4
- Joined: Sun Jul 13, 2008 9:15 pm
- Location: Czech Republic
Re: [?]: S5 135 PLC problem
But your pictures are the some like above ...
1. Is the CPU in the Central rack?
2. Connect to the CPU, open FB47 (Editor -> Step 5 Block, Source CPU),then switch into STL representation (Shift F5) and show addresses (Shift F1). Look for address E213 and send a screen snap.
Yes, this is a hardware defect. Maybe only a contact, maybe some card is wrong. You need to determine which one.
1. Is the CPU in the Central rack?
2. Connect to the CPU, open FB47 (Editor -> Step 5 Block, Source CPU),then switch into STL representation (Shift F5) and show addresses (Shift F1). Look for address E213 and send a screen snap.
Yes, this is a hardware defect. Maybe only a contact, maybe some card is wrong. You need to determine which one.
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
Your Problem is the card after the DO. If you are not able to tell us what card is plugged, we cannot say what you can do.
And don't look to FB47, look to FB57. Here is the command like L PEW or T PEW. So we can see what card is the issue for your problem.
Your problem IS NOT any Digital Input or Output!!!!
So believe it or not, it's your choise.
And don't look to FB47, look to FB57. Here is the command like L PEW or T PEW. So we can see what card is the issue for your problem.
Your problem IS NOT any Digital Input or Output!!!!
So believe it or not, it's your choise.
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
If your CPU is in Stop and so you have BASF it is normal you don't have an Output Signal.
I think you are not the right man for this problem.
I think you are not the right man for this problem.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
So which card is faulty?centipede wrote:Your Problem is the card after the DO. If you are not able to tell us what card is plugged, we cannot say what you can do.
And don't look to FB47, look to FB57. Here is the command like L PEW or T PEW. So we can see what card is the issue for your problem.
Your problem IS NOT any Digital Input or Output!!!!
So believe it or not, it's your choise.
Here is my program
http://plcforum.uz.ua//51170EST.S5D
-
- Posts: 44
- Joined: Tue Apr 11, 2006 4:40 am
- Location: Russia
Re: [?]: S5 135 PLC problem
I agree with centipede... The problem with the cards whose address contains PY 224 or PY 240... I suspect this cards are high speed counter IP242 (after the DO-cards)
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
OK, your problem is the IP242 6ES5 242-1AA13.
It's a 5 Channel Fast Counter Module, very old.
I think you have 2 of them.
The 1st uses the PW 224-239, the 2nd 240-255.
Wich of them is broken are not responsive, you can only check if you are online. So the FB57 is in use several times in your program, for the 1st and for the 2nd IP242.
Normaly you take the part of the 2nd one out of the program and look what happen.
Check the OB20 and OB22, here you have the start OBs with twice the FB161 and twice the FB191 each for each IP.
Now this is your part, show what you have learned.
If you have an other IP242, so change it (check the Jumpers, Settings!).
Or you try it by the Indian Method (from Siemens forum )
It's a 5 Channel Fast Counter Module, very old.
I think you have 2 of them.
The 1st uses the PW 224-239, the 2nd 240-255.
Wich of them is broken are not responsive, you can only check if you are online. So the FB57 is in use several times in your program, for the 1st and for the 2nd IP242.
Normaly you take the part of the 2nd one out of the program and look what happen.
Check the OB20 and OB22, here you have the start OBs with twice the FB161 and twice the FB191 each for each IP.
Now this is your part, show what you have learned.
If you have an other IP242, so change it (check the Jumpers, Settings!).
Or you try it by the Indian Method (from Siemens forum )
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
Thank you for your help.....
i will check it tomorrow........
again thanks
i will check it tomorrow........
again thanks
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
i have 3 card after do card here is the listcentipede wrote:OK, your problem is the IP242 6ES5 242-1AA13.
It's a 5 Channel Fast Counter Module, very old.
I think you have 2 of them.
The 1st uses the PW 224-239, the 2nd 240-255.
Wich of them is broken are not responsive, you can only check if you are online. So the FB57 is in use several times in your program, for the 1st and for the 2nd IP242.
Normaly you take the part of the 2nd one out of the program and look what happen.
Check the OB20 and OB22, here you have the start OBs with twice the FB161 and twice the FB191 each for each IP.
Now this is your part, show what you have learned.
If you have an other IP242, so change it (check the Jumpers, Settings!).
Or you try it by the Indian Method (from Siemens forum )
6ES565-4UA12
6ES565-4UA11
6ES5470-4UA13
Now can u tell me which card?
-
- Posts: 34
- Joined: Tue Feb 23, 2010 7:09 pm
- Location: Germany
Re: [?]: S5 135 PLC problem
centipede means the card on the right (with 4 plugs, named channel 1-4).
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
centipede where are you???
waiting for your reply......
see the images
http://i52.tinypic.com/2vt78qt.jpg
http://i52.tinypic.com/6iuq1y.jpg
waiting for your reply......
see the images
http://i52.tinypic.com/2vt78qt.jpg
http://i52.tinypic.com/6iuq1y.jpg
Last edited by isteak007 on Sun Sep 19, 2010 10:34 am, edited 1 time in total.
-
- Posts: 34
- Joined: Tue Feb 23, 2010 7:09 pm
- Location: Germany
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
THANKS a lot
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
Pls tell us how many IP242 do you have in your PLC?
I always see only one IP242 on your picture. The 2. is an IP243 (near the CPU). It is completely different to the IP242.
If you have only one, than your program is the problem. It's written for 2xIP242.
Are you sure thats your program is written for this PLC?
Do you have only a online copy or do you have a complete with symbolic and comments?
Pls delete the OB23 in the CPU, make a restart, check the istack, make hardcopys and show us.
If your machine don't stop (cause of DX0 parameters) load an OB23 only with a STP command inside in the PLC.
I always see only one IP242 on your picture. The 2. is an IP243 (near the CPU). It is completely different to the IP242.
If you have only one, than your program is the problem. It's written for 2xIP242.
Are you sure thats your program is written for this PLC?
Do you have only a online copy or do you have a complete with symbolic and comments?
Pls delete the OB23 in the CPU, make a restart, check the istack, make hardcopys and show us.
If your machine don't stop (cause of DX0 parameters) load an OB23 only with a STP command inside in the PLC.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
centipede pls be online i am going to factory it is 50 mile from my town. it will take 1 hour i am going to factory now......pls stay online...i will show you the stack when i will get it.....pls stay online.............. it will be a great help for me..
i have only one ip242
i have only one ip242
Last edited by isteak007 on Sun Sep 19, 2010 3:03 pm, edited 1 time in total.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
centipede wrote:Pls tell us how many IP242 do you have in your PLC?
I always see only one IP242 on your picture. The 2. is an IP243 (near the CPU). It is completely different to the IP242.
If you have only one, than your program is the problem. It's written for 2xIP242.
Are you sure thats your program is written for this PLC?
Do you have only a online copy or do you have a complete with symbolic and comments?
Pls delete the OB23 in the CPU, make a restart, check the istack, make hardcopys and show us.
If your machine don't stop (cause of DX0 parameters) load an OB23 only with a STP command inside in the PLC.
i have only two project......here another...
http://plcforum.uz.ua//SCHOEDST.S5D
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
Sorry I just see it now....
If DB18 D31.0 = 0 than you only have one IP242. Its for a other type of machine.
So I think your IP242 is broken. I hope for you, you have a spare part.
Otherwise look at Eba...!
If DB18 D31.0 = 0 than you only have one IP242. Its for a other type of machine.
So I think your IP242 is broken. I hope for you, you have a spare part.
Otherwise look at Eba...!
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
Here is my all istack & bstack
http://plcforum.uz.ua//Error_Report.zip
which of my program is ok?
51170EST.S5D
or another?
http://plcforum.uz.ua//Error_Report.zip
which of my program is ok?
51170EST.S5D
or another?
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
The PB,OB and FB of the programms are the same.
The 51170E is a backup of the PLC, the Schoed is the Offline Version.
Definitly your IP242 is not accessable, if you don't have made any changes before on the IP I'm sure its broken.
You need a sparepart.
I think we can finish the search, you must change the module.
The 51170E is a backup of the PLC, the Schoed is the Offline Version.
Definitly your IP242 is not accessable, if you don't have made any changes before on the IP I'm sure its broken.
You need a sparepart.
I think we can finish the search, you must change the module.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
Hey
i think i find some problem in power supply model
in 5v there is 15v in and other has no volt on that part i marked in image please see the images
http://i56.tinypic.com/1zyajnp.jpg
Now what is your comment
is it a problem??
waiting for your reply
i think i find some problem in power supply model
in 5v there is 15v in and other has no volt on that part i marked in image please see the images
http://i56.tinypic.com/1zyajnp.jpg
Now what is your comment
is it a problem??
waiting for your reply
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
Is it correct, you have a fan fault?
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
yes, i have a fan fault one fan has a little bit problem.
is my power supply voltage is ok?
is my power supply voltage is ok?
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
normaly the powersupply makes a shutdown if it have a fan fault.
15V never exists if you don't have a 15V module inside the PS.
15V never exists if you don't have a 15V module inside the PS.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
there is two power supply
one is cpu power supply(under the CPU)
which is ok and i have a spare power supply of this model.
but the problem is in another power supply model 6es5955-3lc14
i dont have any spare of this power supply
but this two power supply jack is exactly same but difference model
now if i use spare power supply in upward section will it work???
same voltage too......
one is cpu power supply(under the CPU)
which is ok and i have a spare power supply of this model.
but the problem is in another power supply model 6es5955-3lc14
i dont have any spare of this power supply
but this two power supply jack is exactly same but difference model
now if i use spare power supply in upward section will it work???
same voltage too......
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
Ok, for testing....
there is a connector (switch) inside the PowerSupply named F-R. Normaly closed, if you will open the PS don't make a shutdown if it have fanfault.
It is only for testing, the 135U needs the fans!
Why you don't post the Modelnumber of your spare PS??
I can't say if it's ok or not without the MLFB (6ES5...).
there is a connector (switch) inside the PowerSupply named F-R. Normaly closed, if you will open the PS don't make a shutdown if it have fanfault.
It is only for testing, the 135U needs the fans!
Why you don't post the Modelnumber of your spare PS??
I can't say if it's ok or not without the MLFB (6ES5...).
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
i have a power supply problem in S5 plc 135u/155u
now i have two power supply in S5 plc
one is for cpu.............. model 6ES5955-3LC42
another is for digital input/output card etc........model 6ES5955-3LC14
NOW 6ES5955-3LC14 power supply has a problem.... and i have no spare of this exact model power supply
but i have spare 6ES5955-3LC42 power supply. now can i use this power supply instead of 6ES5955-3LC14
now i have two power supply in S5 plc
one is for cpu.............. model 6ES5955-3LC42
another is for digital input/output card etc........model 6ES5955-3LC14
NOW 6ES5955-3LC14 power supply has a problem.... and i have no spare of this exact model power supply
but i have spare 6ES5955-3LC42 power supply. now can i use this power supply instead of 6ES5955-3LC14
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
Take it!!
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
Thanks a lot i will try it tomorrow..........
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
i Change Power Supply and ip242 but still same problem....?
istack, bstack report same......
if i delete ob13 and ob20 why plc go into run mode??
what is in ob13 and 0b20.
please tell me any other way.........because i have no Siemens support in Bangladesh...i already try them....they told me they cant provide support for S5.
Please tell me any other way
here is my digital input card and output card address or settings
Digital input card
http://i53.tinypic.com/33jiwew.jpg
000001
000010
000011
000100
000110
Digital Output card
http://i54.tinypic.com/2daddef.jpg
000001
000010
000011
000110
001100
Why same address.....why the binary combination is difference.....
is it all right
it will be a great help
Waiting for your reply
istack, bstack report same......
if i delete ob13 and ob20 why plc go into run mode??
what is in ob13 and 0b20.
please tell me any other way.........because i have no Siemens support in Bangladesh...i already try them....they told me they cant provide support for S5.
Please tell me any other way
here is my digital input card and output card address or settings
Digital input card
http://i53.tinypic.com/33jiwew.jpg
000001
000010
000011
000100
000110
Digital Output card
http://i54.tinypic.com/2daddef.jpg
000001
000010
000011
000110
001100
Why same address.....why the binary combination is difference.....
is it all right
it will be a great help
Waiting for your reply
Last edited by isteak007 on Tue Sep 21, 2010 9:23 pm, edited 1 time in total.
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
Hi,
do you change both or first the PS and check and second the IP and check?
Are you sure you have the correct settings on the IP?
If you want to pay I come and solve your problem!
do you change both or first the PS and check and second the IP and check?
Are you sure you have the correct settings on the IP?
If you want to pay I come and solve your problem!
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
yes i check all settings
i change power supply and ip242 all at a time.
Can you please tell me how can i check di do card address?
i change power supply and ip242 all at a time.
Can you please tell me how can i check di do card address?
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
You cannot have an QVZ with the Digital Equipment. Your Istack says the last called Block befor OB23 was FB57, this Block read and write to the IP242. It's the 1st block communicate to the IP in FB161 in OB20.
Anyway you can check the Cardadress if pull the card out of the rack, than you see dill-switches on the rightside of every card.
Also the Analogue-Card.
Good Luck, You'll need it.
Anyway you can check the Cardadress if pull the card out of the rack, than you see dill-switches on the rightside of every card.
Also the Analogue-Card.
Good Luck, You'll need it.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
So, You think there is no problem with digital input, digital output & analogue card.......
after changing why it is not working??
if i delete ob13 & ob20 plc comes in run mode
WHY??
Here is address..
Digital input card
http://i53.tinypic.com/33jiwew.jpg
000001
000010
000011
000100
000110
Digital Output card
http://i54.tinypic.com/2daddef.jpg
000001
000010
000011
000110
001100
after changing why it is not working??
if i delete ob13 & ob20 plc comes in run mode
WHY??
Here is address..
Digital input card
http://i53.tinypic.com/33jiwew.jpg
000001
000010
000011
000100
000110
Digital Output card
http://i54.tinypic.com/2daddef.jpg
000001
000010
000011
000110
001100
-
- Posts: 59
- Joined: Mon Feb 05, 2007 1:24 pm
- Location: Europe
Re: [?]: S5 135 PLC problem
In these blocks are the code for the IP and some else.
Look for a person next to you, which can help with Step5.
Now it's not so easy to help you more.
Look for a person next to you, which can help with Step5.
Now it's not so easy to help you more.
-
- Posts: 93
- Joined: Wed Jul 14, 2010 10:23 am
- Location: Bangladesh
Re: [?]: S5 135 PLC problem
Thanks a lot for your help
Could you just tell me address is correct???or not
again thanks...................a lot.............
you have done a great job for me
i learn many new things from you......
here is my email isteak007@gmail.com
expecting a email from you
Again thanks for your help
Could you just tell me address is correct???or not
again thanks...................a lot.............
you have done a great job for me
i learn many new things from you......
here is my email isteak007@gmail.com
expecting a email from you
Again thanks for your help