[?]: error in S5 PLC

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
isteak007
Posts: 93
Joined: Wed Jul 14, 2010 10:23 am
Location: Bangladesh

[?]: error in S5 PLC

Post by isteak007 »

in my s5 program i have no DB1....
and my plc shows qvz and basp error
and stop light is blinking

Please See my DB1 I/O assignment in online......

http://i53.tinypic.com/20ge58z.jpg

Why it is Blank...???

istack image

http://i55.tinypic.com/k53eja.jpg

http://i54.tinypic.com/2lng3dv.jpg

if i enter I/O assignment then......(( I am not sure))
i dont know what to enter....

http://i52.tinypic.com/2dkdbph.jpg

istack report

http://i56.tinypic.com/208xy8n.jpg

http://i51.tinypic.com/2vvvrq9.jpg

Bstack saying

empty or incomplete stack......

and here is my program and all (51170EST.S5D)

http://plcforum.uz.ua//100708S5.rar

Now what should i enter in I/O assignment???
Trafo
Posts: 28
Joined: Sat Oct 09, 2010 11:39 am
Location: SLOVENIJA

Re: [?]: error in S5 PLC

Post by Trafo »

First, you should tell us with which CPU are you working.
DB1 is important block. Every CPU have DB1 defined in it's structure. If you some how delete this block in CPU, you have to make "boot" of your CPU, and your CPU will generate DB1.
And DB1 normaly we don't touch, exceptionaly when we set up some comunications parameters.
:)