in my s5 program i have no DB1....
and my plc shows qvz and basp error
and stop light is blinking
Please See my DB1 I/O assignment in online......
http://i53.tinypic.com/20ge58z.jpg
Why it is Blank...???
istack image
http://i55.tinypic.com/k53eja.jpg
http://i54.tinypic.com/2lng3dv.jpg
if i enter I/O assignment then......(( I am not sure))
i dont know what to enter....
http://i52.tinypic.com/2dkdbph.jpg
istack report
http://i56.tinypic.com/208xy8n.jpg
http://i51.tinypic.com/2vvvrq9.jpg
Bstack saying
empty or incomplete stack......
and here is my program and all (51170EST.S5D)
http://plcforum.uz.ua//100708S5.rar
Now what should i enter in I/O assignment???
[?]: error in S5 PLC
-
- Posts: 28
- Joined: Sat Oct 09, 2010 11:39 am
- Location: SLOVENIJA
Re: [?]: error in S5 PLC
First, you should tell us with which CPU are you working.
DB1 is important block. Every CPU have DB1 defined in it's structure. If you some how delete this block in CPU, you have to make "boot" of your CPU, and your CPU will generate DB1.
And DB1 normaly we don't touch, exceptionaly when we set up some comunications parameters.
DB1 is important block. Every CPU have DB1 defined in it's structure. If you some how delete this block in CPU, you have to make "boot" of your CPU, and your CPU will generate DB1.
And DB1 normaly we don't touch, exceptionaly when we set up some comunications parameters.