Good day. At me a question on the panel of operator Panasonic GT32 Model: AIG32MQ02D-F. This panel GT32 (in mode Master) costs on machine tool LZS-600.
System Menu
System Version 1.15
PLC Driver Modbus (RTU mode)
Version 1.00
And PLC Emerson EC10A (in mode Slave). Programs in PLC and HMI are closed by the password. The controler is faulty. Therefore it is necessary to write the new program for HMI and PLC. My problem now following. I create the project (with any type of controlers), I load it in HMI, but on the screen are visible only the text and a drawing. There are no buttons, bulbs and other components of standard library. Firmware updated (some different versions). It doesn't help. If to create project HMI (in mode Modbus Slave) all works and it is displayed normally. In what there can be a reason?
Добрый день. У меня вопрос по панели оператора Panasonic GT32 Model: AIG32MQ02D-F. Эта панель GT32 (в режиме Master) стоит на станке LZS-600.
System Menu
System Version 1.15
PLC Driver Modbus (RTU mode)
Version 1.00
И PLC Emerson EC10A (в режиме Slave). Программы в PLC и HMI закрыты паролем. Контроллер неисправен. Поэтому приходится писать новую программу для HMI и PLC. Моя проблема сейчас следующая. Я создаю проект (с любым типом контроллеров), загружаю его в HMI, но на экране видны только текст и графика. Нет кнопок, лампочек и других компонентов стандартной библиотеки. Firmware обновлял (несколько разных версий). Это не помогает. Если создать проект HMI (в режиме Modbus Slave), то все работает и отображается нормально. В чем может быть причина?
[?+]: Problem HMI Panasonic GT32
-
- Posts: 30
- Joined: Sun Apr 15, 2007 3:25 pm
- Location: Russia
-
- Posts: 30
- Joined: Sun Apr 15, 2007 3:25 pm
- Location: Russia
Re: Problem HMI Panasonic GT32
The problem is solved. HMI the answer from Slave is required. In this case from PLC.
Проблема решена. HMI требуется ответ от Slave. В данном случае от PLC.
Проблема решена. HMI требуется ответ от Slave. В данном случае от PLC.