[?]: Configuring SIDirect DAServer 2 plc S7

Прочие SCADA: iFix, InTouch, Citect, ...
intou
Posts: 18
Joined: Tue Aug 03, 2010 12:26 pm

[?]: Configuring SIDirect DAServer 2 plc S7

Post by intou »

Hello friends,
i need to add a siemens S7 318 to existant Configuring S7 414-3PN/DP whit ethernet
and supervision made whit Intouch 10.00
Already exist 1 plc and the supervision ( S7 414-3PN/DP)
1) is possible ?
2) if is possible, how i need to configure ?



Thank's in advance. (wow)
Last edited by intou on Fri Dec 03, 2010 12:39 pm, edited 1 time in total.
Umencho
Posts: 508
Joined: Mon Jul 16, 2007 12:28 pm
Location: Europe

Re: [?]: Configuring SIDirect DAServer 2 plc S7

Post by Umencho »

Hello,

Yes, it's possible. Use the same way like in to the first connection. Under the Configuration "tree" there exist S7 414-3PN/DP connection. Right click there and select "Add S7 CP Object"... Now I am thinking "Where is the limit"? To be honest I don't know - but with 9 connections working pretty good.

BR,
Umencho