Hi.
People, yesterday I sent a backup to my Painel View 300 Mini.
This Painel works with rs232, but a sent a backup with dh485. It didn't works any more.
I've tried to send a correct backup with a correct communication, but now it has a conflit with the communication of the Rslinx.
My question is: There is a method to clean the memory of the Painel View 300 Mini without program, just using the keyboard keys?
Would anyone help with this problem?
Thanks.
[PROBLEM] Painel View 300 Mini
-
- Posts: 22
- Joined: Fri Sep 17, 2010 9:06 pm
- Location: Brazil
-
- Posts: 406
- Joined: Mon Mar 31, 2008 11:29 am
- Location: Ryazan, Russia
Re: [PROBLEM] Painel View 300 Mini
To enter the configuration menu, try pressing the keys simultaneously "Left Arrow"and "Right Arrow "
-
- Posts: 22
- Joined: Fri Sep 17, 2010 9:06 pm
- Location: Brazil
Re: [PROBLEM] Painel View 300 Mini
Hello, Ryzhij.
I've tried it, but there is nothing that could help me.
I checked all the parameters about the communication in the configuration , but there
show me DH1 RS232 with all the correct parameters.
I've tried it, but there is nothing that could help me.
I checked all the parameters about the communication in the configuration , but there
show me DH1 RS232 with all the correct parameters.
-
- Posts: 406
- Joined: Mon Mar 31, 2008 11:29 am
- Location: Ryazan, Russia
Re: [PROBLEM] Painel View 300 Mini
If you send me your file for PV300micro I will try to help you.
If you have the A-B PLC program file or correct communication setting send it to me too.
Let me know the cat.# your panel also.
Do you have the 2711-M3A19L1 or the 2711-M3A18L1 panel type?
The both types used RS232 for programming, but for work the 2711-M3A19L1 have DH-485 and the 2711-M3A18L1 have DF1 (based on RS232) interface.
If you have the A-B PLC program file or correct communication setting send it to me too.
Let me know the cat.# your panel also.
Do you have the 2711-M3A19L1 or the 2711-M3A18L1 panel type?
The both types used RS232 for programming, but for work the 2711-M3A19L1 have DH-485 and the 2711-M3A18L1 have DF1 (based on RS232) interface.
-
- Posts: 22
- Joined: Fri Sep 17, 2010 9:06 pm
- Location: Brazil
Re: [PROBLEM] Painel View 300 Micro
Hello everyone...
People I manage to communicate with painel view 300 micro.
let's see what i did:
1 - I put the painel in configuration mode
2 - In communication, I see all the parameters about it and I write it to RSlinx using RS-232 DFI devices.
3 - I didn't press auto-configure, i just press ok.
4 - Now it is works.
When i used Auto-configure it didn't work.
Thanks for all the helps.
I'm great.
People I manage to communicate with painel view 300 micro.
let's see what i did:
1 - I put the painel in configuration mode
2 - In communication, I see all the parameters about it and I write it to RSlinx using RS-232 DFI devices.
3 - I didn't press auto-configure, i just press ok.
4 - Now it is works.
When i used Auto-configure it didn't work.
Thanks for all the helps.
I'm great.