Hi,
I have a problem scheduling my CNET network. The CPU runs on Controllogix v13.XX.
I use the RSNetworx for ControlNet V 9.00.
The actual configuration have one communication adapter 1756-CNB/D (node 01), 3 flex chasis with 1794-ACN15/C whith rev 4.1 (nodes 2 to 4), Panelview 600 standard (node 05).
The two new ones I added, 1794-ACN15/C (nodes 6 & 7) has Major rev. 4 and minor Rev 3.
The problem is when I pick on line at RsNetworx program this begin scanning the network, but no complete the graphical representation of the network, only appears all ACN15 ControlNet adapters (nodes 2 to 4 and 6 &7), panel view (node 5), but the node 01 (1756-CNB/D) is not showing.
The RsNetworx continuous browsing the network but never stop.

Any Idea?

Thanks a lot!
dehell
Posts: 104
Joined: Sat Jun 13, 2009 12:25 pm
Location: Europe

Re: ControNet problem

Post by dehell »

Hi,
Do you use network adaptator to browse your ControlNet Network?
If Yes , chek his adress : keep sure there is no duplicate node!!
Best regards
jramos354
Posts: 5
Joined: Tue May 11, 2010 4:13 pm

Re: [?]: ControNet problem

Post by jramos354 »

Thanks dehell but I connect to PLC via 1756 ENBT/A



Best regards
jramos354
collgl
Posts: 11
Joined: Fri Feb 04, 2011 10:45 am

Re: [?]: ControNet problem

Post by collgl »

update the file EDS for PV600 and 1756-CNB/D
Ryzhij
Posts: 406
Joined: Mon Mar 31, 2008 11:29 am
Location: Ryazan, Russia

Re: [?]: ControNet problem

Post by Ryzhij »

IMHO you must update F/W revision your 1794-ACN15/C (nodes 6 & 7) to same rev 4.1 (nodes 2 to 4).
collgl
Posts: 11
Joined: Fri Feb 04, 2011 10:45 am

Re: [?]: ControNet problem

Post by collgl »

could u try connect pc to plc via RS232