Hi
I have a S7-400 plc.
15 ET200M and many drivers connected to this plc via profibus.
When there is BF (Bus failure or Bus Fault ), system stops.
I have to go to a Pc, open project, be online at hardware and see.. in which dp slave there is a problem.
Now my question is; how can I read this Bus failure from plc?
I'm planning to creat alarms in wincc with this information.
I'll use about 20 bits. When no communication to dp slave profibus address=1 M100.0 will be 1.
No communication to Dp 2 .... M100.1 will be 1.
I saw FB126 "PNIODiag" but I think it sucks. Do you have any example project that you can share with us?
Thanks
S7-300 BusFailure Information
-
- Posts: 25
- Joined: Mon Apr 07, 2008 3:53 pm
- Location: Turkey
-
- Posts: 65
- Joined: Thu Nov 01, 2007 9:41 pm
- Location: Belarus
Re: S7-300 BusFailure Information
Use fc125 it's easierPokajy wrote:I saw FB126 "PNIODiag" but I think it sucks.
https://support.automation.siemens.com/ ... id=6095050