PLC ARRANGEMENT
Rack 0
Slot 1-Power supply Slot 2-CPU Slot 3-IM Slot4-11-DI Cards (321-1BH02-0AA)
Rack1
Slot 3-IM Slot 4-10-DO Cards (322-1HF02-0AA0) Slot11-AI (331-7KF02-0AB0)
Rack2
Slot 3-IM Slot4-6-AI Cards Slot7 -9-AO Cards (332-5HF00-0AB0)
We are slave system we are running the plc either hardwired or profibus according to selection. We have six Pumps starting fro master plc. If we start one by one upto 5 pumps are running if we start any pump in last (i.e. sixth) CPU Going to stop Mode with 5 min. We have Changed All analog card and including CPU its going to stop mode. For Your information we have downloaded OB121, OB122 Block also but it is still going to stop mode. Set point for valve we were getting from master plc.
Finally we have changed analog input (set point to valve) in the rack 1 Slot 4(Replaced from Slot11) it was run for six hours then same problem came. What could be reason?
Diagnostic buffer of module CPU 317-2 DP
Code: Select all
Order No./ Description Component Version
6ES7 317-2AJ10-0AB0 Hardware 5
- - - Firmware V 2.6.5
Boot Loader Firmware expansion A 10.13.9
Rack: 0
Slot: 2
Event 1 of 100: Event ID 16# 4548
STOP caused by I/O management
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
07:32:53.457 AM 06/15/1994
Event 2 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 568
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.457 AM 06/15/1994
Event 3 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 566
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.457 AM 06/15/1994
Event 4 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 564
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.456 AM 06/15/1994
Event 5 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 562
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.456 AM 06/15/1994
Event 6 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 560
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.455 AM 06/15/1994
Event 7 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 594
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.452 AM 06/15/1994
Event 8 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 590
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.451 AM 06/15/1994
Event 9 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 586
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.451 AM 06/15/1994
Event 10 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 582
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.451 AM 06/15/1994
Event 11 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 578
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.451 AM 06/15/1994
Event 12 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 592
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.450 AM 06/15/1994
Event 13 of 100: Event ID 16# 2943
I/O access error, writing
P area, word access, Access address: 588
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
07:32:53.450 AM 06/15/1994
Arun