Hello, I have a problem with Dp/Dp coupler.
I followed the manual but I does not work.
All the leds in DP/DP coupler are ON.
Could you help me?
Thanks
Umencho
Posts: 508
Joined: Mon Jul 16, 2007 12:28 pm
Location: Europe

Re: [?]: DP/DP COUPLER not work

Post by Umencho »

There is only necessary to follow manual and to have correct hardware connection of cables. Please attach your project here in order to understand the problem.

Best regards,
hmi222
Posts: 6
Joined: Mon Mar 28, 2011 5:24 pm

Re: [?]: DP/DP COUPLER not work

Post by hmi222 »

did yu take the right GSD-file for the Coupler in both plcs?
How is it stripped.
How are the DIP configured.
Did yu use Diagnosebyte etc...

Yu have to pst more informations!
obesound
Posts: 2
Joined: Thu Feb 17, 2011 6:11 pm

Re: [?]: DP/DP COUPLER not work

Post by obesound »

I have the same GSD file in both PLCs, the problem is that DP/DP Coupler have all leds ON.

X1 DP X2 DP
ps on on
dia off off
hmi222
Posts: 6
Joined: Mon Mar 28, 2011 5:24 pm

Re: [?]: DP/DP COUPLER not work

Post by hmi222 »

does the GSD MATCH with the coupler? there are different dp/dp copplers from Siemens.
take only the coppler to the Profibus and close both resistors (on PLC side and COPPLer)
Is the DP cable ok (No change of A and B)?
Is the coppler in the GSD configured like yur dip-Switches?
deltafox1002
Posts: 18
Joined: Sun May 18, 2008 8:20 am
Location: Europe

Re: [?]: DP/DP COUPLER not work

Post by deltafox1002 »

Hello

which coupler do you have ?

http://support.automation.siemens.com/W ... id=1179924

In the manual from the coupler v2 is there a fault in the example.

On page 6-12

DB10 Norm_Diag is the ARRAY [1..6] but it must be ARRAY [1..16]
keerati
Posts: 1
Joined: Wed Jul 07, 2010 10:02 am

Re: [?]: DP/DP COUPLER not work

Post by keerati »

Hello,

I think this problem from wrong configuration input and output word in Hardware config of
DP/DP coupler. Example, in master side you start by input word then output word that means
at slave side must start with output word then input word..