Dear Friends,
Is it possible to use MP 277 as routing device between Ethernet & Profibus.
My application is that, MP 277 is connected to the main S7 CPU through Ethernet ( more than 500 meters) and I have one IM 151-1 (Profibus DP interface) near to the MP 277.
Is it possible to connect the Profibus of IM 151-1 to the PLC port of the MP 277 so that it can communicate to main S7 CPU via MP 277.
Means routing function in MP 277 to convert ethernet communication to Profibus and vice-verse
[?]: Siemens MP277 as the router between Ethernet & Profibus
-
- Posts: 25
- Joined: Tue Dec 28, 2010 2:11 pm
-
- Posts: 53
- Joined: Wed Nov 26, 2008 8:01 am
- Location: Iran
Re: [?]: Siemens MP277 as the router between Ethernet & Prof
hi.
i have to edit my post. the next post is true.
i have to edit my post. the next post is true.
Last edited by alireza136110 on Mon Jun 27, 2011 4:50 am, edited 1 time in total.
-
- Posts: 79
- Joined: Sat Apr 14, 2007 4:46 am
- Location: China
Re: [?]: Siemens MP277 as the router between Ethernet & Prof
You need to install software PLC WinAC MP 2007 or WinAC MP 2008.
-
- Posts: 25
- Joined: Tue Dec 28, 2010 2:11 pm
Re: [?]: Siemens MP277 as the router between Ethernet & Prof
Thank you very much for your valuable suggestion.guolibin wrote:You need to install software PLC WinAC MP 2007 or WinAC MP 2008.
Now I am to configure my system.