[?]: CP 5512 Problem witch Profibus

Post by bhole1 »

Hi all

Im have one problem. Im have CP 5512 and HW adapter.
http://www.imageupload.org/?d=04220EA01


And cable
http://www.imageupload.org/?d=0D8258821

Sometimes I do not know why but it happens when I come to the PLC and only connecting to a connector on the network is now Bus Fault. Where will it be? Not only does not set the connect cable.

Thank you for answer
CoMod
Site Admin
Posts: 3992
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia

Re: [?]: CP 5512 Problem witch Profibus

Post by CoMod »

It is possible.
network length ?
number of devices ?

1. check terminator switches - at ends must be ON
2. connect to second (free) interface (for example to MPI)
bhole1
Posts: 9
Joined: Tue Sep 21, 2010 7:18 am

Re: [?]: CP 5512 Problem witch Profibus

Post by bhole1 »

Im have 25PLC network on 20 conect standar not problem
only 5 just plug cable and inscriptions BF. I only 5 just plug cable and inscriptions BF.

Terminator is ok.one is to join the peripheral or the PLC is still useful BF.
Conect MPI or other peripheral is it certainly BF.

:?: