Hi all
Im have one problem. Im have CP 5512 and HW adapter.
http://www.imageupload.org/?d=04220EA01
And cable
http://www.imageupload.org/?d=0D8258821
Sometimes I do not know why but it happens when I come to the PLC and only connecting to a connector on the network is now Bus Fault. Where will it be? Not only does not set the connect cable.
Thank you for answer
[?]: CP 5512 Problem witch Profibus
-
- Site Admin
- Posts: 3992
- Joined: Thu Feb 16, 2006 3:25 pm
- Location: Russia
Re: [?]: CP 5512 Problem witch Profibus
It is possible.
network length ?
number of devices ?
1. check terminator switches - at ends must be ON
2. connect to second (free) interface (for example to MPI)
network length ?
number of devices ?
1. check terminator switches - at ends must be ON
2. connect to second (free) interface (for example to MPI)
-
- Posts: 9
- Joined: Tue Sep 21, 2010 7:18 am
Re: [?]: CP 5512 Problem witch Profibus
Im have 25PLC network on 20 conect standar not problem
only 5 just plug cable and inscriptions BF. I only 5 just plug cable and inscriptions BF.
Terminator is ok.one is to join the peripheral or the PLC is still useful BF.
Conect MPI or other peripheral is it certainly BF.
only 5 just plug cable and inscriptions BF. I only 5 just plug cable and inscriptions BF.
Terminator is ok.one is to join the peripheral or the PLC is still useful BF.
Conect MPI or other peripheral is it certainly BF.