Hi, i have a PLC TSX 57452 with an ethernet card ETY 110 and a normal laptop.
I would like to go online with PL7 (i have the program) using ethernet, but i can't understand if i need special drivers, a card or just insert the IP of the network and push "Connect".
At the moment there is another Pc using windows 98 that permit to browse the program, but it's equipped with a card that i never saw before and i can't find it's IP address (the ethernet cable is plugged into this special PCI card), so i guess i'll just have to do cmd -> ipconfig /all.
Inside PL7 the PLC address is on "Default IP Address".
If anyone can help me with links and tips i appreciate !
Thanks in advance
[? Solved+] Going online with PL7 Tsx plc through Ethernet
-
- Posts: 4
- Joined: Fri Oct 01, 2010 8:07 pm
[? Solved+] Going online with PL7 Tsx plc through Ethernet
Last edited by mesta1 on Thu Aug 18, 2011 2:51 pm, edited 1 time in total.
-
- Posts: 392
- Joined: Fri Dec 18, 2009 3:02 pm
- Location: Киев
Re: [?] Going online with PL7 Tsx plc through Ethernet
do not need a special card.
1) ETY 110 must be configured:
- IP address, eg 192.168.1.1
- XWAY address (NETWORK, STATION, exhibited the switch), for example 1.1
2) In a laptop you need to install driver XIP (there is a Driver Pack for PL7)
3) The driver XIP configure:
- Your own station (XWAY address on the same network), for example 1.2
- Station PLC, for example, IP = 192.168.1.1 XWAY = 1.1
4) After installing the driver ping in XWAY Driver Manager -> XWAY Test:
Driver = XIP, Remote Address = 1.1.0, Connect, Start.
If the test passes, you can connect with PL7
5) In PL7, the menu Deifine PLC Address
Driver = XIP
Address = {1.1} SYS
1) ETY 110 must be configured:
- IP address, eg 192.168.1.1
- XWAY address (NETWORK, STATION, exhibited the switch), for example 1.1
2) In a laptop you need to install driver XIP (there is a Driver Pack for PL7)
3) The driver XIP configure:
- Your own station (XWAY address on the same network), for example 1.2
- Station PLC, for example, IP = 192.168.1.1 XWAY = 1.1
4) After installing the driver ping in XWAY Driver Manager -> XWAY Test:
Driver = XIP, Remote Address = 1.1.0, Connect, Start.
If the test passes, you can connect with PL7
5) In PL7, the menu Deifine PLC Address
Driver = XIP
Address = {1.1} SYS
Russian wrote:Специальная карта не нужна.
1) В ЕТY 110 нужно сконфигурировать:
- IP адрес; например 192.168.1.1
- XWAY адрес (NETWORK,STATION, выставляется переключателем), например 1.1
2) В ноутбуке нужно установить драйвер XIP (есть в Driver Pack к PL7)
3) В драйвере XIP сконфигурировать:
- собственную станцию (XWAY адрес в той же сети), например 1.2
- станцию ПЛК, например IP=192.168.1.1 XWAY=1.1
4) После установки драйвера проверить связь в XWAY Driver Manager ->XWAY Test:
Driver=XIP, Remote Address=1.1.0, Connect, Start.
Если тест проходит, можно соединяться с PL7
5) В PL7, в меню Deifine PLC Address
Driver= XIP
Address={1.1}SYS
-
- Posts: 4
- Joined: Fri Oct 01, 2010 8:07 pm
Re: [Solved] Going online with PL7 Tsx plc through Ethernet
Thanks for your help.
I tried and all was ok
I tried and all was ok