Hello,
I have a problem with CPU 312-1AE13-0AB0 and SM 331-1KF01-0AB0.
In my actual configuration I am using CPU312 with SM321 and SM322. The system is OK.
When I want to extend and plug into the rack SM 331 331-1KF01 the system is going down and all the led's (SF, DC5V, FRCE, RUN, STOP led) are going to ON.
I can't access the system at this point.
I tried also with OB122 but no result. The power supply I think is enough, 2.5A.
The MMC is 64 K and is clean and new. The bus connector is not the same for all cards? I used the same connector from DI and DO cards.
What could be the reason for that??
thanks,
Alin
[?]: When I plug SM 331 the CPU312 STOP led ON
-
- Posts: 2
- Joined: Tue Sep 06, 2011 2:34 pm
-
- Site Admin
- Posts: 1387
- Joined: Sat Aug 13, 2005 6:15 am
Re: [?]: When I plug SM 331 the CPU312 STOP led ON
connect with system power off
it`s same front connector
it`s same front connector
-
- Posts: 508
- Joined: Mon Jul 16, 2007 12:28 pm
- Location: Europe
Re: [?]: When I plug SM 331 the CPU312 STOP led ON
Basically there are need http://support.automation.siemens.com/W ... n/19350076
But in case of all leds is ON means CPU should be replaced after. What is it behavior after removing that module?
But in case of all leds is ON means CPU should be replaced after. What is it behavior after removing that module?