Does somebody have experience in configuring communication between S7-400 PLC and SIPROTEC protection relay, from the side of SIPROEC, configuration with DIGSI?
I have two transformer protection relays 7UT613, which are configured almost the same, the difference is that one is 110/35/10kV and another 110/35/6kV. From the first I successfully read all data according to standard profile mapping.
From the second I only could not read current measurements of side 2 and 3 (35/6kV). In the configuration matrix both relay configured in the same way. I have tried to change scaling parameter and zero offset parameters for side 2 and 3 and nothing changed.
Are there some specific steps to perform before communication configuration changes applies to relay?
Any ideas how to resolve such problem?
Russian wrote:Всем привет!
У кого-нибудь есть опыт работы и настройки связи межди ПЛК S7-400 и реле защиты SIPROTEC, в частности конфигурация в ПО DIGSI?
Проблема: у меня есть два реле защиты трасформатора, модель 7UT613, которые отконфигурированны практически одинаково, разница только в том что первое на 110/35/10 кВ а второе 110/35/6 кВ. С первого я нормально читаю все данные в соответсвии со стандартым профилем связи ProfiBus. А со второго(которое на 110/35/6) я не могу прочитать токи по второй и третей стороне(35/6). В матрице оба реле отконфигурированны одинкого. Я пробовал менять настроики scaling и zero offset для стороны 2 и 3 и ничего не менялось.
Есть ли какие-либо специфические этапы для применения изменений настроек? может инициализация какая-то? мастер-рисет?