Good day, I just want to ask if there's a way to communicate CPU351PN/DP to S7-400 CPU with CP443-1 using ethernet network.
And also please provide the block to communicate these two CPU's.
Thank you very much in advance.
Best regards,
Reymond
[?] S7-315PN/DP comunication to S7-400/CP443-1 via ethernet
-
- Posts: 139
- Joined: Wed Sep 26, 2007 2:57 am
- Location: Philippines
-
- Posts: 5
- Joined: Tue Jul 22, 2008 5:39 am
- Location: China
Re: 315PN/DP comunication to S7-400 with CP443-1 using ether
400 need block SFB12 BSEND and SFB13BRCV
300 need block FB12 BSEND and FB13BRCV
300 need block FB12 BSEND and FB13BRCV
-
- Posts: 186
- Joined: Sun Feb 12, 2006 5:47 pm
- Location: Europe
Re: [?] S7-315PN/DP comunication to S7-400/CP443-1 via ether
Hi,
If You want to use DSEND and BRCV You should configure S7 connection in NetPro.
regards
If You want to use DSEND and BRCV You should configure S7 connection in NetPro.
regards
-
- Posts: 508
- Joined: Mon Jul 16, 2007 12:28 pm
- Location: Europe
Re: [?] S7-315PN/DP comunication to S7-400/CP443-1 via ether
How do you configure a specified and an unspecified S7 connection for data exchange between S7-300 and/or S7-400 by way of Industrial Ethernet CPs?
http://support.automation.siemens.com/W ... n/33118248
http://support.automation.siemens.com/W ... n/33118248
-
- Posts: 139
- Joined: Wed Sep 26, 2007 2:57 am
- Location: Philippines
Re: [?] S7-315PN/DP comunication to S7-400/CP443-1 via ether
Dear Colleagues,
Happy new year....
My concern is, what should be the block to be use in order to communicate Integrated PROFINET of 315 PN/DP to CP443-1. I'am doing offline programming right now and hopefully do the commissioning by january.
Best regards,
Reymond
Happy new year....
My concern is, what should be the block to be use in order to communicate Integrated PROFINET of 315 PN/DP to CP443-1. I'am doing offline programming right now and hopefully do the commissioning by january.
Best regards,
Reymond
-
- Posts: 186
- Joined: Sun Feb 12, 2006 5:47 pm
- Location: Europe
Re: [?] S7-315PN/DP comunication to S7-400/CP443-1 via ether
Hi,
Take a look this manual
https://support.automation.siemens.com/ ... earch.aspx
http://support.automation.siemens.com/W ... n/20982954
Use of proper communication function depends of characteristic of communication partners, amount of data to be exchanged and type of communication (uni- or bi- direction, with or without acknowledgement...)
regards
Take a look this manual
https://support.automation.siemens.com/ ... earch.aspx
http://support.automation.siemens.com/W ... n/20982954
Use of proper communication function depends of characteristic of communication partners, amount of data to be exchanged and type of communication (uni- or bi- direction, with or without acknowledgement...)
regards