Current condition of the CPUs are:
RACK_0 CPU:EXTF(Lit), BUS2F(Blink_Blinking rate almost 2Hz), RUN(Lit), REDF(Lit), IFM1F(Lit), IFM2F(Lit), MSTR(Lit), RACK0(Lit)
RACK_1 CPU: All Leds are Flashing
I also have a fault in a DP called DP 11. I attached the pictures of the DP in the below download link. In that particular IM module SF(Lit) and BF(Flashing).
I couldn't go online with RACK_1 CPU.
I abled to go online with the RACK_0 CPU.
Download link contains the screenshot of the Hardware Configuration with Diagonostic Buffer of the RACK_0 CPU which is now taking care the system.
Download Link: http://www.sendspace.com/file/vlqggw
Please guide me to recover from this condition.
Diagnostic buffer of module CPU 417-4 H
Show
Diagnostic buffer of module CPU 417-4 H
Order No./ Description Component Version
6ES7 417-4HL00-0AB0 Hardware 3
- - - Firmware V 2.1.0
Rack: 0
Slot: 5
Event 1 of 44: Event ID 16# 39B1
I/O access error when updating the process image input table
P area, byte access, access address: 35 ////and also for address 8...35
process image partition no.: 0
not user relevant(Z1): 2942
Requested OB: Program execution error OB (OB85)
Priority class: 26
External error, Incoming event
02:16:.748 9 12/18/2011
......
Event 34 of 44: Event ID 16# 38C7
Distributed I/Os: station operational again, but error(s) in module parameter assignment
Address of the affected DP slave: station number: 11
DP master system ID: 1
Log. base address of the DP slave: Input address: 16366
Log. base address of the DP master: 16377
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Outgoing event
02:16:.674 9 12/18/2011
Event 35 of 44: Event ID 16# 5961
Parameter assignment error in parameters for distributed S7 modules
Input address: 34 of the module with parameter assignment errors
Error type: Slot configured for CPU is not occupied or is occupied by a place holder, or a station has failed or the switched I/O system has lost its redundancy.
Data record number: 250
Operating mode: RUN
Event occurred in the master CPU in rack 0
External error, Incoming event
02:16:.673 9 12/18/2011
.........
Order No./ Description Component Version
6ES7 417-4HL00-0AB0 Hardware 3
- - - Firmware V 2.1.0
Rack: 0
Slot: 5
Event 1 of 44: Event ID 16# 39B1
I/O access error when updating the process image input table
P area, byte access, access address: 35 ////and also for address 8...35
process image partition no.: 0
not user relevant(Z1): 2942
Requested OB: Program execution error OB (OB85)
Priority class: 26
External error, Incoming event
02:16:.748 9 12/18/2011
......
Event 34 of 44: Event ID 16# 38C7
Distributed I/Os: station operational again, but error(s) in module parameter assignment
Address of the affected DP slave: station number: 11
DP master system ID: 1
Log. base address of the DP slave: Input address: 16366
Log. base address of the DP master: 16377
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Outgoing event
02:16:.674 9 12/18/2011
Event 35 of 44: Event ID 16# 5961
Parameter assignment error in parameters for distributed S7 modules
Input address: 34 of the module with parameter assignment errors
Error type: Slot configured for CPU is not occupied or is occupied by a place holder, or a station has failed or the switched I/O system has lost its redundancy.
Data record number: 250
Operating mode: RUN
Event occurred in the master CPU in rack 0
External error, Incoming event
02:16:.673 9 12/18/2011
.........
Uploaded with spamm.us
---
Thanks