[?]: FTView ME - Alarm problem

RSLinx, RSLogix, RSView, LogixPro ...
pembuk
Posts: 10
Joined: Sat Oct 16, 2010 6:16 pm

[?]: FTView ME - Alarm problem

Post by pembuk »

Hi All,

I have problem with alarms by using FTView ME 6.0. The problem is with no displaying any configurated alarms. I had tried every thing and I have no idea what could be wrong. I was chacked every alarm triger and made a indicator with the same expression. The indicator works correctly with alarm expression but alarm doesn't displayed. Has any one had the same problem? I can send my aplication if necessary.

Cheers
Ryzhij
Posts: 406
Joined: Mon Mar 31, 2008 11:29 am
Location: Ryazan, Russia

Re: [?]: FTView ME - Alarm problem

Post by Ryzhij »

I understand that alarms you use special tags.
Please take note that the alarm is not so much the value of the tag, as his property.
This property must be configured.
For an analog tag configured thresholds of various alarms and tag for a discrete type is declared a state of alarm is.
Check tags configuration.
pembuk
Posts: 10
Joined: Sat Oct 16, 2010 6:16 pm

Re: [?]: FTView ME - Alarm problem

Post by pembuk »

Hi,

I think that my problem solved is. Someone tell me that I need to check one option about using Alarms by aplication in system/startup window.
This option was unmarked in my project. Now I thing that it could be the real reason of my problem.

Any way, many thanks for quick reply.

Cheers