[?]: Problem with HW-Update (Step 7 5.5 + WinCC Flex 2008)

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
blukrr
Posts: 5
Joined: Tue May 31, 2011 11:10 pm

[?]: Problem with HW-Update (Step 7 5.5 + WinCC Flex 2008)

Post by blukrr »

I have a project here that was provided with a machine that was bought a couple of years ago, no one usually had go online and modify anything and it was left how it was until now.
I'm having a problem with the source code provided when the equipment was delivered.
We need to modify the program as part of a diversity increase in our process and it seems that the project was created using an older version of Step 7 (probably 5.4) and now we have Step 7 5.5 in our machines. This machine is based in a MP277 HMI using WinAC as the PLC and the HMI it self.

For some reason when I try to open the project (after I have updated the hardware catalog) it says that the HW-Update is an "older version or not fully installed" and you can see in the anexed picture. I have thoroughly followed the procedure to update it (downloaded and then installed the download files).

I tried updating it several times and it didn't work. I starting to think that I'll have to install Step 7 5.4 to be able to open it. At first I had a problem with WinCC flexible now I have installed all of the requires programs and updated the product catalog and it still won't open.
Image

the reason I know it's not the program is that we have a Siemens PG and all the programs (Step 7 5.x and WinCC Flexible) are installed and it's running ok. I might check the real version of the programs running in this PG so I can compare to what I got here.

But this PG it's not avaliable for us engineers it's stricltly for the maintenance crew and even though I can use it once in a while, for develepment and modifications that don't involve maintenance I will have to jeaopardize the avaliability of this machine in case of a problem, and you might know well that if this PG stops working they will probably say I did something to it. And It's not cool to mess with a U$ 10,000 equipment.
Thanks in advance for any help given.
Info
Faq & Info
Faq & Info
Posts: 428
Joined: Wed Oct 05, 2005 9:00 am

Re: [?]: Problem with HW-Update (Step 7 5.5 + WinCC Flex 200

Post by Info »

Download and install
Service Pack 1 for STEP 7 V5.5
http://support.automation.siemens.com/D ... n/52336451

Hardware Support Packages
http://support.automation.siemens.com/D ... n/23183356
blukrr
Posts: 5
Joined: Tue May 31, 2011 11:10 pm

Re: [?]: Problem with HW-Update (Step 7 5.5 + WinCC Flex 200

Post by blukrr »

I was able to get the actual version of the installed hardware in the PG the maintenace uses open those files.
Image

I starting to think that Step 7 5.5 can´t open Step 7 5.4 files but I not sure about this.
CoMod
Site Admin
Posts: 3992
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia

Re: [?]: Problem with HW-Update (Step 7 5.5 + WinCC Flex 200

Post by CoMod »

For use new hardware you need use new Step7 v5.5 SP1.