Dear All,
What Ethernet cable to use for programming and connecting with S7-300 Cpu with ethernet port when connecting directly with the CPU or not using a ethernet network switch? Is it a straight through or crossover cable?
Thanks in advance.
[?]: What Ethernet Cable to use for S7-300 CPU
-
- Posts: 44
- Joined: Sun Aug 10, 2008 3:27 pm
- Location: Philippines
-
- Posts: 12
- Joined: Wed Feb 29, 2012 11:49 pm
Re: [?]: What Ethernet Cable to use for S7-300 CPU
Crossover is the answer, definetly.Peehel wrote:Dear All,
What Ethernet cable to use for programming and connecting with S7-300 Cpu with ethernet port when connecting directly with the CPU or not using a ethernet network switch? Is it a straight through or crossover cable?
Thanks in advance.
With a crossover, even if there is a switch everything is fine. With a straight you can work only with switch or , without a switch, hope that the auto-switching firmware is working properly (pretty rare).
So use a crossover.
For your information the crossover is the dark white cable with green connectors (this is the default aspect).
-
- Posts: 1
- Joined: Mon Jan 03, 2011 9:02 am
Re: [?]: What Ethernet Cable to use for S7-300 CPU
Nomaly Siemens PLC is support both type of the ethernet cable ,it means straight and cross can be actomaticly check by siemens PLC.