[?+]: SINUMERK 840D does not have enough memory for program

Questions about Siemens & Analog Siemens hardware.
Software & hardware exchanger
sergio124816
Posts: 5
Joined: Fri Jun 29, 2012 12:14 pm

[?+]: SINUMERK 840D does not have enough memory for program

Post by sergio124816 »

(sos)
CNC 840D (NPU572 + PLK315-2DP + MMC103)
machine is not working 6 years, respectively, the battery has to NPU572
there is a floppy disk from the manufacturer (BOSH) to the project and archives PLC PLC and NC.
When you turn on the MMS message to the lack of communication with the NPU ...
LEDs SF on three modules perefiriynyh IMR300 ...
When trying to connect to the laptop via step7 x122 is also lack of communication ...
According to the manual cleared the PLC memory, LEDs are turned off, step7 saw PLC, the MMC has left a message that there is no connection ...
I'm trying to fill in Architectural project by a PLC said step should be 131kb low memory and in Col. 48, and third, respectively, filled with blocks and get errors.
With simocom trying to fill the archive PLC (23234PLC.ARC) of the same recorded message and then running out of memory ...
Tell me which way to go further?
(sos)
graf_STEP7
Posts: 57
Joined: Tue Feb 13, 2007 5:41 pm
Location: Europe

Re: SINUMERK 840D does not have enough memory for PLC progra

Post by graf_STEP7 »

Hi

At first !

1. You must clear NCK and PLC !
(You must use switch S3 and S4)
You need dokumention --> https://www.automation.siemens.com/doco ... TTPS=REDIR

2. Read in NCK-Parameter !
Here are options-infos.
as example --> how big is the PLC-Ram

3. Read in the PLC-parameter.


Ready
sergio124816
Posts: 5
Joined: Fri Jun 29, 2012 12:14 pm

Re: SINUMERK 840D does not have enough memory for PLC progra

Post by sergio124816 »

1. Memory clear S3, S4 is ok.
2,3. Step7-> PLC -> Module Information -> Memory = 48kb !!!
Project Memory 138kb...
There are other ideas?
graf_STEP7
Posts: 57
Joined: Tue Feb 13, 2007 5:41 pm
Location: Europe

Re: SINUMERK 840D does not have enough memory for PLC progra

Post by graf_STEP7 »

HI
sergio124816 wrote:1. Memory clear S3, S4 is ok.
2,3. Step7-> PLC -> Module Information -> Memory = 48kb !!!
Project Memory 138kb...
There are other ideas?
1. After clear NCK --> and load defaults --> you have 4 axis ! ?

2. Clear PLC with the switch --> now the PLC-LED must green flash !

3. Read in --> NCK-Datas with MMC103 --> now you must have the orgin "names and counts" of the machine ! ?

4. Read in --> PLC-Datas with MMC103 --> you NOT need Step7-Programm, you only can make this all with MMC103 ! ?


Make this 4 Steps.
Look, if errors ocour ? ( read the Protocoll --> softkey )
sergio124816
Posts: 5
Joined: Fri Jun 29, 2012 12:14 pm

Re: SINUMERK 840D does not have enough memory for PLC progra

Post by sergio124816 »

Problem solved by replacing NCU 572.2 for the same from another machine.
Reading and writing machine data and PLC programs are now available from both the MMC103, and from STEP7.

Thank you for your help.
Boxy
Posts: 44
Joined: Thu May 13, 2010 4:34 pm

Re: SINUMERK 840D does not have enough memory for PLC progra

Post by Boxy »

The Momory for PLC Space can be set inside the MADA's 19250 ???
sergio124816
Posts: 5
Joined: Fri Jun 29, 2012 12:14 pm

Re: SINUMERK 840D does not have enough memory for PLC progra

Post by sergio124816 »

What is meant by "MADA's 19250 ???"
ikavakci
Posts: 2
Joined: Sat Oct 16, 2010 9:44 am

Re: SINUMERK 840D does not have enough memory for PLC progra

Post by ikavakci »

sergio, are you need help? (still) :) :) :) :)
sergio124816
Posts: 5
Joined: Fri Jun 29, 2012 12:14 pm

Re: SINUMERK 840D does not have enough memory for PLC progra

Post by sergio124816 »

Thanks a lot, problem solved.