Anybody can translate this crash file ? I want to find the reason of CPU crash. How to read it?
Diagnostic Data
Show
Fri Oct 05 11:23:48 2012 from RSLogix5 v7.30.10.01
Diagnostic Data for Processor PLC5/40 Series E Revision J
Domino Plug 1 Firmware Series/Rev: A/T
Domino Plug 2 Firmware Series/Rev: A/T
Fault logged by microprocessor: UPA
Error string: "REBOOTp1: i_be_dead trap error vector=00010, at address 000c2"
D0 = 0x000000C5 A0 = 0x00207EEE
D1 = 0x000000BF A1 = 0x00017F91
D2 = 0x00000050 A2 = 0x002404B7
D3 = 0x000000FF A3 = 0x00207F86
D4 = 0x00030004 A4 = 0x0019CF38
D5 = 0x2FFF0000 A5 = 0x00207F86
D6 = 0x00000001 A6 = 0x0020E40E
D7 = 0x00000007 A7 = 0x00207F30
Error Code = 0x008A
Trap Offset = 0x0010
Return address = 0x000000C2
68Ks Status Register = 0x2000
Following are 26 words of stack data in hex
01B4 0000 0020 7F94 0000 6866 0020 7F94 0000 66C8 0020 7F86 0000 0029 0000
0001 0000 0003 2FFF 0000 0024 04A2 0024 043E 0000 6B10
Raw Data of above
0x198DAA 00 01 00 00 00 C5 00 00 00 BF 00 00 00 50 00 00 .............P..
0x198DBA 00 FF 00 03 00 04 2F FF 00 00 00 00 00 01 00 00 ....../.........
0x198DCA 00 07 00 20 7E EE 00 01 7F 91 00 24 04 B7 00 20 ... ~......$...
0x198DDA 7F 86 00 19 CF 38 00 20 7F 86 00 20 E4 0E 00 20 .....8. ... ...
0x198DEA 7F 30 00 8A 00 10 00 00 00 C2 20 00 01 B4 00 00 .0........ .....
0x198DFA 00 20 7F 94 00 00 68 66 00 20 7F 94 00 00 66 C8 . ....hf. ....f.
0x198E0A 00 20 7F 86 00 00 00 29 00 00 00 01 00 00 00 03 . .....)........
0x198E1A 2F FF 00 00 00 24 04 A2 00 24 04 3E 00 00 6B 10 /....$...$.>..k.
0x198E2A 52 45 42 4F 4F 54 70 31 3A 20 69 5F 62 65 5F 64 REBOOTp1: i_be_d
0x198E3A 65 61 64 20 74 72 61 70 20 65 72 72 6F 72 20 76 ead trap error v
0x198E4A 65 63 74 6F 72 3D 30 30 30 31 30 2C 20 61 74 20 ector=00010, at
0x198E5A 61 64 64 72 65 73 73 20 30 30 30 63 32 0D 0A 64 address 000c2..d
0x198E6A AD 84 00 C0 FF 9A 01 0B 9D 20 45 5A 3E 61 90 A0 ......... EZ>a..
0x198E7A FF DB 4C C3 EF 9D 83 F7 CF FB A5 5F DF DF CE 7A ..L........_...z
0x198E8A 6F FF 10 CE 9D 91 1A FE DF FF 60 DB F3 A7 50 B9 o.........`...P.
0x198E9A FF FF 14 48 FF 7B 8C 5A D7 A6 69 EE FE 5A 0E 42 ...H.{.Z..i..Z.B
0x198EAA FE 42 B2 25 7F 77 .B.%.w
=============================================================================
UPAs registers and stack
D0 = 0x00000000 A0 = 0x000000C2
D1 = 0x0000FFFF A1 = 0x2FFF0000
D2 = 0x00006866 A2 = 0x002404A2
D3 = 0x00207F94 A3 = 0x0024043E
D4 = 0x000066C8 A4 = 0x00006B10
D5 = 0x00207F86 A5 = 0x0020842A
D6 = 0x00000029 A6 = 0x002410A6
D7 = 0x00000001 A7 = 0x00200428
Error Code = 0x198A
Trap Offset = 0x7FFF
Return address = 0x29008A19
68Ks Status Register = 0x2000
Following are 30 words of stack data in hex
8085 8580 8032 3280 0000 0400 0000 1000 0000 4000 0001 0000 0000 0020 0020
0040 0000 0080 00C0 0080 00C0 00C0 0000 0008 0008 0008 0008 0008 0008 0008
Raw Data of above
0x19E206 00 01 00 00 00 00 00 00 FF FF 00 00 68 66 00 20 ............hf.
0x19E216 7F 94 00 00 66 C8 00 20 7F 86 00 00 00 29 00 00 ....f.. .....)..
0x19E226 00 01 00 00 00 C2 2F FF 00 00 00 24 04 A2 00 24 ....../....$...$
0x19E236 04 3E 00 00 6B 10 00 20 84 2A 00 24 10 A6 00 20 .>..k.. .*.$...
0x19E246 04 28 19 8A 7F FF 29 00 8A 19 20 00 80 85 85 80 .(....)... .....
0x19E256 80 32 32 80 00 00 04 00 00 00 10 00 00 00 40 00 .22...........@.
0x19E266 00 01 00 00 00 00 00 20 00 20 00 40 00 00 00 80 ....... . .@....
0x19E276 00 C0 00 80 00 C0 00 C0 00 00 00 08 00 08 00 08 ................
0x19E286 00 08 00 08 00 08 00 08 ........
UPBs registers and stack
D0 = 0x00000000 A0 = 0x0018318C
D1 = 0x00000000 A1 = 0x00202584
D2 = 0x00000000 A2 = 0x00000000
D3 = 0x00000F52 A3 = 0x001988DC
D4 = 0x00000001 A4 = 0x00188D78
D5 = 0xFFFFDF00 A5 = 0x0020042C
D6 = 0xDF7EFFFF A6 = 0x00202588
D7 = 0xFDFFFB00 A7 = 0x00202556
Error Code = 0x0001
Trap Offset = 0x0000
Return address = 0x000192B4
68Ks Status Register = 0x2700
Following are 30 words of stack data in hex
2008 0000 9C9C 0018 8E18 0019 88B6 0019 88DC 0000 982E 0020 2584 0000 0000
0002 0000 0000 0019 88DC 0000 0000 0020 25C4 0000 85EC 0019 88DC 0000 0005
Raw Data of above
0x19E28E 00 02 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ................
0x19E29E 0F 52 00 00 00 01 FF FF DF 00 DF 7E FF FF FD FF .R.........~....
0x19E2AE FB 00 00 18 31 8C 00 20 25 84 00 00 00 00 00 19 ....1.. %.......
0x19E2BE 88 DC 00 18 8D 78 00 20 04 2C 00 20 25 88 00 20 .....x. .,. %..
0x19E2CE 25 56 00 01 00 00 00 01 92 B4 27 00 20 08 00 00 %V........'. ...
0x19E2DE 9C 9C 00 18 8E 18 00 19 88 B6 00 19 88 DC 00 00 ................
0x19E2EE 98 2E 00 20 25 84 00 00 00 00 00 02 00 00 00 00 ... %...........
0x19E2FE 00 19 88 DC 00 00 00 00 00 20 25 C4 00 00 85 EC ......... %.....
0x19E30E 00 19 88 DC 00 00 00 05 ........
UPCs registers and stack
D0 = 0x00000000 A0 = 0x00307F09
D1 = 0x00000000 A1 = 0x0002E28C
D2 = 0x00080104 A2 = 0x00201334
D3 = 0x00000001 A3 = 0x00200D5E
D4 = 0x00000003 A4 = 0x002018B8
D5 = 0xFFFF0000 A5 = 0x002026D2
D6 = 0x00002014 A6 = 0x00200CF8
D7 = 0x00000000 A7 = 0x002057F8
Error Code = 0x0001
Trap Offset = 0x0000
Return address = 0x0002C83A
68Ks Status Register = 0x2700
Following are 30 words of stack data in hex
2010 0002 B36E 0002 E288 0002 ABD2 0000 0000 0000 0000 FFFB FF00 0018 0972
0020 842A 0020 5842 2000 0002 C4D8 0019 B75E 0000 1BF8 000B 0000 0000 0020
Raw Data of above
0x19E316 00 04 00 00 00 00 00 00 00 00 00 08 01 04 00 00 ................
0x19E326 00 01 00 00 00 03 FF FF 00 00 00 00 20 14 00 00 ............ ...
0x19E336 00 00 00 30 7F 09 00 02 E2 8C 00 20 13 34 00 20 ...0....... .4.
0x19E346 0D 5E 00 20 18 B8 00 20 26 D2 00 20 0C F8 00 20 .^. ... &.. ...
0x19E356 57 F8 00 01 00 00 00 02 C8 3A 27 00 20 10 00 02 W........:'. ...
0x19E366 B3 6E 00 02 E2 88 00 02 AB D2 00 00 00 00 00 00 .n..............
0x19E376 00 00 FF FB FF 00 00 18 09 72 00 20 84 2A 00 20 .........r. .*.
0x19E386 58 42 20 00 00 02 C4 D8 00 19 B7 5E 00 00 1B F8 XB ........^....
0x19E396 00 0B 00 00 00 00 00 20 .......
=============================================================================
Extended data for UPA valid flag: AAAA
Number of saved UPA tasks: 22
Extended data for UPB valid flag: BBBB
Number of saved UPB tasks: 10
Extended data for UPC valid flag: CCCC
Number of saved UPC tasks: 15
Data format: 0100
Miscellaneous variables:
07 DC 00 0A 00 03 00 05 00 01 00 0D
=============================================================================
UPA saved tasks and stack data:
Task Control Block entry #0
tbrsv1[0]: 7401E400
tbrsv1[1]: E800EC00
tbext: F0100817
tbpri: 0
tbid: 99
tbstat: 7402
tbd0: E800F010
tbd1: 8170099
tbd2: 7404E400
tbd3: F0100817
tbd4: 9A7407
tbd5: E800F01C
tba0: 74020817
tba1: 997407
tba2: F01C7408
tba3: 817009A
tbssp: 7400E800
tbusp: F01C7408
tbstack: 8170099
tbflags: 740A
tbrsv2[0]: F01C
tbrsv2[1]: 7404
tbrsv2[2]: 817
tbrsv2[3]: 9A
tbrsv2[4]: 7400
TCB #0 stack (176 bytes)
0x7400E800 E8 00 F0 1C 74 06 08 17 00 9B 74 00 E4 00 F0 7E
0x7400E810 73 F7 08 17 00 FF E0 13 80 D5 EC 00 F0 1C 74 0F
0x7400E820 08 17 00 9C 74 09 E8 00 F0 10 08 17 00 9C 74 0B
0x7400E830 E4 00 F0 7E 73 F4 08 17 00 FF E0 13 80 D5 F0 10
0x7400E840 08 17 00 9D 74 00 EC 00 F0 12 08 17 00 9C 74 0A
0x7400E850 E8 00 89 8A E4 00 F0 7E 73 F3 08 17 00 FF E0 01
0x7400E860 80 04 E0 13 80 D5 F0 10 08 17 00 96 78 07 00 D1
0x7400E870 8C 81 EC 00 F0 7E 73 F1 08 17 00 FF E8 00 E0 06
0x7400E880 A9 91 E0 01 80 04 E0 13 80 D5 F0 10 08 17 00 99
0x7400E890 74 01 F0 10 08 17 00 9A 74 06 E0 02 98 C3 EC 00
0x7400E8A0 F0 7E 73 EF 08 17 00 FF E8 00 E0 06 AA 91 E0 13
Task Control Block entry #1
tbrsv1[0]: 80D5F010
tbrsv1[1]: 81700FF
tbext: 7402EC00
tbpri: F0
tbid: D4
tbstat: 2817
tbd0: 912816
tbd1: 337414
tbd2: E800F0D4
tbd3: 28170091
tbd4: 281400D5
tbd5: 7414E800
tba0: F02C0817
tba1: FFE800
tba2: EC00F010
tba3: 8170092
tbssp: 7827000F
tbusp: F07E73FF
tbstack: 8170092
tbflags: E800
tbrsv2[0]: F022
tbrsv2[1]: 817
tbrsv2[2]: 92
tbrsv2[3]: 7401
tbrsv2[4]: 817
TCB #1 stack (176 bytes)
0x7827000F 00 92 E4 00 E8 00 F0 2C 08 17 00 9D E8 00 E0 07
0x7827001F A2 E9 E0 0F 84 D1 E0 07 90 D3 F0 18 08 17 00 FF
0x7827002F 74 00 EC 00 E0 08 86 34 F0 86 F0 64 18 08 00 E9
0x7827003F 7C 87 16 00 00 00 60 10 F0 54 18 08 00 E7 60 10
0x7827004F F0 8E E8 00 E0 07 92 E9 E4 00 FF C2 07 D2 EC 00
0x7827005F F0 7E 74 01 08 17 00 FF E8 00 E0 07 A0 D3 E0 0F
0x7827006F 94 D1 F0 10 08 17 00 FF 74 01 F0 2C 08 17 00 FF
0x7827007F E0 07 80 D3 F0 30 08 0B 00 37 EC 00 E0 0B 8D 37
0x7827008F E8 00 E0 0F 94 D1 E4 00 E0 07 B0 D3 F0 88 E0 04
0x7827009F CA 88 F0 10 08 17 00 FE 74 02 E0 13 C0 D7 E0 13
0x782700AF 80 D7 F0 12 08 17 00 4E 74 10 F0 7E 73 FD 08 17
Task Control Block entry #2
tbrsv1[0]: FEE013
tbrsv1[1]: 80D7F01C
tbext: 740A0817
tbpri: 0
tbid: 50 COPRO slow PCCC task
tbstat: 7400
tbd0: F01C7467
tbd1: 8170050
tbd2: 7464F07E
tbd3: 73FA0817
tbd4: FEE013
tbd5: 80D7F01C
tba0: 74080817
tba1: 517400
tba2: F01C746B
tba3: 8170051
tbssp: 7464F07E
tbusp: 73F90817
tbstack: FEE013
tbflags: 80D7
tbrsv2[0]: F01C
tbrsv2[1]: 7406
tbrsv2[2]: 817
tbrsv2[3]: 52
tbrsv2[4]: 7400
TCB #2 stack (176 bytes)
0x7464F07E F0 7E 73 F8 08 17 00 FE E0 13 80 D7 F0 1C 74 02
0x7464F08E 08 17 00 53 73 FE F0 7E 73 F7 08 17 00 FE E0 13
0x7464F09E 80 D7 F0 10 08 17 00 FE 74 02 EC 00 F0 2C 08 17
0x7464F0AE 00 FE E8 00 F0 22 08 17 00 4C 74 01 08 17 00 4C
0x7464F0BE E8 00 F0 D4 28 17 00 4B 28 14 00 8F 74 28 E8 00
0x7464F0CE E0 13 C1 D7 E0 13 81 D7 EC 00 F0 1C 74 65 08 17
0x7464F0DE 00 50 74 67 EC 00 F0 22 08 17 00 50 74 8C 08 0F
0x7464F0EE 00 EF E8 00 F0 24 08 17 00 51 74 64 08 0F 00 0F
0x7464F0FE E4 00 E8 00 F0 1C 74 01 08 17 00 50 74 09 F0 22
0x7464F10E 08 17 00 50 74 E6 08 0F 00 EF E8 00 F0 1C 74 01
0x7464F11E 08 17 00 50 74 09 F0 7E 08 17 00 51 08 0F 00 0F
Task Control Block entry #3
tbrsv1[0]: E800F084
tbrsv1[1]: F024080F
tbext: F7401
tbpri: 60
tbid: 0 unused 0
tbstat: F026
tbd0: 6000744B
tbd1: 6000F024
tbd2: 8170052
tbd3: 74016002
tbd4: F0266002
tbd5: 740F6002
tba0: F0226000
tba1: 60026000
tba2: F0226000
tba3: 7401080F
tbssp: F0F08E
tbusp: E01381D7
tbstack: F0D42814
tbflags: 97
tbrsv2[0]: 4804
tbrsv2[1]: 0
tbrsv2[2]: 80F
tbrsv2[3]: EF
tbrsv2[4]: 80F
TCB #3 stack (176 bytes)
0xF0F08E 00 F0 74 0F E0 04 CB 88 F0 10 08 17 00 FD 74 02
0xF0F09E E0 13 C0 DA E0 13 80 DA EC 00 F0 1C 74 0A 08 17
0xF0F0AE 00 3C 74 00 F0 1C 74 68 08 17 00 3C 74 64 E8 00
0xF0F0BE F0 1C 74 65 08 17 00 3D 74 6A F0 1C 74 68 08 17
0xF0F0CE 00 3C 74 64 E4 00 F0 7E 73 FA 08 17 00 FD E0 13
0xF0F0DE 80 DA EC 00 F0 1C 74 08 08 17 00 3D 74 00 F0 1C
0xF0F0EE 74 6B 08 17 00 3D 74 64 E8 00 F0 1C 74 65 08 17
0xF0F0FE 00 3C 74 67 F0 1C 74 6B 08 17 00 3D 74 64 E4 00
0xF0F10E F0 7E 73 F9 08 17 00 FD E0 13 80 DA F0 1C 74 06
0xF0F11E 08 17 00 3E 74 00 F0 7E 73 F8 08 17 00 FD E0 13
0xF0F12E 80 DA EC 00 F0 1C 74 0A 08 17 00 3F 74 00 F0 1C
Task Control Block entry #4
tbrsv1[0]: 74680817
tbrsv1[1]: 3F7464
tbext: E800F01C
tbpri: 74
tbid: 65
tbstat: 817
tbd0: 40746A
tbd1: F01C7468
tbd2: 817003F
tbd3: 7464E400
tbd4: F07E73F7
tbd5: 81700FD
tba0: E01380DA
tba1: EC00F01C
tba2: 74080817
tba3: 407400
tbssp: F01C746B
tbusp: 8170040
tbstack: 7464E800
tbflags: F01C
tbrsv2[0]: 7465
tbrsv2[1]: 817
tbrsv2[2]: 3F
tbrsv2[3]: 7467
tbrsv2[4]: F01C
TCB #4 stack (176 bytes)
0xF01C746B 74 6B 08 17 00 40 74 64 E4 00 F0 7E 73 F6 08 17
0xF01C747B 00 FD E0 13 80 DA F0 1C 74 06 08 17 00 41 74 00
0xF01C748B F0 7E 73 F5 08 17 00 FD E0 13 80 DA F0 1C 74 03
0xF01C749B 08 17 00 42 74 00 F0 7E 73 F4 08 17 00 FD E0 13
0xF01C74AB 80 DA F0 10 08 17 00 FD 74 02 EC 00 F0 2C 08 17
0xF01C74BB 00 FD E8 00 F0 22 08 17 00 38 74 01 08 17 00 38
0xF01C74CB E8 00 F0 D4 28 17 00 37 28 14 00 7B 74 14 E8 00
0xF01C74DB F0 D4 28 14 00 80 28 08 00 1B 74 06 E8 00 F0 7E
0xF01C74EB 08 14 00 86 08 08 00 22 E8 00 E0 13 C1 DA E0 13
0xF01C74FB 81 DA F0 80 74 41 F0 88 E0 04 C4 89 F0 10 08 17
0xF01C750B 00 F7 74 02 E0 13 C0 D8 E0 13 80 D8 F0 12 08 16
Task Control Block entry #5
tbrsv1[0]: C27410
tbrsv1[1]: F07E73FC
tbext: 81700F7
tbpri: E0
tbid: 13 STI Task
tbstat: 80D8
tbd0: F01C7407
tbd1: 81600C4
tbd2: 7400F07E
tbd3: 73FA0817
tbd4: F7E013
tbd5: 80D8F010
tba0: 81700F7
tba1: 7402EC00
tba2: F02C0817
tba3: F7E800
tbssp: F0D42816
tbusp: BF2814
tbstack: 37406
tbflags: E800
tbrsv2[0]: F022
tbrsv2[1]: 816
tbrsv2[2]: C0
tbrsv2[3]: 7401
tbrsv2[4]: 816
TCB #5 stack (176 bytes)
0xF0D42816 00 C0 E8 00 E0 13 C1 D8 E0 13 81 D8 EC 00 F0 10
0xF0D42826 08 14 00 08 74 01 E0 13 C2 D8 E8 00 F0 10 08 14
0xF0D42836 00 08 74 02 E0 13 C3 D8 E8 00 F0 10 08 14 00 08
0xF0D42846 74 03 E0 13 C4 D8 E8 00 F0 10 08 14 00 08 74 04
0xF0D42856 E0 07 80 E9 E0 07 91 E9 E0 13 C5 D8 EC 00 E0 13
0xF0D42866 84 D8 E8 00 86 F4 E4 00 E0 07 80 E9 E0 07 92 E9
0xF0D42876 EC 00 E0 07 A2 E9 E8 00 F0 7E 74 96 07 FF F0 88
0xF0D42886 E0 04 CE 89 F0 10 08 17 00 F6 74 02 E0 13 C0 D9
0xF0D42896 E0 13 80 D9 F0 12 08 16 00 AE 74 00 F0 7E 73 FC
0xF0D428A6 08 17 00 F6 E0 13 80 D9 F0 1C 74 05 08 16 00 B0
0xF0D428B6 74 00 F0 7E 73 FA 08 17 00 F6 E0 13 80 D9 F0 10
Task Control Block entry #6
tbrsv1[0]: 81700F6
tbrsv1[1]: 7402EC00
tbext: F02C0817
tbpri: 0
tbid: F6
tbstat: E800
tbd0: F0D42816
tbd1: AB2813
tbd2: EF7406
tbd3: E800F022
tbd4: 81600AC
tbd5: 74010816
tba0: ACE800
tba1: E013C1D9
tba2: E01381D9
tba3: EC00F010
tbssp: 81300F4
tbusp: 7401E013
tbstack: C2D9E800
tbflags: F010
tbrsv2[0]: 813
tbrsv2[1]: F4
tbrsv2[2]: 7402
tbrsv2[3]: E013
tbrsv2[4]: C3D9
TCB #6 stack (176 bytes)
0x81300F4 E8 00 F0 10 08 13 00 F4 74 03 E0 13 C4 D9 E8 00
0x8130104 F0 10 08 13 00 F4 74 04 E0 13 C5 D9 F0 88 E0 04
0x8130114 C0 8D E0 07 80 D4 F0 7E 74 01 08 18 00 03 E0 07
0x8130124 80 E2 F0 7E 74 02 08 18 00 03 E0 07 80 E9 EC 00
0x8130134 E0 05 81 E1 F0 7E 74 04 08 18 00 03 E8 00 E0 05
0x8130144 82 E1 F0 7E 74 05 08 18 00 03 E0 06 88 F4 E0 18
0x8130154 C0 04 85 8B EC 00 83 8A E8 00 81 8A E4 00 E0 18
0x8130164 C0 05 9C 81 E0 18 C0 06 8D 81 E0 18 C1 06 98 81
0x8130174 9B 81 E0 18 C0 07 EC 00 89 81 E8 00 8A 81 E4 00
0x8130184 E0 18 C1 07 8E 81 E0 18 C4 07 8F 81 E0 18 C5 07
0x8130194 E0 08 8E 31 F4 C2 07 D3 E0 07 C5 D3 E0 08 8A 2B
Task Control Block entry #7
tbrsv1[0]: F6C207D3
tbrsv1[1]: E007C7D3
tbext: EC00E008
tbpri: 8C
tbid: 33 CNET async BT request task
tbstat: E800
tbd0: E0088634
tbd1: E400F8C2
tbd2: 7D3E007
tbd3: C9D3E001
tbd4: 80049981
tbd5: 9A81EC00
tba0: F0120816
tba1: 387401
tba2: F0120816
tba3: 397402
tbssp: E800E008
tbusp: 9E2CE008
tbstack: 982DE008
tbflags: 922E
tbrsv2[0]: E400
tbrsv2[1]: FAC2
tbrsv2[2]: 7D3
tbrsv2[3]: E007
tbrsv2[4]: CBD3
TCB #7 stack (176 bytes)
0xE800E008 E0 01 80 04 9E 81 9F 81 EC 00 F0 12 08 16 00 38
0xE800E018 74 0A F0 12 08 16 00 39 74 02 E8 00 E0 08 9E 2C
0xE800E028 E0 08 98 2D E0 08 92 2E E4 00 FC C2 07 D3 E0 07
0xE800E038 CD D3 E0 07 87 D3 EC 00 F0 D4 28 16 00 38 28 18
0xE800E048 00 93 74 06 E8 00 F0 7E 74 01 08 18 00 99 E8 00
0xE800E058 F0 7E 08 16 00 3F 08 18 00 9A E8 00 F0 7E 08 16
0xE800E068 00 40 08 18 00 9B E0 07 85 D3 EC 00 F0 D4 28 16
0xE800E078 00 38 28 18 00 93 74 06 E8 00 F0 7E 74 02 08 18
0xE800E088 00 99 E8 00 F0 7E 08 16 00 3F 08 18 00 9A E8 00
0xE800E098 F0 7E 08 16 00 40 08 18 00 9B E0 07 89 D3 EC 00
0xE800E0A8 F0 D4 28 16 00 38 28 18 00 93 74 06 E8 00 F0 7E
Task Control Block entry #8
tbrsv1[0]: 74030818
tbrsv1[1]: 99E800
tbext: F07E0816
tbpri: 0
tbid: 3F CNET PCCC BT task
tbstat: 818
tbd0: 9AE800
tbd1: F07E0816
tbd2: 400818
tbd3: 9BE007
tbd4: 8BD3F012
tbd5: 81B0087
tba0: 7400EC00
tba1: F07E7401
tba2: 8180093
tba3: E800F07E
tbssp: 74020818
tbusp: 94E800
tbstack: F07E7401
tbflags: 818
tbrsv2[0]: 95
tbrsv2[1]: E800
tbrsv2[2]: F0D6
tbrsv2[3]: 2818
tbrsv2[4]: 96
TCB #8 stack (176 bytes)
0x74020818 74 00 74 03 E8 00 F0 7E 74 03 08 18 00 99 E8 00
0x74020828 F0 7E 08 1B 00 87 08 18 00 9A E8 00 F0 7E 78 11
0x74020838 00 31 08 18 00 9B E8 00 F0 D6 28 1B 00 86 74 00
0x74020848 74 03 E0 07 8D D3 F0 12 08 2E 00 05 74 00 EC 00
0x74020858 F0 7E 74 0A 08 18 00 93 E8 00 F0 7E 74 02 08 18
0x74020868 00 94 E8 00 F0 7E 74 01 08 18 00 95 E8 00 F0 D6
0x74020878 28 18 00 96 74 00 74 03 E8 00 F0 7E 74 03 08 18
0x74020888 00 99 E8 00 F0 7E 08 2E 00 05 08 18 00 9A E8 00
0x74020898 F0 7E 78 11 00 31 08 18 00 9B E8 00 F0 D6 28 2E
0x740208A8 00 04 74 00 74 03 F0 10 08 18 00 11 74 00 F0 12
0x740208B8 08 18 00 67 74 00 EC 00 F0 D4 28 18 00 61 28 18
Task Control Block entry #9
tbrsv1[0]: B740A
tbrsv1[1]: E800F0D6
tbext: 28180061
tbpri: 74
tbid: 0 unused 0
tbstat: 740A
tbd0: F0100818
tbd1: 677400
tbd2: F0120818
tbd3: 717400
tbd4: EC00F0D4
tbd5: 2818006B
tba0: 28180061
tba1: 740AE800
tba2: F0D62818
tba3: 6B7400
tbssp: 740AF010
tbusp: 8180071
tbstack: 7400F012
tbflags: 818
tbrsv2[0]: 7B
tbrsv2[1]: 7400
tbrsv2[2]: EC00
tbrsv2[3]: F0D4
tbrsv2[4]: 2818
TCB #9 stack (176 bytes)
0x740AF010 00 75 28 18 00 6B 74 0A E8 00 F0 D6 28 18 00 75
0x740AF020 74 00 74 0A F0 10 08 18 00 7B 74 00 F0 12 08 18
0x740AF030 00 85 74 00 EC 00 F0 D4 28 18 00 7F 28 18 00 75
0x740AF040 74 0A E8 00 F0 D6 28 18 00 7F 74 00 74 0A F0 10
0x740AF050 08 18 00 85 74 00 F0 12 08 18 00 8F 74 00 EC 00
0x740AF060 F0 D4 28 18 00 89 28 18 00 7F 74 0A E8 00 F0 D6
0x740AF070 28 18 00 89 74 00 74 0A F0 10 08 18 00 8F 74 00
0x740AF080 F0 12 08 18 00 99 74 00 EC 00 F0 D4 28 18 00 93
0x740AF090 28 18 00 89 74 0A E8 00 F0 D6 28 18 00 93 74 00
0x740AF0A0 74 0A EC 00 F0 68 18 08 00 E1 7C 82 20 00 00 00
0x740AF0B0 08 18 00 36 E8 00 F0 7C 18 08 00 E5 08 18 00 37
Task Control Block entry #10
tbrsv1[0]: E800F07C
tbrsv1[1]: 180800E7
tbext: 8180038
tbpri: F0
tbid: D4
tbstat: 268C
tbd0: 28180051
tbd1: 7410E001
tbd2: 8004E002
tbd3: 88C3F0D6
tbd4: 281C00B2
tbd5: 74007403
tba0: 99819A81
tba1: EE00F0D6
tba2: 281B0086
tba3: 74007403
tbssp: F088F0D4
tbusp: 284600CE
tbstack: 281A0062
tbflags: 7406
tbrsv2[0]: F010
tbrsv2[1]: 817
tbrsv2[2]: F5
tbrsv2[3]: 7402
tbrsv2[4]: E01A
TCB #10 stack (176 bytes)
0xF088F0D4 C0 5F E0 1A 80 5F F0 1C 78 0B 00 B8 08 16 00 9C
0xF088F0E4 78 07 00 BC F0 7E 73 FA 08 17 00 F5 E0 1A 80 5F
0xF088F0F4 F0 1C 74 0D 08 16 00 9D 74 00 F0 7E 73 F9 08 17
0xF088F104 00 F5 E0 1A 80 5F F0 1C 74 20 08 16 00 9E 74 00
0xF088F114 F0 7E 73 F8 08 17 00 F5 E0 1A 80 5F F0 1C 74 18
0xF088F124 08 16 00 9F 73 FF F0 7E 73 F7 08 17 00 F5 E0 1A
0xF088F134 80 5F F0 1C 74 3C 08 16 00 A0 73 FF F0 7E 73 F6
0xF088F144 08 17 00 F5 E0 1A 80 5F F0 1C 74 3C 08 16 00 A1
0xF088F154 73 FF F0 7E 73 F5 08 17 00 F5 E0 1A 80 5F F0 10
0xF088F164 08 17 00 F5 74 02 EC 00 E0 1A C1 5F E8 00 F0 2C
0xF088F174 08 17 00 F5 E8 00 F0 D4 28 16 00 9C 28 1A 00 58
Task Control Block entry #11
tbrsv1[0]: 7406E800
tbrsv1[1]: F0D42816
tbext: 972813
tbpri: 0
tbid: DB
tbstat: 740B
tbd0: E01A815F
tbd1: EC00F022
tbd2: 84600D3
tbd3: 81100E1
tbd4: 81A0060
tbd5: E800F024
tba0: 84600D3
tba1: 8120013
tba2: 81A0061
tba3: E01AB25F
tbssp: E01A815F
tbusp: EC00F016
tbstack: 81A0061
tbflags: 81A
tbrsv2[0]: 5D
tbrsv2[1]: E800
tbrsv2[2]: F014
tbrsv2[3]: 81A
tbrsv2[4]: 60
TCB #11 stack (176 bytes)
0xE01A815F 08 1A 00 5D E4 00 E0 1A A2 5F E0 1A 81 5F EC 00
0xE01A816F F0 12 08 1A 00 58 08 46 00 CE E8 00 F0 12 08 1A
0xE01A817F 00 59 08 46 00 CF E8 00 F0 12 08 1A 00 5A 08 46
0xE01A818F 00 D0 E4 00 E0 1A A2 5F E0 1A 81 5F EC 00 F0 12
0xE01A819F 08 1A 00 5B 08 46 00 D1 E8 00 F0 12 08 1A 00 5C
0xE01A81AF 08 46 00 D2 E4 00 E0 1A A2 5F E0 1A 82 5F EC 00
0xE01A81BF F0 D4 28 1A 00 58 28 46 00 CE 74 06 E8 00 F0 D4
0xE01A81CF 28 1A 00 58 28 1A 00 6C 74 06 F0 D4 28 46 00 CE
0xE01A81DF 28 19 00 1A 74 06 F0 7E 08 16 00 9B 08 10 00 02
0xE01A81EF E0 01 8E 41 E0 19 C0 20 EC 00 E0 1A 82 5F E8 00
0xE01A81FF E0 01 8E 41 E8 00 E0 01 8D 00 E4 00 F0 30 01 41
Task Control Block entry #12
tbrsv1[0]: F088F088
tbrsv1[1]: E0018D00
tbext: E400F030
tbpri: 1
tbid: 41 CNET SMAC task
tbstat: F088
tbd0: 0
tbd1: 7
tbd2: 0
tbd3: 20
tbd4: 1
tbd5: 2FFF0000
tba0: 20208E
tba1: 3D4CC
tba2: 1FD02
tba3: 3D4C8
tbssp: 2047CE
tbusp: 0
tbstack: 20483C
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 210E
tbrsv2[2]: 20
tbrsv2[3]: 200E
tbrsv2[4]: 0
TCB #12 stack (176 bytes)
0x2047CE 00 00 00 00 FF BD FF 00 00 03 D4 C8 00 20 84 2A
0x2047DE 00 20 48 38 20 00 00 01 FD 1E 00 00 00 21 00 00
0x2047EE 00 01 00 00 00 03 00 02 09 60 00 07 00 00 00 00
0x2047FE 00 00 00 20 00 01 00 20 48 36 00 00 00 21 00 00
0x20480E 00 01 00 00 00 03 2F FF 00 00 00 00 00 00 FF BD
0x20481E FF 00 00 03 D4 CC 00 03 D4 CE 00 03 D4 C8 D4 C8
0x20482E 00 00 00 01 00 20 04 1C 20 00 00 20 04 1C DE AD
0x20483E BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20484E 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20485E 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20486E 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #13
tbrsv1[0]: 202D9C
tbrsv1[1]: 202D9C
tbext: 0
tbpri: 23
tbid: 22 Remote read request task
tbstat: 40
tbd0: 0
tbd1: 3
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: 2FFF0000
tba0: 204BEA
tba1: 3D4D4
tba2: 3D4D6
tba3: 3D4D0
tbssp: 204BA2
tbusp: 0
tbstack: 204BF2
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 208E
tbrsv2[2]: 20
tbrsv2[3]: 1F8E
tbrsv2[4]: 0
TCB #13 stack (176 bytes)
0x204BA2 00 00 00 00 FF BD FF 00 00 03 D4 D0 00 20 84 2A
0x204BB2 00 20 4B EE 20 00 00 01 FC 5A 00 00 00 22 00 01
0x204BC2 A4 7C 00 03 00 00 00 00 00 20 4B EA 00 00 00 22
0x204BD2 00 00 00 01 00 00 00 03 00 03 D4 D4 00 03 D4 D6
0x204BE2 D4 D0 00 20 84 2A 00 20 00 00 20 00 00 20 04 1C
0x204BF2 DE AD BE EF 00 00 00 00 00 00 00 00 00 00 00 00
0x204C02 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204C12 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204C22 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204C32 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204C42 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #14
tbrsv1[0]: 201D8E
tbrsv1[1]: 202B26
tbext: 0
tbpri: 41
tbid: 23 Make PCL message task
tbstat: 200
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 48000000
tbd4: 1
tbd5: 2FFF0000
tba0: 201A8E
tba1: 3D52C
tba2: 3D52E
tba3: 3D528
tbssp: 207466
tbusp: 0
tbstack: 2074C4
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1B0E
tbrsv2[2]: 20
tbrsv2[3]: 1A0E
tbrsv2[4]: 0
TCB #14 stack (176 bytes)
0x207466 00 00 00 00 FF BD FF 00 00 03 D5 28 00 20 84 2A
0x207476 00 20 74 C0 20 00 00 01 FD 1E 00 00 00 23 00 00
0x207486 00 01 00 00 00 03 00 03 13 A2 00 01 00 00 00 00
0x207496 48 00 00 00 00 01 00 20 74 B6 00 00 00 23 00 00
0x2074A6 00 01 00 03 D5 2C 00 03 D5 2E 00 03 D5 28 D5 28
0x2074B6 00 20 84 2A 00 20 04 1C 20 00 00 20 04 1C DE AD
0x2074C6 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2074D6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2074E6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2074F6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207506 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #15
tbrsv1[0]: 202A46
tbrsv1[1]: 202A46
tbext: 0
tbpri: 40
tbid: 24 Serial port get buffer task
tbstat: 200
tbd0: 0
tbd1: 8
tbd2: 0
tbd3: 1
tbd4: 0
tbd5: 2FFF0000
tba0: 201E8E
tba1: 3D4EC
tba2: 3D4EE
tba3: 3D4E8
tbssp: 2056C4
tbusp: 0
tbstack: 205714
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1F0E
tbrsv2[2]: 20
tbrsv2[3]: 1E0E
tbrsv2[4]: 0
TCB #15 stack (176 bytes)
0x2056C4 00 00 00 00 FF BD FF 00 00 03 D4 E8 00 20 84 2A
0x2056D4 00 20 57 10 20 00 00 01 FD 1E 00 00 00 24 00 00
0x2056E4 00 01 00 00 00 03 00 01 54 F8 00 08 00 00 00 00
0x2056F4 00 00 00 01 00 00 00 20 57 0E 00 00 00 24 00 00
0x205704 00 01 00 03 D4 EC 00 03 D4 EE 20 00 00 20 04 1C
0x205714 DE AD BE EF 00 00 00 00 00 00 00 00 00 00 00 00
0x205724 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205734 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205744 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205754 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205764 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #16
tbrsv1[0]: 2029E6
tbrsv1[1]: 2029E6
tbext: 0
tbpri: 3F
tbid: 25 Serial port modem control task
tbstat: 200
tbd0: 0
tbd1: B
tbd2: 0
tbd3: E
tbd4: 0
tbd5: 2FFF00FD
tba0: 209C7A
tba1: 209C7A
tba2: 209C54
tba3: 209C55
tbssp: 205A54
tbusp: 0
tbstack: 205ACA
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1E8E
tbrsv2[2]: 20
tbrsv2[3]: 1D8E
tbrsv2[4]: 0
TCB #16 stack (176 bytes)
0x205A54 00 00 00 00 FF BD FF 00 00 20 9C 7A 00 20 84 2A
0x205A64 00 20 5A A0 20 00 00 01 FD 1E 00 00 00 00 00 00
0x205A74 00 01 00 00 00 12 00 01 39 62 00 0B 00 00 00 00
0x205A84 00 00 00 0E 00 00 00 20 5A 9E 00 00 00 01 00 00
0x205A94 00 B2 00 00 00 12 00 16 00 00 9C 54 00 20 5A C6
0x205AA4 00 01 35 74 00 00 00 25 00 00 00 01 00 00 00 03
0x205AB4 2F FF 00 00 00 03 D4 F4 00 03 D4 F6 00 03 D4 F0
0x205AC4 00 00 00 20 04 1C DE AD BE EF 00 00 00 00 00 00
0x205AD4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205AE4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205AF4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #17
tbrsv1[0]: 202966
tbrsv1[1]: 202966
tbext: 0
tbpri: 1E
tbid: 27 EEPROM task
tbstat: 200
tbd0: 0
tbd1: F
tbd2: 0
tbd3: F
tbd4: 0
tbd5: 2FFF0000
tba0: 201A0E
tba1: 20A968
tba2: 3D536
tba3: 3D530
tbssp: 2077D4
tbusp: 0
tbstack: 20787A
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1A8E
tbrsv2[2]: 20
tbrsv2[3]: 198E
tbrsv2[4]: 0
TCB #17 stack (176 bytes)
0x2077D4 00 00 00 00 FF BD FF 00 00 03 D5 30 00 20 84 2A
0x2077E4 00 20 78 76 20 00 00 01 FD 1E 00 00 00 27 00 00
0x2077F4 00 01 00 00 00 03 00 03 A4 A6 00 0F 00 00 00 00
0x207804 00 00 00 0F 00 00 00 20 78 74 00 00 00 27 00 00
0x207814 00 01 00 00 00 03 2F FF 00 00 00 00 00 00 FF BD
0x207824 FF 00 00 03 D5 34 00 03 D5 36 00 03 D5 30 00 01
0x207834 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207844 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207854 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207864 FF BD FF 00 00 03 D5 30 00 20 84 2A 00 20 04 1C
0x207874 20 00 00 20 04 1C DE AD BE EF 00 00 00 00 00 00
Task Control Block entry #18
tbrsv1[0]: 202DC8
tbrsv1[1]: 202DC8
tbext: 0
tbpri: 23
tbid: 28 Rung cache remote mod task
tbstat: 40
tbd0: 0
tbd1: 8
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: 2FFF0000
tba0: 207C26
tba1: 3ACA6
tba2: 3D53E
tba3: 3D538
tbssp: 207BF2
tbusp: 0
tbstack: 207C30
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1A0E
tbrsv2[2]: 20
tbrsv2[3]: 190E
tbrsv2[4]: 0
TCB #18 stack (176 bytes)
0x207BF2 00 00 00 00 FF BD FF 00 00 03 D5 38 00 20 84 2A
0x207C02 00 20 7C 2C 20 00 00 01 FC 5A 00 00 00 28 00 02
0x207C12 7C 9E 00 08 00 00 00 00 00 20 7C 26 00 03 D5 3C
0x207C22 00 20 84 2A 00 00 04 1C 20 00 00 20 04 1C DE AD
0x207C32 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C42 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C52 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C62 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C72 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C82 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C92 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #19
tbrsv1[0]: 20230E
tbrsv1[1]: 20230E
tbext: 0
tbpri: 41
tbid: 29 COPRO interface task
tbstat: 0
tbd0: 0
tbd1: 19
tbd2: 0
tbd3: 7
tbd4: 0
tbd5: 2FFF0000
tba0: 2404A2
tba1: 207F8A
tba2: 207F86
tba3: 207F36
tbssp: 207FA8
tbusp: 0
tbstack: 207FE6
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 198E
tbrsv2[2]: 20
tbrsv2[3]: 188E
tbrsv2[4]: 0
TCB #19 stack (176 bytes)
0x207FA8 00 00 00 20 E6 AE 00 20 E6 B4 00 00 00 00 E6 AA
0x207FB8 00 01 00 20 04 1C 00 00 93 02 00 24 04 A2 00 00
0x207FC8 00 00 00 20 E5 D0 00 20 E6 A8 00 20 E6 A6 00 00
0x207FD8 91 F8 00 03 D5 44 00 03 D5 46 00 03 D5 40 DE AD
0x207FE8 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207FF8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208008 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208018 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208028 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208038 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208048 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #20
tbrsv1[0]: 20210E
tbrsv1[1]: 201A8E
tbext: 0
tbpri: 2F
tbid: 45 RIO IOT task
tbstat: 200
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 4000000
tbd4: 0
tbd5: 2FFF0000
tba0: 205E7A
tba1: 3ACA6
tba2: 3D4FE
tba3: 3D4F8
tbssp: 205E34
tbusp: 0
tbstack: 205E80
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1E0E
tbrsv2[2]: 20
tbrsv2[3]: 1D0E
tbrsv2[4]: 0
TCB #20 stack (176 bytes)
0x205E34 00 00 00 00 FF BD FF 00 00 03 D4 F8 00 20 84 2A
0x205E44 00 20 5E 7C 20 00 00 01 FD 1E 00 00 00 45 00 00
0x205E54 00 01 00 00 00 03 00 03 55 EA 00 01 00 00 00 00
0x205E64 04 00 00 00 00 00 00 20 5E 7A 00 00 00 45 00 00
0x205E74 00 01 00 03 D4 FC 00 00 00 20 04 1C DE AD BE EF
0x205E84 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205E94 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205EA4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205EB4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205EC4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205ED4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #21
tbrsv1[0]: 203038
tbrsv1[1]: 203038
tbext: 0
tbpri: 41
tbid: 50 COPRO slow PCCC task
tbstat: 40
tbd0: 0
tbd1: 32
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: 2FFF0000
tba0: 208396
tba1: 3ACA6
tba2: 240376
tba3: 240506
tbssp: 20835A
tbusp: 0
tbstack: 20839C
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 190E
tbrsv2[2]: 20
tbrsv2[3]: D74
tbrsv2[4]: 0
TCB #21 stack (176 bytes)
0x20835A 00 00 00 00 FF BD FF 00 00 24 03 76 00 20 84 2A
0x20836A 00 20 83 98 20 00 00 01 FC 5A 00 00 00 50 00 00
0x20837A 7F F8 00 32 00 00 00 00 00 20 83 96 00 03 D5 4C
0x20838A 00 03 D5 4E 00 03 D5 48 00 20 04 1C 00 05 00 20
0x20839A 04 1C 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083AA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083BA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083CA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083DA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083EA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083FA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Current task (COPRO interface task) stack (506 bytes):
0x207DF0 00 02 5E 86 00 20 7E C4 00 20 7E CE 00 20 7E 38
0x207E00 08 7E 00 20 7E 3E 00 00 00 00 00 00 08 7E 00 00
0x207E10 00 02 2F FF 08 82 00 00 00 00 FF BD 00 00 00 20
0x207E20 7E CE 00 20 7E DE 00 20 7E E0 7E CE 00 20 84 2A
0x207E30 00 20 7E 86 00 24 19 32 00 24 19 39 00 00 00 09
0x207E40 08 82 00 00 00 02 00 20 7E CE 00 02 03 04 00 20
0x207E50 7E 86 00 02 53 7C 00 20 7E C4 00 20 7E CE 00 20
0x207E60 7E 80 08 7E 00 20 7E 84 00 00 00 00 00 00 00 00
0x207E70 00 00 BF FF 00 00 00 00 00 19 CF 38 00 20 7F 86
0x207E80 00 00 BF FF 00 00 00 00 00 19 CF 38 00 20 2A 66
0x207E90 00 00 00 01 00 00 00 0F 00 19 CF 38 00 20 7F 86
0x207EA0 00 20 7E CC 00 20 2A 66 00 00 00 01 00 00 00 00
0x207EB0 00 19 CF 38 00 20 7F 86 00 03 7B E4 00 00 00 01
0x207EC0 00 00 00 07 00 20 84 08 00 20 7F 86 00 20 7F 18
0x207ED0 20 00 00 01 FB BE 00 00 00 16 00 00 00 58 00 20
0x207EE0 7F 86 00 03 C1 70 00 20 7F 0E 00 00 00 20 7F 0C
0x207EF0 00 00 00 50 00 00 00 FF 00 03 00 04 00 01 7F 91
0x207F00 00 24 04 B7 00 20 7D F0 00 04 00 01 00 00 00 29
0x207F10 00 41 00 00 00 20 7F 18 00 20 E4 0E 00 03 AC D0
0x207F20 00 00 00 C5 00 00 00 BF 00 20 7E EE 00 19 CF 38
0x207F30 00 03 B1 24 00 8A 00 10 20 09 00 00 00 C2 01 B4
0x207F40 00 00 00 20 7F 94 00 00 68 66 00 20 7F 94 00 00
0x207F50 66 C8 00 20 7F 86 00 00 00 29 00 00 00 01 00 00
0x207F60 00 03 2F FF 00 00 00 24 04 A2 00 24 04 3E 00 00
0x207F70 6B 10 00 20 84 2A 00 24 10 A6 20 00 00 00 00 21
0x207F80 00 24 21 B2 00 20 30 AE 00 04 00 01 01 01 00 00
0x207F90 00 24 04 A2 00 20 7F BA 00 00 7F 24 00 24 04 A2
0x207FA0 00 24 04 3E 00 00 00 00 00 00 00 20 E6 AE 00 20
0x207FB0 E6 B4 00 00 00 00 E6 AA 00 01 00 20 04 1C 00 00
0x207FC0 93 02 00 24 04 A2 00 00 00 00 00 20 E5 D0 00 20
0x207FD0 E6 A8 00 20 E6 A6 00 00 91 F8 00 03 D5 44 00 03
0x207FE0 D5 46 00 03 D5 40 DE AD BE EF
Interrupt stack (252 bytes):
0x207EE8 00 03 C1 C2 00 20 7F 14 00 00 00 50 00 00 00 FF
0x207EF8 00 03 00 04 00 01 7F 91 00 24 04 B7 00 20 7E E8
0x207F08 00 04 00 01 00 00 00 29 00 41 00 00 00 20 7F 18
0x207F18 00 20 E4 0E 00 03 AC D0 00 00 00 C5 00 00 00 BF
0x207F28 00 20 7E EE 00 19 CF 38 00 03 B1 24 00 8A 00 10
0x207F38 20 09 00 00 00 C2 01 B4 00 00 00 20 7F 94 00 00
0x207F48 68 66 00 20 7F 94 00 00 66 C8 00 20 7F 86 00 00
0x207F58 00 29 00 00 00 01 00 00 00 03 2F FF 00 00 00 24
0x207F68 04 A2 00 24 04 3E 00 00 6B 10 00 20 84 2A 00 24
0x207F78 10 A6 20 00 00 00 00 21 00 24 21 B2 00 20 30 AE
0x207F88 00 04 00 01 01 01 00 00 00 24 04 A2 00 20 7F BA
0x207F98 00 00 7F 24 00 24 04 A2 00 24 04 3E 00 00 00 00
0x207FA8 00 00 00 20 E6 AE 00 20 E6 B4 00 00 00 00 E6 AA
0x207FB8 00 01 00 20 04 1C 00 00 93 02 00 24 04 A2 00 00
0x207FC8 00 00 00 20 E5 D0 00 20 E6 A8 00 20 E6 A6 00 00
0x207FD8 91 F8 00 03 D5 44 00 03 D5 46 00 03
=============================================================================
UPB saved tasks and stack data:
Task Control Block entry #0
tbrsv1[0]: 20159C
tbrsv1[1]: 20159C
tbext: 0
tbpri: 14
tbid: 1 cp_control_processor task
tbstat: 0
tbd0: 0
tbd1: 0
tbd2: 33
tbd3: 105
tbd4: 1
tbd5: FFFFDFBF
tba0: 199214
tba1: 200428
tba2: 206C92
tba3: 1988B6
tbssp: 202576
tbusp: 0
tbstack: 20260A
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 582
tbrsv2[2]: 20
tbrsv2[3]: 151C
tbrsv2[4]: 0
TCB #0 stack (176 bytes)
0x202576 00 00 00 00 00 02 00 00 00 00 00 19 88 DC 00 00
0x202586 00 00 00 20 25 C4 00 00 85 EC 00 19 88 DC 00 00
0x202596 00 05 00 00 00 05 00 00 E3 FF FF FF DF BF DF 7E
0x2025A6 FF FF FD FF FB FF 00 20 04 28 00 20 6C 92 00 19
0x2025B6 88 B6 00 00 00 00 00 00 00 00 00 19 72 14 00 20
0x2025C6 25 E2 00 01 85 98 00 00 00 05 00 00 00 05 00 13
0x2025D6 00 00 00 19 C6 DC 00 01 75 AE 00 05 00 20 26 06
0x2025E6 00 01 81 54 00 05 00 00 00 01 00 00 00 01 00 00
0x2025F6 00 03 00 01 D5 48 00 01 D5 4A 00 01 D5 44 20 00
0x202606 00 20 04 1C DE AD BE EF 00 00 00 00 00 00 00 00
0x202616 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #1
tbrsv1[0]: 201C74
tbrsv1[1]: 201C74
tbext: 0
tbpri: A
tbid: 2 cp_shutdown_system task
tbstat: 200
tbd0: 0
tbd1: 0
tbd2: 0
tbd3: 800
tbd4: 1
tbd5: FFFFDFBF
tba0: 20151C
tba1: 18828
tba2: 19DE98
tba3: 1D54C
tbssp: 20294C
tbusp: 0
tbstack: 2029C0
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 159C
tbrsv2[2]: 20
tbrsv2[3]: 149C
tbrsv2[4]: 0
TCB #1 stack (176 bytes)
0x20294C DF 7E FF FF FD FF FB FF 00 01 D5 4C 00 20 04 2C
0x20295C 00 20 29 92 20 00 00 01 71 9C 00 00 00 00 00 00
0x20296C 00 01 00 00 00 03 00 01 88 52 00 00 00 00 00 00
0x20297C 00 00 08 00 00 01 00 20 29 8C 00 00 08 00 00 00
0x20298C 00 00 00 00 00 00 00 20 29 BC 00 01 8A B8 00 00
0x20299C 08 00 00 00 00 00 00 00 00 02 00 00 00 01 00 00
0x2029AC 00 03 00 01 D5 50 00 01 D5 52 00 20 04 1C 20 00
0x2029BC 00 20 04 1C DE AD BE EF 00 00 00 00 00 00 00 00
0x2029CC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2029DC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2029EC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #2
tbrsv1[0]: 20149C
tbrsv1[1]: 20149C
tbext: 0
tbpri: 41
tbid: 3 cp_diagnostics task
tbstat: 0
tbd0: 0
tbd1: 0
tbd2: 41
tbd3: 1
tbd4: 7
tbd5: AAAAAAAA
tba0: 20149C
tba1: 1D558
tba2: 1D55A
tba3: 210000
tbssp: 202D5C
tbusp: 0
tbstack: 202D76
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 151C
tbrsv2[2]: 20
tbrsv2[3]: 141C
tbrsv2[4]: 0
TCB #2 stack (176 bytes)
0x202D5C 00 00 00 00 C3 6D A7 CF 00 20 21 D4 00 04 00 00
0x202D6C 00 00 21 D4 20 00 00 01 9D 96 DE AD BE EF 00 00
0x202D7C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202D8C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202D9C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DAC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DBC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DCC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DDC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DEC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DFC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #3
tbrsv1[0]: 201D3A
tbrsv1[1]: 201D3A
tbext: 0
tbpri: B
tbid: 11 User Program Control Task
tbstat: 40
tbd0: 0
tbd1: D2560014
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 206E46
tba1: 206E3C
tba2: 1D56A
tba3: 1D564
tbssp: 2034A8
tbusp: 0
tbstack: 2034E2
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 141C
tbrsv2[2]: 20
tbrsv2[3]: 131C
tbrsv2[4]: 0
TCB #3 stack (176 bytes)
0x2034A8 DF 7E FF FF FD FF FB FF 00 20 6E 9A 00 20 04 2C
0x2034B8 00 20 34 DE 20 00 00 01 70 D8 00 00 00 03 00 00
0x2034C8 8F 30 00 14 00 00 00 00 00 20 34 DC 00 00 00 11
0x2034D8 00 01 D5 68 00 00 00 20 04 1C DE AD BE EF 00 00
0x2034E8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2034F8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203508 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203518 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203528 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203538 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203548 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #4
tbrsv1[0]: 201754
tbrsv1[1]: 201754
tbext: 0
tbpri: F
tbid: 12 PII Task
tbstat: 2
tbd0: 0
tbd1: 0
tbd2: 12
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 206E62
tba1: 1988B6
tba2: 198B34
tba3: 1D564
tbssp: 20436E
tbusp: 0
tbstack: 2043BA
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 121C
tbrsv2[2]: 20
tbrsv2[3]: 111C
tbrsv2[4]: 0
TCB #4 stack (176 bytes)
0x20436E DF 7E FF FF FD FF FB FF 00 18 8D 78 00 20 04 2C
0x20437E 00 20 43 B6 20 00 00 01 70 7E 00 00 A8 DC 00 20
0x20438E 6E 62 00 00 00 00 00 20 43 B4 00 00 00 12 00 00
0x20439E 00 01 00 00 00 03 FF FF DF BF DF 7E FF FF 00 20
0x2043AE 6E 3C 00 01 D5 6A 20 00 00 20 34 CC DE AD BE EF
0x2043BE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2043CE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2043DE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2043EE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2043FE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20440E 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #5
tbrsv1[0]: 201734
tbrsv1[1]: 201734
tbext: 0
tbpri: 10
tbid: 13 STI Task
tbstat: 2
tbd0: 0
tbd1: 0
tbd2: 13
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 206E5E
tba1: 1988B6
tba2: 198A08
tba3: 1D564
tbssp: 204728
tbusp: 0
tbstack: 204770
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 119C
tbrsv2[2]: 20
tbrsv2[3]: 582
tbrsv2[4]: 0
TCB #5 stack (176 bytes)
0x204728 DF 7E FF FF FD FF FB FF 00 18 8D 78 00 20 04 2C
0x204738 00 20 47 6C 20 00 00 01 70 7E 00 00 8D 6A 00 20
0x204748 6E 5E 00 00 00 00 00 20 47 6A 00 00 00 13 00 00
0x204758 00 01 00 00 00 03 FF FF DF BF 00 20 6E 3C 00 01
0x204768 D5 6A 20 00 00 20 34 CC 00 00 00 00 00 00 00 00
0x204778 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204788 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204798 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2047A8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2047B8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2047C8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #6
tbrsv1[0]: 201D76
tbrsv1[1]: 201D76
tbext: 0
tbpri: C
tbid: 14 System RTE Task
tbstat: 40
tbd0: 0
tbd1: 15
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 20131C
tba1: 1D570
tba2: 206E5A
tba3: 1D56C
tbssp: 203846
tbusp: 0
tbstack: 203898
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 139C
tbrsv2[2]: 20
tbrsv2[3]: 129C
tbrsv2[4]: 0
TCB #6 stack (176 bytes)
0x203846 DF 7E FF FF FD FF FB FF 00 01 D5 6C 00 20 04 2C
0x203856 00 20 38 94 20 00 00 01 70 D8 00 00 00 14 00 00
0x203866 9F 6A 00 15 00 00 00 00 00 20 38 92 00 01 D5 70
0x203876 00 01 D5 72 00 01 D5 6C DF 7E FF FF FD FF FB FF
0x203886 00 01 D5 6C 00 20 04 2C 00 20 04 1C 20 00 00 20
0x203896 04 1C DE AD BE EF 00 00 00 00 00 00 00 00 00 00
0x2038A6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2038B6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2038C6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2038D6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2038E6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #7
tbrsv1[0]: 201774
tbrsv1[1]: 201774
tbext: 0
tbpri: D
tbid: 15 User's RTE Task
tbstat: 2
tbd0: 0
tbd1: 0
tbd2: 15
tbd3: 1
tbd4: E3FF
tbd5: FFFFDFBF
tba0: 206D04
tba1: 130000
tba2: 198C60
tba3: 175AE
tbssp: 203FAC
tbusp: 0
tbstack: 204004
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 129C
tbrsv2[2]: 20
tbrsv2[3]: 119C
tbrsv2[4]: 0
TCB #7 stack (176 bytes)
0x203FAC DF 7E FF FF FD FF FB FF 00 19 88 B0 00 20 04 2C
0x203FBC 00 20 40 00 20 00 00 01 70 7E 00 00 A2 02 00 20
0x203FCC 6D 04 00 00 00 00 00 20 3F FE 00 00 00 15 00 00
0x203FDC 00 01 00 00 E3 FF 00 13 00 00 00 19 88 B6 00 01
0x203FEC 75 AE FD FF FB FF 00 19 88 B0 00 20 04 2C 00 20
0x203FFC 25 D8 20 00 00 20 25 D8 DE AD BE EF 00 00 00 00
0x20400C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20401C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20402C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20403C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20404C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #8
tbrsv1[0]: 201DB2
tbrsv1[1]: 201DB2
tbext: 0
tbpri: 23
tbid: 22 Remote read request task
tbstat: 40
tbd0: 0
tbd1: 4
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 203124
tba1: 1D560
tba2: 1D562
tba3: 1D55C
tbssp: 2030E0
tbusp: 0
tbstack: 20312C
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 149C
tbrsv2[2]: 20
tbrsv2[3]: 139C
tbrsv2[4]: 0
TCB #8 stack (176 bytes)
0x2030E0 DF 7E FF FF FD FF FB FF 00 01 D5 5C 00 20 04 2C
0x2030F0 00 20 31 28 20 00 00 01 70 D8 00 00 00 22 00 00
0x203100 EC 62 00 04 00 00 00 00 00 20 31 24 00 00 00 22
0x203110 00 00 00 01 00 01 D5 60 00 01 D5 62 D5 5C 00 20
0x203120 04 2C 00 20 00 00 20 00 00 20 04 1C DE AD BE EF
0x203130 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203140 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203150 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203160 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203170 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203180 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #9
tbrsv1[0]: 201DDE
tbrsv1[1]: 201DDE
tbext: 0
tbpri: 23
tbid: 28 Rung cache remote mod task
tbstat: 40
tbd0: 0
tbd1: 8
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 203C44
tba1: 1949E
tba2: 1D57A
tba3: 1D574
tbssp: 203C10
tbusp: 0
tbstack: 203C4E
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 131C
tbrsv2[2]: 20
tbrsv2[3]: 121C
tbrsv2[4]: 0
TCB #9 stack (176 bytes)
0x203C10 DF 7E FF FF FD FF FB FF 00 01 D5 74 00 20 04 2C
0x203C20 00 20 3C 4A 20 00 00 01 70 D8 00 00 00 28 00 01
0x203C30 11 5A 00 08 00 00 00 00 00 20 3C 44 00 01 D5 78
0x203C40 00 20 04 2C 00 00 04 1C 20 00 00 20 04 1C DE AD
0x203C50 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203C60 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203C70 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203C80 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203C90 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203CA0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203CB0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Current task (cp_control_processor task) stack (506 bytes):
0x202414 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202424 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202434 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202444 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202454 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202464 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202474 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202484 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202494 00 00 00 00 22 00 00 00 00 60 00 20 05 DC 20 00
0x2024A4 22 00 00 00 19 01 00 20 05 DC 22 00 22 00 00 00
0x2024B4 DF 7E FF FF 00 00 00 00 00 19 22 00 00 00 06 D8
0x2024C4 00 20 25 04 20 09 00 00 BF 72 00 00 80 00 00 00
0x2024D4 00 00 00 00 00 00 FF FF DF 00 00 01 53 44 DF 7E
0x2024E4 FF FF FD FF FB 00 00 20 3C BE 00 20 04 2C 00 20
0x2024F4 25 3E 27 00 00 01 70 3C 00 00 00 0A 00 00 00 58
0x202504 00 19 88 DC 00 01 A2 5A 00 20 25 34 00 00 00 20
0x202514 25 32 00 00 00 00 00 00 0F 52 00 00 00 01 00 20
0x202524 25 84 00 00 00 00 00 20 24 14 88 DC 00 19 00 00
0x202534 00 01 00 14 00 00 00 20 25 3E 00 20 25 88 00 01
0x202544 9A 00 00 00 00 00 00 00 00 00 00 18 31 8C 00 18
0x202554 8D 78 00 01 92 B4 00 01 20 08 00 00 9C 9C 00 18
0x202564 8E 18 00 19 88 B6 00 19 88 DC 00 00 98 2E 00 20
0x202574 25 84 00 00 00 00 00 02 00 00 00 00 00 19 88 DC
0x202584 00 00 00 00 00 20 25 C4 00 00 85 EC 00 19 88 DC
0x202594 00 00 00 05 00 00 00 05 00 00 E3 FF FF FF DF BF
0x2025A4 DF 7E FF FF FD FF FB FF 00 20 04 28 00 20 6C 92
0x2025B4 00 19 88 B6 00 00 00 00 00 00 00 00 00 19 72 14
0x2025C4 00 20 25 E2 00 01 85 98 00 00 00 05 00 00 00 05
0x2025D4 00 13 00 00 00 19 C6 DC 00 01 75 AE 00 05 00 20
0x2025E4 26 06 00 01 81 54 00 05 00 00 00 01 00 00 00 01
0x2025F4 00 00 00 03 00 01 D5 48 00 01 D5 4A 00 01 D5 44
0x202604 20 00 00 20 04 1C DE AD BE EF
Interrupt stack (252 bytes):
0x20250E 00 01 A2 AC 00 20 25 3A 00 00 00 00 00 00 0F 52
0x20251E 00 00 00 01 00 20 25 84 00 00 00 00 00 20 25 0E
0x20252E 88 DC 00 19 00 00 00 01 00 14 00 00 00 20 25 3E
0x20253E 00 20 25 88 00 01 9A 00 00 00 00 00 00 00 00 00
0x20254E 00 18 31 8C 00 18 8D 78 00 01 92 B4 00 01 20 08
0x20255E 00 00 9C 9C 00 18 8E 18 00 19 88 B6 00 19 88 DC
0x20256E 00 00 98 2E 00 20 25 84 00 00 00 00 00 02 00 00
0x20257E 00 00 00 19 88 DC 00 00 00 00 00 20 25 C4 00 00
0x20258E 85 EC 00 19 88 DC 00 00 00 05 00 00 00 05 00 00
0x20259E E3 FF FF FF DF BF DF 7E FF FF FD FF FB FF 00 20
0x2025AE 04 28 00 20 6C 92 00 19 88 B6 00 00 00 00 00 00
0x2025BE 00 00 00 19 72 14 00 20 25 E2 00 01 85 98 00 00
0x2025CE 00 05 00 00 00 05 00 13 00 00 00 19 C6 DC 00 01
0x2025DE 75 AE 00 05 00 20 26 06 00 01 81 54 00 05 00 00
0x2025EE 00 01 00 00 00 01 00 00 00 03 00 01 D5 48 00 01
0x2025FE D5 4A 00 01 D5 44 20 00 00 20 04 1C
=============================================================================
UPC saved tasks and stack data:
Task Control Block entry #0
tbrsv1[0]: 201E38
tbrsv1[1]: 201E38
tbext: 0
tbpri: 41
tbid: 3 cp_diagnostics task
tbstat: 0
tbd0: 0
tbd1: 0
tbd2: 41
tbd3: 1
tbd4: A
tbd5: AAAAAAAA
tba0: 201E38
tba1: 2E234
tba2: 2E236
tba3: 210000
tbssp: 202F5A
tbusp: 0
tbstack: 202F74
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: C9E
tbrsv2[2]: 20
tbrsv2[3]: 1DB8
tbrsv2[4]: 0
TCB #0 stack (176 bytes)
0x202F5A 00 00 00 00 58 BB 70 DA 00 20 CF 4C 00 04 00 00
0x202F6A 00 00 CF 4C 20 00 00 02 D2 52 DE AD BE EF 00 00
0x202F7A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202F8A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202F9A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FAA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FBA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FCA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FDA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FEA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FFA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #1
tbrsv1[0]: 201A38
tbrsv1[1]: 201A38
tbext: 0
tbpri: 2D
tbid: 6 rio_pg_srvc_task
tbstat: 20
tbd0: 0
tbd1: 1
tbd2: 2
tbd3: 1
tbd4: 3
tbd5: 20
tba0: 20D020
tba1: 30BBA9
tba2: 308151
tba3: 20BDA2
tbssp: 204CC0
tbusp: 0
tbstack: 204D24
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1AB8
tbrsv2[2]: 20
tbrsv2[3]: 19B8
tbrsv2[4]: 0
TCB #1 stack (176 bytes)
0x204CC0 00 00 00 00 FF FB FF 00 00 20 CF B7 00 20 84 2A
0x204CD0 00 20 4D 20 20 00 00 02 C6 90 00 02 75 58 00 00
0x204CE0 00 01 00 00 00 06 00 00 00 01 00 00 00 03 FF FF
0x204CF0 00 00 00 02 E2 74 00 02 E2 76 00 02 E2 70 00 20
0x204D00 D0 62 00 20 D0 52 00 20 D0 6A 00 20 D0 56 00 20
0x204D10 CF B9 00 30 01 D1 00 20 84 2A 00 20 CF B7 00 00
0x204D20 00 20 04 20 DE AD BE EF 00 00 00 00 00 00 00 00
0x204D30 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204D40 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204D50 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204D60 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #2
tbrsv1[0]: 20268E
tbrsv1[1]: 20268E
tbext: 0
tbpri: 41
tbid: 7 rio_async_task
tbstat: 40
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFF0000
tba0: 2050CC
tba1: 19B75E
tba2: 19B75E
tba3: 2E278
tbssp: 205088
tbusp: 0
tbstack: 2050DA
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1A38
tbrsv2[2]: 20
tbrsv2[3]: 1938
tbrsv2[4]: 0
TCB #2 stack (176 bytes)
0x205088 00 00 00 00 FF FB FF 00 00 18 8D 78 00 20 84 2A
0x205098 00 20 50 D6 20 00 00 02 C4 D8 00 00 00 07 00 00
0x2050A8 2C 50 00 01 00 00 00 00 00 20 50 CC 00 00 00 07
0x2050B8 00 00 00 01 00 02 E2 7C 00 02 E2 7E 00 02 E2 78
0x2050C8 00 19 CD 66 00 00 84 2A 00 20 04 20 20 00 00 20
0x2050D8 04 20 DE AD BE EF 00 00 00 00 00 00 00 00 00 00
0x2050E8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2050F8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205108 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205118 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205128 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #3
tbrsv1[0]: 202726
tbrsv1[1]: 202726
tbext: 0
tbpri: 41
tbid: 8 rio_start_btx_task
tbstat: 40
tbd0: 0
tbd1: D
tbd2: 0
tbd3: 1
tbd4: 100
tbd5: FFFF0002
tba0: 30A1D9
tba1: 19B800
tba2: 207BB4
tba3: 30A1D9
tbssp: 205426
tbusp: 0
tbstack: 205490
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 19B8
tbrsv2[2]: 20
tbrsv2[3]: 18B8
tbrsv2[4]: 0
TCB #3 stack (176 bytes)
0x205426 00 00 00 0E FF FB FF 00 00 30 A1 D9 00 20 84 2A
0x205436 00 20 54 8C 20 00 00 02 C4 D8 00 00 00 01 00 00
0x205446 12 1E 00 0D 00 00 00 00 00 20 54 7E 00 00 00 08
0x205456 00 00 00 01 00 00 00 03 FF FF 00 00 00 00 00 00
0x205466 FF FB FF 00 00 02 E2 84 00 02 E2 86 00 02 E2 80
0x205476 00 00 00 00 00 41 00 81 00 00 00 18 33 8C 00 18
0x205486 09 72 00 30 C0 E9 00 20 04 20 DE AD BE EF 00 00
0x205496 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2054A6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2054B6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2054C6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #4
tbrsv1[0]: 2026D2
tbrsv1[1]: 2026D2
tbext: 0
tbpri: 41
tbid: 9 rio_cplt_btx
tbstat: 60
tbd0: 0
tbd1: B
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFF0000
tba0: 307F09
tba1: 2E28C
tba2: 2E28E
tba3: 2E288
tbssp: 20581A
tbusp: 0
tbstack: 205846
tbflags: 8000
tbrsv2[0]: 20
tbrsv2[1]: 1938
tbrsv2[2]: 20
tbrsv2[3]: 1838
tbrsv2[4]: 0
TCB #4 stack (176 bytes)
0x20581A 09 72 00 20 84 2A 00 20 58 42 20 00 00 02 C4 D8
0x20582A 00 19 B7 5E 00 00 1B F8 00 0B 00 00 00 00 00 20
0x20583A 58 40 00 00 00 09 00 00 00 20 04 20 DE AD BE EF
0x20584A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20585A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20586A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20587A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20588A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20589A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2058AA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2058BA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #5
tbrsv1[0]: 201838
tbrsv1[1]: 201838
tbext: 0
tbpri: 37
tbid: B timing task
tbstat: 20
tbd0: 0
tbd1: 14
tbd2: E
tbd3: 1
tbd4: 3
tbd5: 14
tba0: 205BAC
tba1: 207EC7
tba2: 2C688
tba3: 2E290
tbssp: 205BBC
tbusp: 0
tbstack: 205BFC
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 18B8
tbrsv2[2]: 20
tbrsv2[3]: 17B8
tbrsv2[4]: 0
TCB #5 stack (176 bytes)
0x205BBC 00 00 00 00 FF FB FF 00 00 20 5B C8 00 20 84 2A
0x205BCC 00 20 5B F8 20 00 00 02 C6 90 00 02 4A 58 00 00
0x205BDC 00 14 00 00 00 0B 00 00 00 01 00 00 00 03 FF FF
0x205BEC 00 00 00 02 E2 94 00 02 E2 96 00 00 00 20 04 20
0x205BFC DE AD BE EF 00 00 00 00 00 00 00 00 00 00 00 00
0x205C0C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C1C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C2C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C3C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C4C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C5C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #6
tbrsv1[0]: 20279A
tbrsv1[1]: 20279A
tbext: 0
tbpri: 41
tbid: 1B DH1 task
tbstat: 40
tbd0: 0
tbd1: 28
tbd2: 0
tbd3: 1
tbd4: 28
tbd5: FFFF0000
tba0: 203324
tba1: 2E23C
tba2: 2E23E
tba3: 2E238
tbssp: 2032E4
tbusp: 0
tbstack: 20332A
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1E38
tbrsv2[2]: 20
tbrsv2[3]: 1D38
tbrsv2[4]: 0
TCB #6 stack (176 bytes)
0x2032E4 00 00 00 00 FF FB FF 00 00 02 E2 38 00 20 84 2A
0x2032F4 00 20 33 26 20 00 00 02 C4 D8 00 00 00 1B 00 02
0x203304 24 96 00 28 00 00 00 00 00 20 33 24 00 00 00 1B
0x203314 00 00 00 01 00 00 00 03 00 02 E2 3C 00 20 04 20
0x203324 00 00 00 20 04 20 DE AD BE EF 00 00 00 00 00 00
0x203334 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203344 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203354 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203364 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203374 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203384 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #7
tbrsv1[0]: 202802
tbrsv1[1]: 202802
tbext: 0
tbpri: 41
tbid: 1C DH2 task
tbstat: 40
tbd0: 0
tbd1: 29
tbd2: 0
tbd3: 1
tbd4: 29
tbd5: FFFF0000
tba0: 2036DA
tba1: 2E244
tba2: 2E246
tba3: 2E240
tbssp: 20369A
tbusp: 0
tbstack: 2036E0
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1DB8
tbrsv2[2]: 20
tbrsv2[3]: 1CB8
tbrsv2[4]: 0
TCB #7 stack (176 bytes)
0x20369A 00 00 00 00 FF FB FF 00 00 02 E2 40 00 20 84 2A
0x2036AA 00 20 36 DC 20 00 00 02 C4 D8 00 00 00 1C 00 02
0x2036BA 24 96 00 29 00 00 00 00 00 20 36 DA 00 00 00 1C
0x2036CA 00 00 00 01 00 00 00 03 00 02 E2 44 00 20 04 20
0x2036DA 00 00 00 20 04 20 DE AD BE EF 00 00 00 00 00 00
0x2036EA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2036FA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20370A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20371A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20372A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20373A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #8
tbrsv1[0]: 20286A
tbrsv1[1]: 20286A
tbext: 0
tbpri: 41
tbid: 1D DH3 task
tbstat: 40
tbd0: 0
tbd1: 2A
tbd2: 0
tbd3: 1
tbd4: 2A
tbd5: FFFF0000
tba0: 203A90
tba1: 2E24C
tba2: 2E24E
tba3: 2E248
tbssp: 203A50
tbusp: 0
tbstack: 203A96
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1D38
tbrsv2[2]: 20
tbrsv2[3]: 1C38
tbrsv2[4]: 0
TCB #8 stack (176 bytes)
0x203A50 00 00 00 00 FF FB FF 00 00 02 E2 48 00 20 84 2A
0x203A60 00 20 3A 92 20 00 00 02 C4 D8 00 00 00 1D 00 02
0x203A70 24 96 00 2A 00 00 00 00 00 20 3A 90 00 00 00 1D
0x203A80 00 00 00 01 00 00 00 03 00 02 E2 4C 00 20 04 20
0x203A90 00 00 00 20 04 20 DE AD BE EF 00 00 00 00 00 00
0x203AA0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AB0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AC0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AD0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AE0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AF0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #9
tbrsv1[0]: 202550
tbrsv1[1]: 201AB8
tbext: 0
tbpri: 28
tbid: 1F DH task
tbstat: 220
tbd0: 0
tbd1: 1
tbd2: 6A
tbd3: 7FFB0
tbd4: 0
tbd5: FFFF0001
tba0: 307F01
tba1: 20CF2C
tba2: 20CF44
tba3: 2C9BC
tbssp: 203DDC
tbusp: 0
tbstack: 203E4C
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1CB8
tbrsv2[2]: 20
tbrsv2[3]: 1BB8
tbrsv2[4]: 0
TCB #9 stack (176 bytes)
0x203DDC 00 00 00 6A FF FB FF 00 00 30 BB 5D 00 20 84 2A
0x203DEC 00 20 3E 48 20 00 00 02 C5 9C 00 00 00 02 18 20
0x203DFC 02 0C 00 00 00 03 00 02 84 96 00 01 00 00 00 6A
0x203E0C 00 07 FF B0 00 00 00 20 3E 46 00 00 00 1F 00 00
0x203E1C 00 01 00 00 00 03 FF FF 00 00 00 00 00 00 FF FB
0x203E2C FF 00 00 02 E2 54 00 02 E2 56 00 02 E2 50 00 20
0x203E3C D0 82 00 01 00 00 00 04 04 20 00 34 00 20 04 20
0x203E4C DE AD BE EF 00 00 00 00 00 00 00 00 00 00 00 00
0x203E5C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203E6C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203E7C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #10
tbrsv1[0]: 202490
tbrsv1[1]: 202490
tbext: 0
tbpri: 15
tbid: 21 DH histogram task
tbstat: 200
tbd0: 0
tbd1: 7
tbd2: 0
tbd3: 20
tbd4: 1
tbd5: FFFF0000
tba0: 201BB8
tba1: 2E25C
tba2: 2C580
tba3: 2E258
tbssp: 204194
tbusp: 0
tbstack: 204202
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1C38
tbrsv2[2]: 20
tbrsv2[3]: 1B38
tbrsv2[4]: 0
TCB #10 stack (176 bytes)
0x204194 00 00 00 00 FF FB FF 00 00 02 E2 58 00 20 84 2A
0x2041A4 00 20 41 FE 20 00 00 02 C5 9C 00 00 00 21 00 00
0x2041B4 00 01 00 00 00 03 00 01 1E 70 00 07 00 00 00 00
0x2041C4 00 00 00 20 00 01 00 20 41 FC 00 00 00 21 00 00
0x2041D4 00 01 00 00 00 03 FF FF 00 00 00 00 00 00 FF FB
0x2041E4 FF 00 00 02 E2 5C 00 02 E2 5E 00 02 E2 58 E2 58
0x2041F4 00 00 00 01 00 20 04 20 20 00 00 20 04 20 DE AD
0x204204 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204214 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204224 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204234 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #11
tbrsv1[0]: 202636
tbrsv1[1]: 202636
tbext: 0
tbpri: 23
tbid: 22 Remote read request task
tbstat: 40
tbd0: 0
tbd1: 5
tbd2: 0
tbd3: 0
tbd4: 3
tbd5: FFFF0000
tba0: 2045B0
tba1: 300100
tba2: 19CD84
tba3: 2E260
tbssp: 20456C
tbusp: 0
tbstack: 2045B8
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1BB8
tbrsv2[2]: 20
tbrsv2[3]: 1AB8
tbrsv2[4]: 0
TCB #11 stack (176 bytes)
0x20456C 00 00 00 00 FF FB FF 00 00 19 CF 38 00 20 84 2A
0x20457C 00 20 45 B4 20 00 00 02 C4 D8 00 00 00 00 00 00
0x20458C C1 82 00 05 00 00 00 00 00 20 45 B0 00 00 00 22
0x20459C 00 00 00 01 00 02 E2 64 00 02 E2 66 01 03 01 00
0x2045AC 84 2A 00 20 00 00 20 00 00 20 04 20 DE AD BE EF
0x2045BC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2045CC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2045DC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2045EC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2045FC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20460C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #12
tbrsv1[0]: 201AB8
tbrsv1[1]: 202550
tbext: 0
tbpri: 41
tbid: 23 Make PCL message task
tbstat: 200
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 48000000
tbd4: 1
tbd5: FFFF0000
tba0: 2017B8
tba1: 2E29C
tba2: 2E29E
tba3: 2E298
tbssp: 205F54
tbusp: 0
tbstack: 205FB2
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1838
tbrsv2[2]: 20
tbrsv2[3]: 1738
tbrsv2[4]: 0
TCB #12 stack (176 bytes)
0x205F54 00 00 00 00 FF FB FF 00 00 02 E2 98 00 20 84 2A
0x205F64 00 20 5F AE 20 00 00 02 C5 9C 00 00 00 23 00 00
0x205F74 00 01 00 00 00 03 00 02 44 6E 00 01 00 00 00 00
0x205F84 48 00 00 00 00 01 00 20 5F A4 00 00 00 23 00 00
0x205F94 00 01 00 02 E2 9C 00 02 E2 9E 00 02 E2 98 E2 98
0x205FA4 00 20 84 2A 00 20 04 20 20 00 00 20 04 20 DE AD
0x205FB4 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205FC4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205FD4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205FE4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205FF4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #13
tbrsv1[0]: 202662
tbrsv1[1]: 202662
tbext: 0
tbpri: 23
tbid: 28 Rung cache remote mod task
tbstat: 40
tbd0: 0
tbd1: 8
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFF0000
tba0: 20635E
tba1: 2C9BC
tba2: 2E2A6
tba3: 2E2A0
tbssp: 20632A
tbusp: 0
tbstack: 206368
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 17B8
tbrsv2[2]: 20
tbrsv2[3]: C9E
tbrsv2[4]: 0
TCB #13 stack (176 bytes)
0x20632A 00 00 00 00 FF FB FF 00 00 02 E2 A0 00 20 84 2A
0x20633A 00 20 63 64 20 00 00 02 C4 D8 00 00 00 28 00 01
0x20634A 91 AE 00 08 00 00 00 00 00 20 63 5E 00 02 E2 A4
0x20635A 00 20 84 2A 00 00 04 20 20 00 00 20 04 20 00 00
0x20636A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20637A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20638A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20639A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2063AA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2063BA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2063CA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #14
tbrsv1[0]: 201C38
tbrsv1[1]: 2017B8
tbext: 0
tbpri: 2F
tbid: 45 RIO IOT task
tbstat: 200
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 800000
tbd4: 0
tbd5: FFFF0000
tba0: 204968
tba1: 2C9BC
tba2: 2E26E
tba3: 2E268
tbssp: 204922
tbusp: 0
tbstack: 20496E
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1B38
tbrsv2[2]: 20
tbrsv2[3]: 1A38
tbrsv2[4]: 0
Diagnostic Data for Processor PLC5/40 Series E Revision J
Domino Plug 1 Firmware Series/Rev: A/T
Domino Plug 2 Firmware Series/Rev: A/T
Fault logged by microprocessor: UPA
Error string: "REBOOTp1: i_be_dead trap error vector=00010, at address 000c2"
D0 = 0x000000C5 A0 = 0x00207EEE
D1 = 0x000000BF A1 = 0x00017F91
D2 = 0x00000050 A2 = 0x002404B7
D3 = 0x000000FF A3 = 0x00207F86
D4 = 0x00030004 A4 = 0x0019CF38
D5 = 0x2FFF0000 A5 = 0x00207F86
D6 = 0x00000001 A6 = 0x0020E40E
D7 = 0x00000007 A7 = 0x00207F30
Error Code = 0x008A
Trap Offset = 0x0010
Return address = 0x000000C2
68Ks Status Register = 0x2000
Following are 26 words of stack data in hex
01B4 0000 0020 7F94 0000 6866 0020 7F94 0000 66C8 0020 7F86 0000 0029 0000
0001 0000 0003 2FFF 0000 0024 04A2 0024 043E 0000 6B10
Raw Data of above
0x198DAA 00 01 00 00 00 C5 00 00 00 BF 00 00 00 50 00 00 .............P..
0x198DBA 00 FF 00 03 00 04 2F FF 00 00 00 00 00 01 00 00 ....../.........
0x198DCA 00 07 00 20 7E EE 00 01 7F 91 00 24 04 B7 00 20 ... ~......$...
0x198DDA 7F 86 00 19 CF 38 00 20 7F 86 00 20 E4 0E 00 20 .....8. ... ...
0x198DEA 7F 30 00 8A 00 10 00 00 00 C2 20 00 01 B4 00 00 .0........ .....
0x198DFA 00 20 7F 94 00 00 68 66 00 20 7F 94 00 00 66 C8 . ....hf. ....f.
0x198E0A 00 20 7F 86 00 00 00 29 00 00 00 01 00 00 00 03 . .....)........
0x198E1A 2F FF 00 00 00 24 04 A2 00 24 04 3E 00 00 6B 10 /....$...$.>..k.
0x198E2A 52 45 42 4F 4F 54 70 31 3A 20 69 5F 62 65 5F 64 REBOOTp1: i_be_d
0x198E3A 65 61 64 20 74 72 61 70 20 65 72 72 6F 72 20 76 ead trap error v
0x198E4A 65 63 74 6F 72 3D 30 30 30 31 30 2C 20 61 74 20 ector=00010, at
0x198E5A 61 64 64 72 65 73 73 20 30 30 30 63 32 0D 0A 64 address 000c2..d
0x198E6A AD 84 00 C0 FF 9A 01 0B 9D 20 45 5A 3E 61 90 A0 ......... EZ>a..
0x198E7A FF DB 4C C3 EF 9D 83 F7 CF FB A5 5F DF DF CE 7A ..L........_...z
0x198E8A 6F FF 10 CE 9D 91 1A FE DF FF 60 DB F3 A7 50 B9 o.........`...P.
0x198E9A FF FF 14 48 FF 7B 8C 5A D7 A6 69 EE FE 5A 0E 42 ...H.{.Z..i..Z.B
0x198EAA FE 42 B2 25 7F 77 .B.%.w
=============================================================================
UPAs registers and stack
D0 = 0x00000000 A0 = 0x000000C2
D1 = 0x0000FFFF A1 = 0x2FFF0000
D2 = 0x00006866 A2 = 0x002404A2
D3 = 0x00207F94 A3 = 0x0024043E
D4 = 0x000066C8 A4 = 0x00006B10
D5 = 0x00207F86 A5 = 0x0020842A
D6 = 0x00000029 A6 = 0x002410A6
D7 = 0x00000001 A7 = 0x00200428
Error Code = 0x198A
Trap Offset = 0x7FFF
Return address = 0x29008A19
68Ks Status Register = 0x2000
Following are 30 words of stack data in hex
8085 8580 8032 3280 0000 0400 0000 1000 0000 4000 0001 0000 0000 0020 0020
0040 0000 0080 00C0 0080 00C0 00C0 0000 0008 0008 0008 0008 0008 0008 0008
Raw Data of above
0x19E206 00 01 00 00 00 00 00 00 FF FF 00 00 68 66 00 20 ............hf.
0x19E216 7F 94 00 00 66 C8 00 20 7F 86 00 00 00 29 00 00 ....f.. .....)..
0x19E226 00 01 00 00 00 C2 2F FF 00 00 00 24 04 A2 00 24 ....../....$...$
0x19E236 04 3E 00 00 6B 10 00 20 84 2A 00 24 10 A6 00 20 .>..k.. .*.$...
0x19E246 04 28 19 8A 7F FF 29 00 8A 19 20 00 80 85 85 80 .(....)... .....
0x19E256 80 32 32 80 00 00 04 00 00 00 10 00 00 00 40 00 .22...........@.
0x19E266 00 01 00 00 00 00 00 20 00 20 00 40 00 00 00 80 ....... . .@....
0x19E276 00 C0 00 80 00 C0 00 C0 00 00 00 08 00 08 00 08 ................
0x19E286 00 08 00 08 00 08 00 08 ........
UPBs registers and stack
D0 = 0x00000000 A0 = 0x0018318C
D1 = 0x00000000 A1 = 0x00202584
D2 = 0x00000000 A2 = 0x00000000
D3 = 0x00000F52 A3 = 0x001988DC
D4 = 0x00000001 A4 = 0x00188D78
D5 = 0xFFFFDF00 A5 = 0x0020042C
D6 = 0xDF7EFFFF A6 = 0x00202588
D7 = 0xFDFFFB00 A7 = 0x00202556
Error Code = 0x0001
Trap Offset = 0x0000
Return address = 0x000192B4
68Ks Status Register = 0x2700
Following are 30 words of stack data in hex
2008 0000 9C9C 0018 8E18 0019 88B6 0019 88DC 0000 982E 0020 2584 0000 0000
0002 0000 0000 0019 88DC 0000 0000 0020 25C4 0000 85EC 0019 88DC 0000 0005
Raw Data of above
0x19E28E 00 02 00 00 00 00 00 00 00 00 00 00 00 00 00 00 ................
0x19E29E 0F 52 00 00 00 01 FF FF DF 00 DF 7E FF FF FD FF .R.........~....
0x19E2AE FB 00 00 18 31 8C 00 20 25 84 00 00 00 00 00 19 ....1.. %.......
0x19E2BE 88 DC 00 18 8D 78 00 20 04 2C 00 20 25 88 00 20 .....x. .,. %..
0x19E2CE 25 56 00 01 00 00 00 01 92 B4 27 00 20 08 00 00 %V........'. ...
0x19E2DE 9C 9C 00 18 8E 18 00 19 88 B6 00 19 88 DC 00 00 ................
0x19E2EE 98 2E 00 20 25 84 00 00 00 00 00 02 00 00 00 00 ... %...........
0x19E2FE 00 19 88 DC 00 00 00 00 00 20 25 C4 00 00 85 EC ......... %.....
0x19E30E 00 19 88 DC 00 00 00 05 ........
UPCs registers and stack
D0 = 0x00000000 A0 = 0x00307F09
D1 = 0x00000000 A1 = 0x0002E28C
D2 = 0x00080104 A2 = 0x00201334
D3 = 0x00000001 A3 = 0x00200D5E
D4 = 0x00000003 A4 = 0x002018B8
D5 = 0xFFFF0000 A5 = 0x002026D2
D6 = 0x00002014 A6 = 0x00200CF8
D7 = 0x00000000 A7 = 0x002057F8
Error Code = 0x0001
Trap Offset = 0x0000
Return address = 0x0002C83A
68Ks Status Register = 0x2700
Following are 30 words of stack data in hex
2010 0002 B36E 0002 E288 0002 ABD2 0000 0000 0000 0000 FFFB FF00 0018 0972
0020 842A 0020 5842 2000 0002 C4D8 0019 B75E 0000 1BF8 000B 0000 0000 0020
Raw Data of above
0x19E316 00 04 00 00 00 00 00 00 00 00 00 08 01 04 00 00 ................
0x19E326 00 01 00 00 00 03 FF FF 00 00 00 00 20 14 00 00 ............ ...
0x19E336 00 00 00 30 7F 09 00 02 E2 8C 00 20 13 34 00 20 ...0....... .4.
0x19E346 0D 5E 00 20 18 B8 00 20 26 D2 00 20 0C F8 00 20 .^. ... &.. ...
0x19E356 57 F8 00 01 00 00 00 02 C8 3A 27 00 20 10 00 02 W........:'. ...
0x19E366 B3 6E 00 02 E2 88 00 02 AB D2 00 00 00 00 00 00 .n..............
0x19E376 00 00 FF FB FF 00 00 18 09 72 00 20 84 2A 00 20 .........r. .*.
0x19E386 58 42 20 00 00 02 C4 D8 00 19 B7 5E 00 00 1B F8 XB ........^....
0x19E396 00 0B 00 00 00 00 00 20 .......
=============================================================================
Extended data for UPA valid flag: AAAA
Number of saved UPA tasks: 22
Extended data for UPB valid flag: BBBB
Number of saved UPB tasks: 10
Extended data for UPC valid flag: CCCC
Number of saved UPC tasks: 15
Data format: 0100
Miscellaneous variables:
07 DC 00 0A 00 03 00 05 00 01 00 0D
=============================================================================
UPA saved tasks and stack data:
Task Control Block entry #0
tbrsv1[0]: 7401E400
tbrsv1[1]: E800EC00
tbext: F0100817
tbpri: 0
tbid: 99
tbstat: 7402
tbd0: E800F010
tbd1: 8170099
tbd2: 7404E400
tbd3: F0100817
tbd4: 9A7407
tbd5: E800F01C
tba0: 74020817
tba1: 997407
tba2: F01C7408
tba3: 817009A
tbssp: 7400E800
tbusp: F01C7408
tbstack: 8170099
tbflags: 740A
tbrsv2[0]: F01C
tbrsv2[1]: 7404
tbrsv2[2]: 817
tbrsv2[3]: 9A
tbrsv2[4]: 7400
TCB #0 stack (176 bytes)
0x7400E800 E8 00 F0 1C 74 06 08 17 00 9B 74 00 E4 00 F0 7E
0x7400E810 73 F7 08 17 00 FF E0 13 80 D5 EC 00 F0 1C 74 0F
0x7400E820 08 17 00 9C 74 09 E8 00 F0 10 08 17 00 9C 74 0B
0x7400E830 E4 00 F0 7E 73 F4 08 17 00 FF E0 13 80 D5 F0 10
0x7400E840 08 17 00 9D 74 00 EC 00 F0 12 08 17 00 9C 74 0A
0x7400E850 E8 00 89 8A E4 00 F0 7E 73 F3 08 17 00 FF E0 01
0x7400E860 80 04 E0 13 80 D5 F0 10 08 17 00 96 78 07 00 D1
0x7400E870 8C 81 EC 00 F0 7E 73 F1 08 17 00 FF E8 00 E0 06
0x7400E880 A9 91 E0 01 80 04 E0 13 80 D5 F0 10 08 17 00 99
0x7400E890 74 01 F0 10 08 17 00 9A 74 06 E0 02 98 C3 EC 00
0x7400E8A0 F0 7E 73 EF 08 17 00 FF E8 00 E0 06 AA 91 E0 13
Task Control Block entry #1
tbrsv1[0]: 80D5F010
tbrsv1[1]: 81700FF
tbext: 7402EC00
tbpri: F0
tbid: D4
tbstat: 2817
tbd0: 912816
tbd1: 337414
tbd2: E800F0D4
tbd3: 28170091
tbd4: 281400D5
tbd5: 7414E800
tba0: F02C0817
tba1: FFE800
tba2: EC00F010
tba3: 8170092
tbssp: 7827000F
tbusp: F07E73FF
tbstack: 8170092
tbflags: E800
tbrsv2[0]: F022
tbrsv2[1]: 817
tbrsv2[2]: 92
tbrsv2[3]: 7401
tbrsv2[4]: 817
TCB #1 stack (176 bytes)
0x7827000F 00 92 E4 00 E8 00 F0 2C 08 17 00 9D E8 00 E0 07
0x7827001F A2 E9 E0 0F 84 D1 E0 07 90 D3 F0 18 08 17 00 FF
0x7827002F 74 00 EC 00 E0 08 86 34 F0 86 F0 64 18 08 00 E9
0x7827003F 7C 87 16 00 00 00 60 10 F0 54 18 08 00 E7 60 10
0x7827004F F0 8E E8 00 E0 07 92 E9 E4 00 FF C2 07 D2 EC 00
0x7827005F F0 7E 74 01 08 17 00 FF E8 00 E0 07 A0 D3 E0 0F
0x7827006F 94 D1 F0 10 08 17 00 FF 74 01 F0 2C 08 17 00 FF
0x7827007F E0 07 80 D3 F0 30 08 0B 00 37 EC 00 E0 0B 8D 37
0x7827008F E8 00 E0 0F 94 D1 E4 00 E0 07 B0 D3 F0 88 E0 04
0x7827009F CA 88 F0 10 08 17 00 FE 74 02 E0 13 C0 D7 E0 13
0x782700AF 80 D7 F0 12 08 17 00 4E 74 10 F0 7E 73 FD 08 17
Task Control Block entry #2
tbrsv1[0]: FEE013
tbrsv1[1]: 80D7F01C
tbext: 740A0817
tbpri: 0
tbid: 50 COPRO slow PCCC task
tbstat: 7400
tbd0: F01C7467
tbd1: 8170050
tbd2: 7464F07E
tbd3: 73FA0817
tbd4: FEE013
tbd5: 80D7F01C
tba0: 74080817
tba1: 517400
tba2: F01C746B
tba3: 8170051
tbssp: 7464F07E
tbusp: 73F90817
tbstack: FEE013
tbflags: 80D7
tbrsv2[0]: F01C
tbrsv2[1]: 7406
tbrsv2[2]: 817
tbrsv2[3]: 52
tbrsv2[4]: 7400
TCB #2 stack (176 bytes)
0x7464F07E F0 7E 73 F8 08 17 00 FE E0 13 80 D7 F0 1C 74 02
0x7464F08E 08 17 00 53 73 FE F0 7E 73 F7 08 17 00 FE E0 13
0x7464F09E 80 D7 F0 10 08 17 00 FE 74 02 EC 00 F0 2C 08 17
0x7464F0AE 00 FE E8 00 F0 22 08 17 00 4C 74 01 08 17 00 4C
0x7464F0BE E8 00 F0 D4 28 17 00 4B 28 14 00 8F 74 28 E8 00
0x7464F0CE E0 13 C1 D7 E0 13 81 D7 EC 00 F0 1C 74 65 08 17
0x7464F0DE 00 50 74 67 EC 00 F0 22 08 17 00 50 74 8C 08 0F
0x7464F0EE 00 EF E8 00 F0 24 08 17 00 51 74 64 08 0F 00 0F
0x7464F0FE E4 00 E8 00 F0 1C 74 01 08 17 00 50 74 09 F0 22
0x7464F10E 08 17 00 50 74 E6 08 0F 00 EF E8 00 F0 1C 74 01
0x7464F11E 08 17 00 50 74 09 F0 7E 08 17 00 51 08 0F 00 0F
Task Control Block entry #3
tbrsv1[0]: E800F084
tbrsv1[1]: F024080F
tbext: F7401
tbpri: 60
tbid: 0 unused 0
tbstat: F026
tbd0: 6000744B
tbd1: 6000F024
tbd2: 8170052
tbd3: 74016002
tbd4: F0266002
tbd5: 740F6002
tba0: F0226000
tba1: 60026000
tba2: F0226000
tba3: 7401080F
tbssp: F0F08E
tbusp: E01381D7
tbstack: F0D42814
tbflags: 97
tbrsv2[0]: 4804
tbrsv2[1]: 0
tbrsv2[2]: 80F
tbrsv2[3]: EF
tbrsv2[4]: 80F
TCB #3 stack (176 bytes)
0xF0F08E 00 F0 74 0F E0 04 CB 88 F0 10 08 17 00 FD 74 02
0xF0F09E E0 13 C0 DA E0 13 80 DA EC 00 F0 1C 74 0A 08 17
0xF0F0AE 00 3C 74 00 F0 1C 74 68 08 17 00 3C 74 64 E8 00
0xF0F0BE F0 1C 74 65 08 17 00 3D 74 6A F0 1C 74 68 08 17
0xF0F0CE 00 3C 74 64 E4 00 F0 7E 73 FA 08 17 00 FD E0 13
0xF0F0DE 80 DA EC 00 F0 1C 74 08 08 17 00 3D 74 00 F0 1C
0xF0F0EE 74 6B 08 17 00 3D 74 64 E8 00 F0 1C 74 65 08 17
0xF0F0FE 00 3C 74 67 F0 1C 74 6B 08 17 00 3D 74 64 E4 00
0xF0F10E F0 7E 73 F9 08 17 00 FD E0 13 80 DA F0 1C 74 06
0xF0F11E 08 17 00 3E 74 00 F0 7E 73 F8 08 17 00 FD E0 13
0xF0F12E 80 DA EC 00 F0 1C 74 0A 08 17 00 3F 74 00 F0 1C
Task Control Block entry #4
tbrsv1[0]: 74680817
tbrsv1[1]: 3F7464
tbext: E800F01C
tbpri: 74
tbid: 65
tbstat: 817
tbd0: 40746A
tbd1: F01C7468
tbd2: 817003F
tbd3: 7464E400
tbd4: F07E73F7
tbd5: 81700FD
tba0: E01380DA
tba1: EC00F01C
tba2: 74080817
tba3: 407400
tbssp: F01C746B
tbusp: 8170040
tbstack: 7464E800
tbflags: F01C
tbrsv2[0]: 7465
tbrsv2[1]: 817
tbrsv2[2]: 3F
tbrsv2[3]: 7467
tbrsv2[4]: F01C
TCB #4 stack (176 bytes)
0xF01C746B 74 6B 08 17 00 40 74 64 E4 00 F0 7E 73 F6 08 17
0xF01C747B 00 FD E0 13 80 DA F0 1C 74 06 08 17 00 41 74 00
0xF01C748B F0 7E 73 F5 08 17 00 FD E0 13 80 DA F0 1C 74 03
0xF01C749B 08 17 00 42 74 00 F0 7E 73 F4 08 17 00 FD E0 13
0xF01C74AB 80 DA F0 10 08 17 00 FD 74 02 EC 00 F0 2C 08 17
0xF01C74BB 00 FD E8 00 F0 22 08 17 00 38 74 01 08 17 00 38
0xF01C74CB E8 00 F0 D4 28 17 00 37 28 14 00 7B 74 14 E8 00
0xF01C74DB F0 D4 28 14 00 80 28 08 00 1B 74 06 E8 00 F0 7E
0xF01C74EB 08 14 00 86 08 08 00 22 E8 00 E0 13 C1 DA E0 13
0xF01C74FB 81 DA F0 80 74 41 F0 88 E0 04 C4 89 F0 10 08 17
0xF01C750B 00 F7 74 02 E0 13 C0 D8 E0 13 80 D8 F0 12 08 16
Task Control Block entry #5
tbrsv1[0]: C27410
tbrsv1[1]: F07E73FC
tbext: 81700F7
tbpri: E0
tbid: 13 STI Task
tbstat: 80D8
tbd0: F01C7407
tbd1: 81600C4
tbd2: 7400F07E
tbd3: 73FA0817
tbd4: F7E013
tbd5: 80D8F010
tba0: 81700F7
tba1: 7402EC00
tba2: F02C0817
tba3: F7E800
tbssp: F0D42816
tbusp: BF2814
tbstack: 37406
tbflags: E800
tbrsv2[0]: F022
tbrsv2[1]: 816
tbrsv2[2]: C0
tbrsv2[3]: 7401
tbrsv2[4]: 816
TCB #5 stack (176 bytes)
0xF0D42816 00 C0 E8 00 E0 13 C1 D8 E0 13 81 D8 EC 00 F0 10
0xF0D42826 08 14 00 08 74 01 E0 13 C2 D8 E8 00 F0 10 08 14
0xF0D42836 00 08 74 02 E0 13 C3 D8 E8 00 F0 10 08 14 00 08
0xF0D42846 74 03 E0 13 C4 D8 E8 00 F0 10 08 14 00 08 74 04
0xF0D42856 E0 07 80 E9 E0 07 91 E9 E0 13 C5 D8 EC 00 E0 13
0xF0D42866 84 D8 E8 00 86 F4 E4 00 E0 07 80 E9 E0 07 92 E9
0xF0D42876 EC 00 E0 07 A2 E9 E8 00 F0 7E 74 96 07 FF F0 88
0xF0D42886 E0 04 CE 89 F0 10 08 17 00 F6 74 02 E0 13 C0 D9
0xF0D42896 E0 13 80 D9 F0 12 08 16 00 AE 74 00 F0 7E 73 FC
0xF0D428A6 08 17 00 F6 E0 13 80 D9 F0 1C 74 05 08 16 00 B0
0xF0D428B6 74 00 F0 7E 73 FA 08 17 00 F6 E0 13 80 D9 F0 10
Task Control Block entry #6
tbrsv1[0]: 81700F6
tbrsv1[1]: 7402EC00
tbext: F02C0817
tbpri: 0
tbid: F6
tbstat: E800
tbd0: F0D42816
tbd1: AB2813
tbd2: EF7406
tbd3: E800F022
tbd4: 81600AC
tbd5: 74010816
tba0: ACE800
tba1: E013C1D9
tba2: E01381D9
tba3: EC00F010
tbssp: 81300F4
tbusp: 7401E013
tbstack: C2D9E800
tbflags: F010
tbrsv2[0]: 813
tbrsv2[1]: F4
tbrsv2[2]: 7402
tbrsv2[3]: E013
tbrsv2[4]: C3D9
TCB #6 stack (176 bytes)
0x81300F4 E8 00 F0 10 08 13 00 F4 74 03 E0 13 C4 D9 E8 00
0x8130104 F0 10 08 13 00 F4 74 04 E0 13 C5 D9 F0 88 E0 04
0x8130114 C0 8D E0 07 80 D4 F0 7E 74 01 08 18 00 03 E0 07
0x8130124 80 E2 F0 7E 74 02 08 18 00 03 E0 07 80 E9 EC 00
0x8130134 E0 05 81 E1 F0 7E 74 04 08 18 00 03 E8 00 E0 05
0x8130144 82 E1 F0 7E 74 05 08 18 00 03 E0 06 88 F4 E0 18
0x8130154 C0 04 85 8B EC 00 83 8A E8 00 81 8A E4 00 E0 18
0x8130164 C0 05 9C 81 E0 18 C0 06 8D 81 E0 18 C1 06 98 81
0x8130174 9B 81 E0 18 C0 07 EC 00 89 81 E8 00 8A 81 E4 00
0x8130184 E0 18 C1 07 8E 81 E0 18 C4 07 8F 81 E0 18 C5 07
0x8130194 E0 08 8E 31 F4 C2 07 D3 E0 07 C5 D3 E0 08 8A 2B
Task Control Block entry #7
tbrsv1[0]: F6C207D3
tbrsv1[1]: E007C7D3
tbext: EC00E008
tbpri: 8C
tbid: 33 CNET async BT request task
tbstat: E800
tbd0: E0088634
tbd1: E400F8C2
tbd2: 7D3E007
tbd3: C9D3E001
tbd4: 80049981
tbd5: 9A81EC00
tba0: F0120816
tba1: 387401
tba2: F0120816
tba3: 397402
tbssp: E800E008
tbusp: 9E2CE008
tbstack: 982DE008
tbflags: 922E
tbrsv2[0]: E400
tbrsv2[1]: FAC2
tbrsv2[2]: 7D3
tbrsv2[3]: E007
tbrsv2[4]: CBD3
TCB #7 stack (176 bytes)
0xE800E008 E0 01 80 04 9E 81 9F 81 EC 00 F0 12 08 16 00 38
0xE800E018 74 0A F0 12 08 16 00 39 74 02 E8 00 E0 08 9E 2C
0xE800E028 E0 08 98 2D E0 08 92 2E E4 00 FC C2 07 D3 E0 07
0xE800E038 CD D3 E0 07 87 D3 EC 00 F0 D4 28 16 00 38 28 18
0xE800E048 00 93 74 06 E8 00 F0 7E 74 01 08 18 00 99 E8 00
0xE800E058 F0 7E 08 16 00 3F 08 18 00 9A E8 00 F0 7E 08 16
0xE800E068 00 40 08 18 00 9B E0 07 85 D3 EC 00 F0 D4 28 16
0xE800E078 00 38 28 18 00 93 74 06 E8 00 F0 7E 74 02 08 18
0xE800E088 00 99 E8 00 F0 7E 08 16 00 3F 08 18 00 9A E8 00
0xE800E098 F0 7E 08 16 00 40 08 18 00 9B E0 07 89 D3 EC 00
0xE800E0A8 F0 D4 28 16 00 38 28 18 00 93 74 06 E8 00 F0 7E
Task Control Block entry #8
tbrsv1[0]: 74030818
tbrsv1[1]: 99E800
tbext: F07E0816
tbpri: 0
tbid: 3F CNET PCCC BT task
tbstat: 818
tbd0: 9AE800
tbd1: F07E0816
tbd2: 400818
tbd3: 9BE007
tbd4: 8BD3F012
tbd5: 81B0087
tba0: 7400EC00
tba1: F07E7401
tba2: 8180093
tba3: E800F07E
tbssp: 74020818
tbusp: 94E800
tbstack: F07E7401
tbflags: 818
tbrsv2[0]: 95
tbrsv2[1]: E800
tbrsv2[2]: F0D6
tbrsv2[3]: 2818
tbrsv2[4]: 96
TCB #8 stack (176 bytes)
0x74020818 74 00 74 03 E8 00 F0 7E 74 03 08 18 00 99 E8 00
0x74020828 F0 7E 08 1B 00 87 08 18 00 9A E8 00 F0 7E 78 11
0x74020838 00 31 08 18 00 9B E8 00 F0 D6 28 1B 00 86 74 00
0x74020848 74 03 E0 07 8D D3 F0 12 08 2E 00 05 74 00 EC 00
0x74020858 F0 7E 74 0A 08 18 00 93 E8 00 F0 7E 74 02 08 18
0x74020868 00 94 E8 00 F0 7E 74 01 08 18 00 95 E8 00 F0 D6
0x74020878 28 18 00 96 74 00 74 03 E8 00 F0 7E 74 03 08 18
0x74020888 00 99 E8 00 F0 7E 08 2E 00 05 08 18 00 9A E8 00
0x74020898 F0 7E 78 11 00 31 08 18 00 9B E8 00 F0 D6 28 2E
0x740208A8 00 04 74 00 74 03 F0 10 08 18 00 11 74 00 F0 12
0x740208B8 08 18 00 67 74 00 EC 00 F0 D4 28 18 00 61 28 18
Task Control Block entry #9
tbrsv1[0]: B740A
tbrsv1[1]: E800F0D6
tbext: 28180061
tbpri: 74
tbid: 0 unused 0
tbstat: 740A
tbd0: F0100818
tbd1: 677400
tbd2: F0120818
tbd3: 717400
tbd4: EC00F0D4
tbd5: 2818006B
tba0: 28180061
tba1: 740AE800
tba2: F0D62818
tba3: 6B7400
tbssp: 740AF010
tbusp: 8180071
tbstack: 7400F012
tbflags: 818
tbrsv2[0]: 7B
tbrsv2[1]: 7400
tbrsv2[2]: EC00
tbrsv2[3]: F0D4
tbrsv2[4]: 2818
TCB #9 stack (176 bytes)
0x740AF010 00 75 28 18 00 6B 74 0A E8 00 F0 D6 28 18 00 75
0x740AF020 74 00 74 0A F0 10 08 18 00 7B 74 00 F0 12 08 18
0x740AF030 00 85 74 00 EC 00 F0 D4 28 18 00 7F 28 18 00 75
0x740AF040 74 0A E8 00 F0 D6 28 18 00 7F 74 00 74 0A F0 10
0x740AF050 08 18 00 85 74 00 F0 12 08 18 00 8F 74 00 EC 00
0x740AF060 F0 D4 28 18 00 89 28 18 00 7F 74 0A E8 00 F0 D6
0x740AF070 28 18 00 89 74 00 74 0A F0 10 08 18 00 8F 74 00
0x740AF080 F0 12 08 18 00 99 74 00 EC 00 F0 D4 28 18 00 93
0x740AF090 28 18 00 89 74 0A E8 00 F0 D6 28 18 00 93 74 00
0x740AF0A0 74 0A EC 00 F0 68 18 08 00 E1 7C 82 20 00 00 00
0x740AF0B0 08 18 00 36 E8 00 F0 7C 18 08 00 E5 08 18 00 37
Task Control Block entry #10
tbrsv1[0]: E800F07C
tbrsv1[1]: 180800E7
tbext: 8180038
tbpri: F0
tbid: D4
tbstat: 268C
tbd0: 28180051
tbd1: 7410E001
tbd2: 8004E002
tbd3: 88C3F0D6
tbd4: 281C00B2
tbd5: 74007403
tba0: 99819A81
tba1: EE00F0D6
tba2: 281B0086
tba3: 74007403
tbssp: F088F0D4
tbusp: 284600CE
tbstack: 281A0062
tbflags: 7406
tbrsv2[0]: F010
tbrsv2[1]: 817
tbrsv2[2]: F5
tbrsv2[3]: 7402
tbrsv2[4]: E01A
TCB #10 stack (176 bytes)
0xF088F0D4 C0 5F E0 1A 80 5F F0 1C 78 0B 00 B8 08 16 00 9C
0xF088F0E4 78 07 00 BC F0 7E 73 FA 08 17 00 F5 E0 1A 80 5F
0xF088F0F4 F0 1C 74 0D 08 16 00 9D 74 00 F0 7E 73 F9 08 17
0xF088F104 00 F5 E0 1A 80 5F F0 1C 74 20 08 16 00 9E 74 00
0xF088F114 F0 7E 73 F8 08 17 00 F5 E0 1A 80 5F F0 1C 74 18
0xF088F124 08 16 00 9F 73 FF F0 7E 73 F7 08 17 00 F5 E0 1A
0xF088F134 80 5F F0 1C 74 3C 08 16 00 A0 73 FF F0 7E 73 F6
0xF088F144 08 17 00 F5 E0 1A 80 5F F0 1C 74 3C 08 16 00 A1
0xF088F154 73 FF F0 7E 73 F5 08 17 00 F5 E0 1A 80 5F F0 10
0xF088F164 08 17 00 F5 74 02 EC 00 E0 1A C1 5F E8 00 F0 2C
0xF088F174 08 17 00 F5 E8 00 F0 D4 28 16 00 9C 28 1A 00 58
Task Control Block entry #11
tbrsv1[0]: 7406E800
tbrsv1[1]: F0D42816
tbext: 972813
tbpri: 0
tbid: DB
tbstat: 740B
tbd0: E01A815F
tbd1: EC00F022
tbd2: 84600D3
tbd3: 81100E1
tbd4: 81A0060
tbd5: E800F024
tba0: 84600D3
tba1: 8120013
tba2: 81A0061
tba3: E01AB25F
tbssp: E01A815F
tbusp: EC00F016
tbstack: 81A0061
tbflags: 81A
tbrsv2[0]: 5D
tbrsv2[1]: E800
tbrsv2[2]: F014
tbrsv2[3]: 81A
tbrsv2[4]: 60
TCB #11 stack (176 bytes)
0xE01A815F 08 1A 00 5D E4 00 E0 1A A2 5F E0 1A 81 5F EC 00
0xE01A816F F0 12 08 1A 00 58 08 46 00 CE E8 00 F0 12 08 1A
0xE01A817F 00 59 08 46 00 CF E8 00 F0 12 08 1A 00 5A 08 46
0xE01A818F 00 D0 E4 00 E0 1A A2 5F E0 1A 81 5F EC 00 F0 12
0xE01A819F 08 1A 00 5B 08 46 00 D1 E8 00 F0 12 08 1A 00 5C
0xE01A81AF 08 46 00 D2 E4 00 E0 1A A2 5F E0 1A 82 5F EC 00
0xE01A81BF F0 D4 28 1A 00 58 28 46 00 CE 74 06 E8 00 F0 D4
0xE01A81CF 28 1A 00 58 28 1A 00 6C 74 06 F0 D4 28 46 00 CE
0xE01A81DF 28 19 00 1A 74 06 F0 7E 08 16 00 9B 08 10 00 02
0xE01A81EF E0 01 8E 41 E0 19 C0 20 EC 00 E0 1A 82 5F E8 00
0xE01A81FF E0 01 8E 41 E8 00 E0 01 8D 00 E4 00 F0 30 01 41
Task Control Block entry #12
tbrsv1[0]: F088F088
tbrsv1[1]: E0018D00
tbext: E400F030
tbpri: 1
tbid: 41 CNET SMAC task
tbstat: F088
tbd0: 0
tbd1: 7
tbd2: 0
tbd3: 20
tbd4: 1
tbd5: 2FFF0000
tba0: 20208E
tba1: 3D4CC
tba2: 1FD02
tba3: 3D4C8
tbssp: 2047CE
tbusp: 0
tbstack: 20483C
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 210E
tbrsv2[2]: 20
tbrsv2[3]: 200E
tbrsv2[4]: 0
TCB #12 stack (176 bytes)
0x2047CE 00 00 00 00 FF BD FF 00 00 03 D4 C8 00 20 84 2A
0x2047DE 00 20 48 38 20 00 00 01 FD 1E 00 00 00 21 00 00
0x2047EE 00 01 00 00 00 03 00 02 09 60 00 07 00 00 00 00
0x2047FE 00 00 00 20 00 01 00 20 48 36 00 00 00 21 00 00
0x20480E 00 01 00 00 00 03 2F FF 00 00 00 00 00 00 FF BD
0x20481E FF 00 00 03 D4 CC 00 03 D4 CE 00 03 D4 C8 D4 C8
0x20482E 00 00 00 01 00 20 04 1C 20 00 00 20 04 1C DE AD
0x20483E BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20484E 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20485E 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20486E 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #13
tbrsv1[0]: 202D9C
tbrsv1[1]: 202D9C
tbext: 0
tbpri: 23
tbid: 22 Remote read request task
tbstat: 40
tbd0: 0
tbd1: 3
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: 2FFF0000
tba0: 204BEA
tba1: 3D4D4
tba2: 3D4D6
tba3: 3D4D0
tbssp: 204BA2
tbusp: 0
tbstack: 204BF2
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 208E
tbrsv2[2]: 20
tbrsv2[3]: 1F8E
tbrsv2[4]: 0
TCB #13 stack (176 bytes)
0x204BA2 00 00 00 00 FF BD FF 00 00 03 D4 D0 00 20 84 2A
0x204BB2 00 20 4B EE 20 00 00 01 FC 5A 00 00 00 22 00 01
0x204BC2 A4 7C 00 03 00 00 00 00 00 20 4B EA 00 00 00 22
0x204BD2 00 00 00 01 00 00 00 03 00 03 D4 D4 00 03 D4 D6
0x204BE2 D4 D0 00 20 84 2A 00 20 00 00 20 00 00 20 04 1C
0x204BF2 DE AD BE EF 00 00 00 00 00 00 00 00 00 00 00 00
0x204C02 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204C12 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204C22 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204C32 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204C42 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #14
tbrsv1[0]: 201D8E
tbrsv1[1]: 202B26
tbext: 0
tbpri: 41
tbid: 23 Make PCL message task
tbstat: 200
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 48000000
tbd4: 1
tbd5: 2FFF0000
tba0: 201A8E
tba1: 3D52C
tba2: 3D52E
tba3: 3D528
tbssp: 207466
tbusp: 0
tbstack: 2074C4
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1B0E
tbrsv2[2]: 20
tbrsv2[3]: 1A0E
tbrsv2[4]: 0
TCB #14 stack (176 bytes)
0x207466 00 00 00 00 FF BD FF 00 00 03 D5 28 00 20 84 2A
0x207476 00 20 74 C0 20 00 00 01 FD 1E 00 00 00 23 00 00
0x207486 00 01 00 00 00 03 00 03 13 A2 00 01 00 00 00 00
0x207496 48 00 00 00 00 01 00 20 74 B6 00 00 00 23 00 00
0x2074A6 00 01 00 03 D5 2C 00 03 D5 2E 00 03 D5 28 D5 28
0x2074B6 00 20 84 2A 00 20 04 1C 20 00 00 20 04 1C DE AD
0x2074C6 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2074D6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2074E6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2074F6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207506 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #15
tbrsv1[0]: 202A46
tbrsv1[1]: 202A46
tbext: 0
tbpri: 40
tbid: 24 Serial port get buffer task
tbstat: 200
tbd0: 0
tbd1: 8
tbd2: 0
tbd3: 1
tbd4: 0
tbd5: 2FFF0000
tba0: 201E8E
tba1: 3D4EC
tba2: 3D4EE
tba3: 3D4E8
tbssp: 2056C4
tbusp: 0
tbstack: 205714
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1F0E
tbrsv2[2]: 20
tbrsv2[3]: 1E0E
tbrsv2[4]: 0
TCB #15 stack (176 bytes)
0x2056C4 00 00 00 00 FF BD FF 00 00 03 D4 E8 00 20 84 2A
0x2056D4 00 20 57 10 20 00 00 01 FD 1E 00 00 00 24 00 00
0x2056E4 00 01 00 00 00 03 00 01 54 F8 00 08 00 00 00 00
0x2056F4 00 00 00 01 00 00 00 20 57 0E 00 00 00 24 00 00
0x205704 00 01 00 03 D4 EC 00 03 D4 EE 20 00 00 20 04 1C
0x205714 DE AD BE EF 00 00 00 00 00 00 00 00 00 00 00 00
0x205724 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205734 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205744 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205754 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205764 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #16
tbrsv1[0]: 2029E6
tbrsv1[1]: 2029E6
tbext: 0
tbpri: 3F
tbid: 25 Serial port modem control task
tbstat: 200
tbd0: 0
tbd1: B
tbd2: 0
tbd3: E
tbd4: 0
tbd5: 2FFF00FD
tba0: 209C7A
tba1: 209C7A
tba2: 209C54
tba3: 209C55
tbssp: 205A54
tbusp: 0
tbstack: 205ACA
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1E8E
tbrsv2[2]: 20
tbrsv2[3]: 1D8E
tbrsv2[4]: 0
TCB #16 stack (176 bytes)
0x205A54 00 00 00 00 FF BD FF 00 00 20 9C 7A 00 20 84 2A
0x205A64 00 20 5A A0 20 00 00 01 FD 1E 00 00 00 00 00 00
0x205A74 00 01 00 00 00 12 00 01 39 62 00 0B 00 00 00 00
0x205A84 00 00 00 0E 00 00 00 20 5A 9E 00 00 00 01 00 00
0x205A94 00 B2 00 00 00 12 00 16 00 00 9C 54 00 20 5A C6
0x205AA4 00 01 35 74 00 00 00 25 00 00 00 01 00 00 00 03
0x205AB4 2F FF 00 00 00 03 D4 F4 00 03 D4 F6 00 03 D4 F0
0x205AC4 00 00 00 20 04 1C DE AD BE EF 00 00 00 00 00 00
0x205AD4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205AE4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205AF4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #17
tbrsv1[0]: 202966
tbrsv1[1]: 202966
tbext: 0
tbpri: 1E
tbid: 27 EEPROM task
tbstat: 200
tbd0: 0
tbd1: F
tbd2: 0
tbd3: F
tbd4: 0
tbd5: 2FFF0000
tba0: 201A0E
tba1: 20A968
tba2: 3D536
tba3: 3D530
tbssp: 2077D4
tbusp: 0
tbstack: 20787A
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1A8E
tbrsv2[2]: 20
tbrsv2[3]: 198E
tbrsv2[4]: 0
TCB #17 stack (176 bytes)
0x2077D4 00 00 00 00 FF BD FF 00 00 03 D5 30 00 20 84 2A
0x2077E4 00 20 78 76 20 00 00 01 FD 1E 00 00 00 27 00 00
0x2077F4 00 01 00 00 00 03 00 03 A4 A6 00 0F 00 00 00 00
0x207804 00 00 00 0F 00 00 00 20 78 74 00 00 00 27 00 00
0x207814 00 01 00 00 00 03 2F FF 00 00 00 00 00 00 FF BD
0x207824 FF 00 00 03 D5 34 00 03 D5 36 00 03 D5 30 00 01
0x207834 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207844 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207854 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207864 FF BD FF 00 00 03 D5 30 00 20 84 2A 00 20 04 1C
0x207874 20 00 00 20 04 1C DE AD BE EF 00 00 00 00 00 00
Task Control Block entry #18
tbrsv1[0]: 202DC8
tbrsv1[1]: 202DC8
tbext: 0
tbpri: 23
tbid: 28 Rung cache remote mod task
tbstat: 40
tbd0: 0
tbd1: 8
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: 2FFF0000
tba0: 207C26
tba1: 3ACA6
tba2: 3D53E
tba3: 3D538
tbssp: 207BF2
tbusp: 0
tbstack: 207C30
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1A0E
tbrsv2[2]: 20
tbrsv2[3]: 190E
tbrsv2[4]: 0
TCB #18 stack (176 bytes)
0x207BF2 00 00 00 00 FF BD FF 00 00 03 D5 38 00 20 84 2A
0x207C02 00 20 7C 2C 20 00 00 01 FC 5A 00 00 00 28 00 02
0x207C12 7C 9E 00 08 00 00 00 00 00 20 7C 26 00 03 D5 3C
0x207C22 00 20 84 2A 00 00 04 1C 20 00 00 20 04 1C DE AD
0x207C32 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C42 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C52 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C62 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C72 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C82 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207C92 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #19
tbrsv1[0]: 20230E
tbrsv1[1]: 20230E
tbext: 0
tbpri: 41
tbid: 29 COPRO interface task
tbstat: 0
tbd0: 0
tbd1: 19
tbd2: 0
tbd3: 7
tbd4: 0
tbd5: 2FFF0000
tba0: 2404A2
tba1: 207F8A
tba2: 207F86
tba3: 207F36
tbssp: 207FA8
tbusp: 0
tbstack: 207FE6
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 198E
tbrsv2[2]: 20
tbrsv2[3]: 188E
tbrsv2[4]: 0
TCB #19 stack (176 bytes)
0x207FA8 00 00 00 20 E6 AE 00 20 E6 B4 00 00 00 00 E6 AA
0x207FB8 00 01 00 20 04 1C 00 00 93 02 00 24 04 A2 00 00
0x207FC8 00 00 00 20 E5 D0 00 20 E6 A8 00 20 E6 A6 00 00
0x207FD8 91 F8 00 03 D5 44 00 03 D5 46 00 03 D5 40 DE AD
0x207FE8 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x207FF8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208008 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208018 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208028 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208038 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x208048 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #20
tbrsv1[0]: 20210E
tbrsv1[1]: 201A8E
tbext: 0
tbpri: 2F
tbid: 45 RIO IOT task
tbstat: 200
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 4000000
tbd4: 0
tbd5: 2FFF0000
tba0: 205E7A
tba1: 3ACA6
tba2: 3D4FE
tba3: 3D4F8
tbssp: 205E34
tbusp: 0
tbstack: 205E80
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1E0E
tbrsv2[2]: 20
tbrsv2[3]: 1D0E
tbrsv2[4]: 0
TCB #20 stack (176 bytes)
0x205E34 00 00 00 00 FF BD FF 00 00 03 D4 F8 00 20 84 2A
0x205E44 00 20 5E 7C 20 00 00 01 FD 1E 00 00 00 45 00 00
0x205E54 00 01 00 00 00 03 00 03 55 EA 00 01 00 00 00 00
0x205E64 04 00 00 00 00 00 00 20 5E 7A 00 00 00 45 00 00
0x205E74 00 01 00 03 D4 FC 00 00 00 20 04 1C DE AD BE EF
0x205E84 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205E94 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205EA4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205EB4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205EC4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205ED4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #21
tbrsv1[0]: 203038
tbrsv1[1]: 203038
tbext: 0
tbpri: 41
tbid: 50 COPRO slow PCCC task
tbstat: 40
tbd0: 0
tbd1: 32
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: 2FFF0000
tba0: 208396
tba1: 3ACA6
tba2: 240376
tba3: 240506
tbssp: 20835A
tbusp: 0
tbstack: 20839C
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 190E
tbrsv2[2]: 20
tbrsv2[3]: D74
tbrsv2[4]: 0
TCB #21 stack (176 bytes)
0x20835A 00 00 00 00 FF BD FF 00 00 24 03 76 00 20 84 2A
0x20836A 00 20 83 98 20 00 00 01 FC 5A 00 00 00 50 00 00
0x20837A 7F F8 00 32 00 00 00 00 00 20 83 96 00 03 D5 4C
0x20838A 00 03 D5 4E 00 03 D5 48 00 20 04 1C 00 05 00 20
0x20839A 04 1C 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083AA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083BA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083CA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083DA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083EA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2083FA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Current task (COPRO interface task) stack (506 bytes):
0x207DF0 00 02 5E 86 00 20 7E C4 00 20 7E CE 00 20 7E 38
0x207E00 08 7E 00 20 7E 3E 00 00 00 00 00 00 08 7E 00 00
0x207E10 00 02 2F FF 08 82 00 00 00 00 FF BD 00 00 00 20
0x207E20 7E CE 00 20 7E DE 00 20 7E E0 7E CE 00 20 84 2A
0x207E30 00 20 7E 86 00 24 19 32 00 24 19 39 00 00 00 09
0x207E40 08 82 00 00 00 02 00 20 7E CE 00 02 03 04 00 20
0x207E50 7E 86 00 02 53 7C 00 20 7E C4 00 20 7E CE 00 20
0x207E60 7E 80 08 7E 00 20 7E 84 00 00 00 00 00 00 00 00
0x207E70 00 00 BF FF 00 00 00 00 00 19 CF 38 00 20 7F 86
0x207E80 00 00 BF FF 00 00 00 00 00 19 CF 38 00 20 2A 66
0x207E90 00 00 00 01 00 00 00 0F 00 19 CF 38 00 20 7F 86
0x207EA0 00 20 7E CC 00 20 2A 66 00 00 00 01 00 00 00 00
0x207EB0 00 19 CF 38 00 20 7F 86 00 03 7B E4 00 00 00 01
0x207EC0 00 00 00 07 00 20 84 08 00 20 7F 86 00 20 7F 18
0x207ED0 20 00 00 01 FB BE 00 00 00 16 00 00 00 58 00 20
0x207EE0 7F 86 00 03 C1 70 00 20 7F 0E 00 00 00 20 7F 0C
0x207EF0 00 00 00 50 00 00 00 FF 00 03 00 04 00 01 7F 91
0x207F00 00 24 04 B7 00 20 7D F0 00 04 00 01 00 00 00 29
0x207F10 00 41 00 00 00 20 7F 18 00 20 E4 0E 00 03 AC D0
0x207F20 00 00 00 C5 00 00 00 BF 00 20 7E EE 00 19 CF 38
0x207F30 00 03 B1 24 00 8A 00 10 20 09 00 00 00 C2 01 B4
0x207F40 00 00 00 20 7F 94 00 00 68 66 00 20 7F 94 00 00
0x207F50 66 C8 00 20 7F 86 00 00 00 29 00 00 00 01 00 00
0x207F60 00 03 2F FF 00 00 00 24 04 A2 00 24 04 3E 00 00
0x207F70 6B 10 00 20 84 2A 00 24 10 A6 20 00 00 00 00 21
0x207F80 00 24 21 B2 00 20 30 AE 00 04 00 01 01 01 00 00
0x207F90 00 24 04 A2 00 20 7F BA 00 00 7F 24 00 24 04 A2
0x207FA0 00 24 04 3E 00 00 00 00 00 00 00 20 E6 AE 00 20
0x207FB0 E6 B4 00 00 00 00 E6 AA 00 01 00 20 04 1C 00 00
0x207FC0 93 02 00 24 04 A2 00 00 00 00 00 20 E5 D0 00 20
0x207FD0 E6 A8 00 20 E6 A6 00 00 91 F8 00 03 D5 44 00 03
0x207FE0 D5 46 00 03 D5 40 DE AD BE EF
Interrupt stack (252 bytes):
0x207EE8 00 03 C1 C2 00 20 7F 14 00 00 00 50 00 00 00 FF
0x207EF8 00 03 00 04 00 01 7F 91 00 24 04 B7 00 20 7E E8
0x207F08 00 04 00 01 00 00 00 29 00 41 00 00 00 20 7F 18
0x207F18 00 20 E4 0E 00 03 AC D0 00 00 00 C5 00 00 00 BF
0x207F28 00 20 7E EE 00 19 CF 38 00 03 B1 24 00 8A 00 10
0x207F38 20 09 00 00 00 C2 01 B4 00 00 00 20 7F 94 00 00
0x207F48 68 66 00 20 7F 94 00 00 66 C8 00 20 7F 86 00 00
0x207F58 00 29 00 00 00 01 00 00 00 03 2F FF 00 00 00 24
0x207F68 04 A2 00 24 04 3E 00 00 6B 10 00 20 84 2A 00 24
0x207F78 10 A6 20 00 00 00 00 21 00 24 21 B2 00 20 30 AE
0x207F88 00 04 00 01 01 01 00 00 00 24 04 A2 00 20 7F BA
0x207F98 00 00 7F 24 00 24 04 A2 00 24 04 3E 00 00 00 00
0x207FA8 00 00 00 20 E6 AE 00 20 E6 B4 00 00 00 00 E6 AA
0x207FB8 00 01 00 20 04 1C 00 00 93 02 00 24 04 A2 00 00
0x207FC8 00 00 00 20 E5 D0 00 20 E6 A8 00 20 E6 A6 00 00
0x207FD8 91 F8 00 03 D5 44 00 03 D5 46 00 03
=============================================================================
UPB saved tasks and stack data:
Task Control Block entry #0
tbrsv1[0]: 20159C
tbrsv1[1]: 20159C
tbext: 0
tbpri: 14
tbid: 1 cp_control_processor task
tbstat: 0
tbd0: 0
tbd1: 0
tbd2: 33
tbd3: 105
tbd4: 1
tbd5: FFFFDFBF
tba0: 199214
tba1: 200428
tba2: 206C92
tba3: 1988B6
tbssp: 202576
tbusp: 0
tbstack: 20260A
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 582
tbrsv2[2]: 20
tbrsv2[3]: 151C
tbrsv2[4]: 0
TCB #0 stack (176 bytes)
0x202576 00 00 00 00 00 02 00 00 00 00 00 19 88 DC 00 00
0x202586 00 00 00 20 25 C4 00 00 85 EC 00 19 88 DC 00 00
0x202596 00 05 00 00 00 05 00 00 E3 FF FF FF DF BF DF 7E
0x2025A6 FF FF FD FF FB FF 00 20 04 28 00 20 6C 92 00 19
0x2025B6 88 B6 00 00 00 00 00 00 00 00 00 19 72 14 00 20
0x2025C6 25 E2 00 01 85 98 00 00 00 05 00 00 00 05 00 13
0x2025D6 00 00 00 19 C6 DC 00 01 75 AE 00 05 00 20 26 06
0x2025E6 00 01 81 54 00 05 00 00 00 01 00 00 00 01 00 00
0x2025F6 00 03 00 01 D5 48 00 01 D5 4A 00 01 D5 44 20 00
0x202606 00 20 04 1C DE AD BE EF 00 00 00 00 00 00 00 00
0x202616 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #1
tbrsv1[0]: 201C74
tbrsv1[1]: 201C74
tbext: 0
tbpri: A
tbid: 2 cp_shutdown_system task
tbstat: 200
tbd0: 0
tbd1: 0
tbd2: 0
tbd3: 800
tbd4: 1
tbd5: FFFFDFBF
tba0: 20151C
tba1: 18828
tba2: 19DE98
tba3: 1D54C
tbssp: 20294C
tbusp: 0
tbstack: 2029C0
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 159C
tbrsv2[2]: 20
tbrsv2[3]: 149C
tbrsv2[4]: 0
TCB #1 stack (176 bytes)
0x20294C DF 7E FF FF FD FF FB FF 00 01 D5 4C 00 20 04 2C
0x20295C 00 20 29 92 20 00 00 01 71 9C 00 00 00 00 00 00
0x20296C 00 01 00 00 00 03 00 01 88 52 00 00 00 00 00 00
0x20297C 00 00 08 00 00 01 00 20 29 8C 00 00 08 00 00 00
0x20298C 00 00 00 00 00 00 00 20 29 BC 00 01 8A B8 00 00
0x20299C 08 00 00 00 00 00 00 00 00 02 00 00 00 01 00 00
0x2029AC 00 03 00 01 D5 50 00 01 D5 52 00 20 04 1C 20 00
0x2029BC 00 20 04 1C DE AD BE EF 00 00 00 00 00 00 00 00
0x2029CC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2029DC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2029EC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #2
tbrsv1[0]: 20149C
tbrsv1[1]: 20149C
tbext: 0
tbpri: 41
tbid: 3 cp_diagnostics task
tbstat: 0
tbd0: 0
tbd1: 0
tbd2: 41
tbd3: 1
tbd4: 7
tbd5: AAAAAAAA
tba0: 20149C
tba1: 1D558
tba2: 1D55A
tba3: 210000
tbssp: 202D5C
tbusp: 0
tbstack: 202D76
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 151C
tbrsv2[2]: 20
tbrsv2[3]: 141C
tbrsv2[4]: 0
TCB #2 stack (176 bytes)
0x202D5C 00 00 00 00 C3 6D A7 CF 00 20 21 D4 00 04 00 00
0x202D6C 00 00 21 D4 20 00 00 01 9D 96 DE AD BE EF 00 00
0x202D7C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202D8C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202D9C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DAC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DBC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DCC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DDC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DEC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202DFC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #3
tbrsv1[0]: 201D3A
tbrsv1[1]: 201D3A
tbext: 0
tbpri: B
tbid: 11 User Program Control Task
tbstat: 40
tbd0: 0
tbd1: D2560014
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 206E46
tba1: 206E3C
tba2: 1D56A
tba3: 1D564
tbssp: 2034A8
tbusp: 0
tbstack: 2034E2
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 141C
tbrsv2[2]: 20
tbrsv2[3]: 131C
tbrsv2[4]: 0
TCB #3 stack (176 bytes)
0x2034A8 DF 7E FF FF FD FF FB FF 00 20 6E 9A 00 20 04 2C
0x2034B8 00 20 34 DE 20 00 00 01 70 D8 00 00 00 03 00 00
0x2034C8 8F 30 00 14 00 00 00 00 00 20 34 DC 00 00 00 11
0x2034D8 00 01 D5 68 00 00 00 20 04 1C DE AD BE EF 00 00
0x2034E8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2034F8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203508 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203518 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203528 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203538 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203548 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #4
tbrsv1[0]: 201754
tbrsv1[1]: 201754
tbext: 0
tbpri: F
tbid: 12 PII Task
tbstat: 2
tbd0: 0
tbd1: 0
tbd2: 12
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 206E62
tba1: 1988B6
tba2: 198B34
tba3: 1D564
tbssp: 20436E
tbusp: 0
tbstack: 2043BA
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 121C
tbrsv2[2]: 20
tbrsv2[3]: 111C
tbrsv2[4]: 0
TCB #4 stack (176 bytes)
0x20436E DF 7E FF FF FD FF FB FF 00 18 8D 78 00 20 04 2C
0x20437E 00 20 43 B6 20 00 00 01 70 7E 00 00 A8 DC 00 20
0x20438E 6E 62 00 00 00 00 00 20 43 B4 00 00 00 12 00 00
0x20439E 00 01 00 00 00 03 FF FF DF BF DF 7E FF FF 00 20
0x2043AE 6E 3C 00 01 D5 6A 20 00 00 20 34 CC DE AD BE EF
0x2043BE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2043CE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2043DE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2043EE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2043FE 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20440E 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #5
tbrsv1[0]: 201734
tbrsv1[1]: 201734
tbext: 0
tbpri: 10
tbid: 13 STI Task
tbstat: 2
tbd0: 0
tbd1: 0
tbd2: 13
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 206E5E
tba1: 1988B6
tba2: 198A08
tba3: 1D564
tbssp: 204728
tbusp: 0
tbstack: 204770
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 119C
tbrsv2[2]: 20
tbrsv2[3]: 582
tbrsv2[4]: 0
TCB #5 stack (176 bytes)
0x204728 DF 7E FF FF FD FF FB FF 00 18 8D 78 00 20 04 2C
0x204738 00 20 47 6C 20 00 00 01 70 7E 00 00 8D 6A 00 20
0x204748 6E 5E 00 00 00 00 00 20 47 6A 00 00 00 13 00 00
0x204758 00 01 00 00 00 03 FF FF DF BF 00 20 6E 3C 00 01
0x204768 D5 6A 20 00 00 20 34 CC 00 00 00 00 00 00 00 00
0x204778 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204788 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204798 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2047A8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2047B8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2047C8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #6
tbrsv1[0]: 201D76
tbrsv1[1]: 201D76
tbext: 0
tbpri: C
tbid: 14 System RTE Task
tbstat: 40
tbd0: 0
tbd1: 15
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 20131C
tba1: 1D570
tba2: 206E5A
tba3: 1D56C
tbssp: 203846
tbusp: 0
tbstack: 203898
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 139C
tbrsv2[2]: 20
tbrsv2[3]: 129C
tbrsv2[4]: 0
TCB #6 stack (176 bytes)
0x203846 DF 7E FF FF FD FF FB FF 00 01 D5 6C 00 20 04 2C
0x203856 00 20 38 94 20 00 00 01 70 D8 00 00 00 14 00 00
0x203866 9F 6A 00 15 00 00 00 00 00 20 38 92 00 01 D5 70
0x203876 00 01 D5 72 00 01 D5 6C DF 7E FF FF FD FF FB FF
0x203886 00 01 D5 6C 00 20 04 2C 00 20 04 1C 20 00 00 20
0x203896 04 1C DE AD BE EF 00 00 00 00 00 00 00 00 00 00
0x2038A6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2038B6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2038C6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2038D6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2038E6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #7
tbrsv1[0]: 201774
tbrsv1[1]: 201774
tbext: 0
tbpri: D
tbid: 15 User's RTE Task
tbstat: 2
tbd0: 0
tbd1: 0
tbd2: 15
tbd3: 1
tbd4: E3FF
tbd5: FFFFDFBF
tba0: 206D04
tba1: 130000
tba2: 198C60
tba3: 175AE
tbssp: 203FAC
tbusp: 0
tbstack: 204004
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 129C
tbrsv2[2]: 20
tbrsv2[3]: 119C
tbrsv2[4]: 0
TCB #7 stack (176 bytes)
0x203FAC DF 7E FF FF FD FF FB FF 00 19 88 B0 00 20 04 2C
0x203FBC 00 20 40 00 20 00 00 01 70 7E 00 00 A2 02 00 20
0x203FCC 6D 04 00 00 00 00 00 20 3F FE 00 00 00 15 00 00
0x203FDC 00 01 00 00 E3 FF 00 13 00 00 00 19 88 B6 00 01
0x203FEC 75 AE FD FF FB FF 00 19 88 B0 00 20 04 2C 00 20
0x203FFC 25 D8 20 00 00 20 25 D8 DE AD BE EF 00 00 00 00
0x20400C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20401C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20402C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20403C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20404C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #8
tbrsv1[0]: 201DB2
tbrsv1[1]: 201DB2
tbext: 0
tbpri: 23
tbid: 22 Remote read request task
tbstat: 40
tbd0: 0
tbd1: 4
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 203124
tba1: 1D560
tba2: 1D562
tba3: 1D55C
tbssp: 2030E0
tbusp: 0
tbstack: 20312C
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 149C
tbrsv2[2]: 20
tbrsv2[3]: 139C
tbrsv2[4]: 0
TCB #8 stack (176 bytes)
0x2030E0 DF 7E FF FF FD FF FB FF 00 01 D5 5C 00 20 04 2C
0x2030F0 00 20 31 28 20 00 00 01 70 D8 00 00 00 22 00 00
0x203100 EC 62 00 04 00 00 00 00 00 20 31 24 00 00 00 22
0x203110 00 00 00 01 00 01 D5 60 00 01 D5 62 D5 5C 00 20
0x203120 04 2C 00 20 00 00 20 00 00 20 04 1C DE AD BE EF
0x203130 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203140 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203150 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203160 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203170 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203180 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #9
tbrsv1[0]: 201DDE
tbrsv1[1]: 201DDE
tbext: 0
tbpri: 23
tbid: 28 Rung cache remote mod task
tbstat: 40
tbd0: 0
tbd1: 8
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFFDFBF
tba0: 203C44
tba1: 1949E
tba2: 1D57A
tba3: 1D574
tbssp: 203C10
tbusp: 0
tbstack: 203C4E
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 131C
tbrsv2[2]: 20
tbrsv2[3]: 121C
tbrsv2[4]: 0
TCB #9 stack (176 bytes)
0x203C10 DF 7E FF FF FD FF FB FF 00 01 D5 74 00 20 04 2C
0x203C20 00 20 3C 4A 20 00 00 01 70 D8 00 00 00 28 00 01
0x203C30 11 5A 00 08 00 00 00 00 00 20 3C 44 00 01 D5 78
0x203C40 00 20 04 2C 00 00 04 1C 20 00 00 20 04 1C DE AD
0x203C50 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203C60 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203C70 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203C80 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203C90 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203CA0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203CB0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Current task (cp_control_processor task) stack (506 bytes):
0x202414 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202424 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202434 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202444 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202454 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202464 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202474 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202484 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202494 00 00 00 00 22 00 00 00 00 60 00 20 05 DC 20 00
0x2024A4 22 00 00 00 19 01 00 20 05 DC 22 00 22 00 00 00
0x2024B4 DF 7E FF FF 00 00 00 00 00 19 22 00 00 00 06 D8
0x2024C4 00 20 25 04 20 09 00 00 BF 72 00 00 80 00 00 00
0x2024D4 00 00 00 00 00 00 FF FF DF 00 00 01 53 44 DF 7E
0x2024E4 FF FF FD FF FB 00 00 20 3C BE 00 20 04 2C 00 20
0x2024F4 25 3E 27 00 00 01 70 3C 00 00 00 0A 00 00 00 58
0x202504 00 19 88 DC 00 01 A2 5A 00 20 25 34 00 00 00 20
0x202514 25 32 00 00 00 00 00 00 0F 52 00 00 00 01 00 20
0x202524 25 84 00 00 00 00 00 20 24 14 88 DC 00 19 00 00
0x202534 00 01 00 14 00 00 00 20 25 3E 00 20 25 88 00 01
0x202544 9A 00 00 00 00 00 00 00 00 00 00 18 31 8C 00 18
0x202554 8D 78 00 01 92 B4 00 01 20 08 00 00 9C 9C 00 18
0x202564 8E 18 00 19 88 B6 00 19 88 DC 00 00 98 2E 00 20
0x202574 25 84 00 00 00 00 00 02 00 00 00 00 00 19 88 DC
0x202584 00 00 00 00 00 20 25 C4 00 00 85 EC 00 19 88 DC
0x202594 00 00 00 05 00 00 00 05 00 00 E3 FF FF FF DF BF
0x2025A4 DF 7E FF FF FD FF FB FF 00 20 04 28 00 20 6C 92
0x2025B4 00 19 88 B6 00 00 00 00 00 00 00 00 00 19 72 14
0x2025C4 00 20 25 E2 00 01 85 98 00 00 00 05 00 00 00 05
0x2025D4 00 13 00 00 00 19 C6 DC 00 01 75 AE 00 05 00 20
0x2025E4 26 06 00 01 81 54 00 05 00 00 00 01 00 00 00 01
0x2025F4 00 00 00 03 00 01 D5 48 00 01 D5 4A 00 01 D5 44
0x202604 20 00 00 20 04 1C DE AD BE EF
Interrupt stack (252 bytes):
0x20250E 00 01 A2 AC 00 20 25 3A 00 00 00 00 00 00 0F 52
0x20251E 00 00 00 01 00 20 25 84 00 00 00 00 00 20 25 0E
0x20252E 88 DC 00 19 00 00 00 01 00 14 00 00 00 20 25 3E
0x20253E 00 20 25 88 00 01 9A 00 00 00 00 00 00 00 00 00
0x20254E 00 18 31 8C 00 18 8D 78 00 01 92 B4 00 01 20 08
0x20255E 00 00 9C 9C 00 18 8E 18 00 19 88 B6 00 19 88 DC
0x20256E 00 00 98 2E 00 20 25 84 00 00 00 00 00 02 00 00
0x20257E 00 00 00 19 88 DC 00 00 00 00 00 20 25 C4 00 00
0x20258E 85 EC 00 19 88 DC 00 00 00 05 00 00 00 05 00 00
0x20259E E3 FF FF FF DF BF DF 7E FF FF FD FF FB FF 00 20
0x2025AE 04 28 00 20 6C 92 00 19 88 B6 00 00 00 00 00 00
0x2025BE 00 00 00 19 72 14 00 20 25 E2 00 01 85 98 00 00
0x2025CE 00 05 00 00 00 05 00 13 00 00 00 19 C6 DC 00 01
0x2025DE 75 AE 00 05 00 20 26 06 00 01 81 54 00 05 00 00
0x2025EE 00 01 00 00 00 01 00 00 00 03 00 01 D5 48 00 01
0x2025FE D5 4A 00 01 D5 44 20 00 00 20 04 1C
=============================================================================
UPC saved tasks and stack data:
Task Control Block entry #0
tbrsv1[0]: 201E38
tbrsv1[1]: 201E38
tbext: 0
tbpri: 41
tbid: 3 cp_diagnostics task
tbstat: 0
tbd0: 0
tbd1: 0
tbd2: 41
tbd3: 1
tbd4: A
tbd5: AAAAAAAA
tba0: 201E38
tba1: 2E234
tba2: 2E236
tba3: 210000
tbssp: 202F5A
tbusp: 0
tbstack: 202F74
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: C9E
tbrsv2[2]: 20
tbrsv2[3]: 1DB8
tbrsv2[4]: 0
TCB #0 stack (176 bytes)
0x202F5A 00 00 00 00 58 BB 70 DA 00 20 CF 4C 00 04 00 00
0x202F6A 00 00 CF 4C 20 00 00 02 D2 52 DE AD BE EF 00 00
0x202F7A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202F8A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202F9A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FAA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FBA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FCA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FDA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FEA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x202FFA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #1
tbrsv1[0]: 201A38
tbrsv1[1]: 201A38
tbext: 0
tbpri: 2D
tbid: 6 rio_pg_srvc_task
tbstat: 20
tbd0: 0
tbd1: 1
tbd2: 2
tbd3: 1
tbd4: 3
tbd5: 20
tba0: 20D020
tba1: 30BBA9
tba2: 308151
tba3: 20BDA2
tbssp: 204CC0
tbusp: 0
tbstack: 204D24
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1AB8
tbrsv2[2]: 20
tbrsv2[3]: 19B8
tbrsv2[4]: 0
TCB #1 stack (176 bytes)
0x204CC0 00 00 00 00 FF FB FF 00 00 20 CF B7 00 20 84 2A
0x204CD0 00 20 4D 20 20 00 00 02 C6 90 00 02 75 58 00 00
0x204CE0 00 01 00 00 00 06 00 00 00 01 00 00 00 03 FF FF
0x204CF0 00 00 00 02 E2 74 00 02 E2 76 00 02 E2 70 00 20
0x204D00 D0 62 00 20 D0 52 00 20 D0 6A 00 20 D0 56 00 20
0x204D10 CF B9 00 30 01 D1 00 20 84 2A 00 20 CF B7 00 00
0x204D20 00 20 04 20 DE AD BE EF 00 00 00 00 00 00 00 00
0x204D30 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204D40 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204D50 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204D60 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #2
tbrsv1[0]: 20268E
tbrsv1[1]: 20268E
tbext: 0
tbpri: 41
tbid: 7 rio_async_task
tbstat: 40
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFF0000
tba0: 2050CC
tba1: 19B75E
tba2: 19B75E
tba3: 2E278
tbssp: 205088
tbusp: 0
tbstack: 2050DA
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1A38
tbrsv2[2]: 20
tbrsv2[3]: 1938
tbrsv2[4]: 0
TCB #2 stack (176 bytes)
0x205088 00 00 00 00 FF FB FF 00 00 18 8D 78 00 20 84 2A
0x205098 00 20 50 D6 20 00 00 02 C4 D8 00 00 00 07 00 00
0x2050A8 2C 50 00 01 00 00 00 00 00 20 50 CC 00 00 00 07
0x2050B8 00 00 00 01 00 02 E2 7C 00 02 E2 7E 00 02 E2 78
0x2050C8 00 19 CD 66 00 00 84 2A 00 20 04 20 20 00 00 20
0x2050D8 04 20 DE AD BE EF 00 00 00 00 00 00 00 00 00 00
0x2050E8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2050F8 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205108 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205118 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205128 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #3
tbrsv1[0]: 202726
tbrsv1[1]: 202726
tbext: 0
tbpri: 41
tbid: 8 rio_start_btx_task
tbstat: 40
tbd0: 0
tbd1: D
tbd2: 0
tbd3: 1
tbd4: 100
tbd5: FFFF0002
tba0: 30A1D9
tba1: 19B800
tba2: 207BB4
tba3: 30A1D9
tbssp: 205426
tbusp: 0
tbstack: 205490
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 19B8
tbrsv2[2]: 20
tbrsv2[3]: 18B8
tbrsv2[4]: 0
TCB #3 stack (176 bytes)
0x205426 00 00 00 0E FF FB FF 00 00 30 A1 D9 00 20 84 2A
0x205436 00 20 54 8C 20 00 00 02 C4 D8 00 00 00 01 00 00
0x205446 12 1E 00 0D 00 00 00 00 00 20 54 7E 00 00 00 08
0x205456 00 00 00 01 00 00 00 03 FF FF 00 00 00 00 00 00
0x205466 FF FB FF 00 00 02 E2 84 00 02 E2 86 00 02 E2 80
0x205476 00 00 00 00 00 41 00 81 00 00 00 18 33 8C 00 18
0x205486 09 72 00 30 C0 E9 00 20 04 20 DE AD BE EF 00 00
0x205496 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2054A6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2054B6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2054C6 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #4
tbrsv1[0]: 2026D2
tbrsv1[1]: 2026D2
tbext: 0
tbpri: 41
tbid: 9 rio_cplt_btx
tbstat: 60
tbd0: 0
tbd1: B
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFF0000
tba0: 307F09
tba1: 2E28C
tba2: 2E28E
tba3: 2E288
tbssp: 20581A
tbusp: 0
tbstack: 205846
tbflags: 8000
tbrsv2[0]: 20
tbrsv2[1]: 1938
tbrsv2[2]: 20
tbrsv2[3]: 1838
tbrsv2[4]: 0
TCB #4 stack (176 bytes)
0x20581A 09 72 00 20 84 2A 00 20 58 42 20 00 00 02 C4 D8
0x20582A 00 19 B7 5E 00 00 1B F8 00 0B 00 00 00 00 00 20
0x20583A 58 40 00 00 00 09 00 00 00 20 04 20 DE AD BE EF
0x20584A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20585A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20586A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20587A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20588A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20589A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2058AA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2058BA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #5
tbrsv1[0]: 201838
tbrsv1[1]: 201838
tbext: 0
tbpri: 37
tbid: B timing task
tbstat: 20
tbd0: 0
tbd1: 14
tbd2: E
tbd3: 1
tbd4: 3
tbd5: 14
tba0: 205BAC
tba1: 207EC7
tba2: 2C688
tba3: 2E290
tbssp: 205BBC
tbusp: 0
tbstack: 205BFC
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 18B8
tbrsv2[2]: 20
tbrsv2[3]: 17B8
tbrsv2[4]: 0
TCB #5 stack (176 bytes)
0x205BBC 00 00 00 00 FF FB FF 00 00 20 5B C8 00 20 84 2A
0x205BCC 00 20 5B F8 20 00 00 02 C6 90 00 02 4A 58 00 00
0x205BDC 00 14 00 00 00 0B 00 00 00 01 00 00 00 03 FF FF
0x205BEC 00 00 00 02 E2 94 00 02 E2 96 00 00 00 20 04 20
0x205BFC DE AD BE EF 00 00 00 00 00 00 00 00 00 00 00 00
0x205C0C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C1C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C2C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C3C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C4C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205C5C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #6
tbrsv1[0]: 20279A
tbrsv1[1]: 20279A
tbext: 0
tbpri: 41
tbid: 1B DH1 task
tbstat: 40
tbd0: 0
tbd1: 28
tbd2: 0
tbd3: 1
tbd4: 28
tbd5: FFFF0000
tba0: 203324
tba1: 2E23C
tba2: 2E23E
tba3: 2E238
tbssp: 2032E4
tbusp: 0
tbstack: 20332A
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1E38
tbrsv2[2]: 20
tbrsv2[3]: 1D38
tbrsv2[4]: 0
TCB #6 stack (176 bytes)
0x2032E4 00 00 00 00 FF FB FF 00 00 02 E2 38 00 20 84 2A
0x2032F4 00 20 33 26 20 00 00 02 C4 D8 00 00 00 1B 00 02
0x203304 24 96 00 28 00 00 00 00 00 20 33 24 00 00 00 1B
0x203314 00 00 00 01 00 00 00 03 00 02 E2 3C 00 20 04 20
0x203324 00 00 00 20 04 20 DE AD BE EF 00 00 00 00 00 00
0x203334 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203344 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203354 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203364 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203374 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203384 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #7
tbrsv1[0]: 202802
tbrsv1[1]: 202802
tbext: 0
tbpri: 41
tbid: 1C DH2 task
tbstat: 40
tbd0: 0
tbd1: 29
tbd2: 0
tbd3: 1
tbd4: 29
tbd5: FFFF0000
tba0: 2036DA
tba1: 2E244
tba2: 2E246
tba3: 2E240
tbssp: 20369A
tbusp: 0
tbstack: 2036E0
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1DB8
tbrsv2[2]: 20
tbrsv2[3]: 1CB8
tbrsv2[4]: 0
TCB #7 stack (176 bytes)
0x20369A 00 00 00 00 FF FB FF 00 00 02 E2 40 00 20 84 2A
0x2036AA 00 20 36 DC 20 00 00 02 C4 D8 00 00 00 1C 00 02
0x2036BA 24 96 00 29 00 00 00 00 00 20 36 DA 00 00 00 1C
0x2036CA 00 00 00 01 00 00 00 03 00 02 E2 44 00 20 04 20
0x2036DA 00 00 00 20 04 20 DE AD BE EF 00 00 00 00 00 00
0x2036EA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2036FA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20370A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20371A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20372A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20373A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #8
tbrsv1[0]: 20286A
tbrsv1[1]: 20286A
tbext: 0
tbpri: 41
tbid: 1D DH3 task
tbstat: 40
tbd0: 0
tbd1: 2A
tbd2: 0
tbd3: 1
tbd4: 2A
tbd5: FFFF0000
tba0: 203A90
tba1: 2E24C
tba2: 2E24E
tba3: 2E248
tbssp: 203A50
tbusp: 0
tbstack: 203A96
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1D38
tbrsv2[2]: 20
tbrsv2[3]: 1C38
tbrsv2[4]: 0
TCB #8 stack (176 bytes)
0x203A50 00 00 00 00 FF FB FF 00 00 02 E2 48 00 20 84 2A
0x203A60 00 20 3A 92 20 00 00 02 C4 D8 00 00 00 1D 00 02
0x203A70 24 96 00 2A 00 00 00 00 00 20 3A 90 00 00 00 1D
0x203A80 00 00 00 01 00 00 00 03 00 02 E2 4C 00 20 04 20
0x203A90 00 00 00 20 04 20 DE AD BE EF 00 00 00 00 00 00
0x203AA0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AB0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AC0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AD0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AE0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203AF0 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #9
tbrsv1[0]: 202550
tbrsv1[1]: 201AB8
tbext: 0
tbpri: 28
tbid: 1F DH task
tbstat: 220
tbd0: 0
tbd1: 1
tbd2: 6A
tbd3: 7FFB0
tbd4: 0
tbd5: FFFF0001
tba0: 307F01
tba1: 20CF2C
tba2: 20CF44
tba3: 2C9BC
tbssp: 203DDC
tbusp: 0
tbstack: 203E4C
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1CB8
tbrsv2[2]: 20
tbrsv2[3]: 1BB8
tbrsv2[4]: 0
TCB #9 stack (176 bytes)
0x203DDC 00 00 00 6A FF FB FF 00 00 30 BB 5D 00 20 84 2A
0x203DEC 00 20 3E 48 20 00 00 02 C5 9C 00 00 00 02 18 20
0x203DFC 02 0C 00 00 00 03 00 02 84 96 00 01 00 00 00 6A
0x203E0C 00 07 FF B0 00 00 00 20 3E 46 00 00 00 1F 00 00
0x203E1C 00 01 00 00 00 03 FF FF 00 00 00 00 00 00 FF FB
0x203E2C FF 00 00 02 E2 54 00 02 E2 56 00 02 E2 50 00 20
0x203E3C D0 82 00 01 00 00 00 04 04 20 00 34 00 20 04 20
0x203E4C DE AD BE EF 00 00 00 00 00 00 00 00 00 00 00 00
0x203E5C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203E6C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x203E7C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #10
tbrsv1[0]: 202490
tbrsv1[1]: 202490
tbext: 0
tbpri: 15
tbid: 21 DH histogram task
tbstat: 200
tbd0: 0
tbd1: 7
tbd2: 0
tbd3: 20
tbd4: 1
tbd5: FFFF0000
tba0: 201BB8
tba1: 2E25C
tba2: 2C580
tba3: 2E258
tbssp: 204194
tbusp: 0
tbstack: 204202
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1C38
tbrsv2[2]: 20
tbrsv2[3]: 1B38
tbrsv2[4]: 0
TCB #10 stack (176 bytes)
0x204194 00 00 00 00 FF FB FF 00 00 02 E2 58 00 20 84 2A
0x2041A4 00 20 41 FE 20 00 00 02 C5 9C 00 00 00 21 00 00
0x2041B4 00 01 00 00 00 03 00 01 1E 70 00 07 00 00 00 00
0x2041C4 00 00 00 20 00 01 00 20 41 FC 00 00 00 21 00 00
0x2041D4 00 01 00 00 00 03 FF FF 00 00 00 00 00 00 FF FB
0x2041E4 FF 00 00 02 E2 5C 00 02 E2 5E 00 02 E2 58 E2 58
0x2041F4 00 00 00 01 00 20 04 20 20 00 00 20 04 20 DE AD
0x204204 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204214 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204224 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x204234 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #11
tbrsv1[0]: 202636
tbrsv1[1]: 202636
tbext: 0
tbpri: 23
tbid: 22 Remote read request task
tbstat: 40
tbd0: 0
tbd1: 5
tbd2: 0
tbd3: 0
tbd4: 3
tbd5: FFFF0000
tba0: 2045B0
tba1: 300100
tba2: 19CD84
tba3: 2E260
tbssp: 20456C
tbusp: 0
tbstack: 2045B8
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1BB8
tbrsv2[2]: 20
tbrsv2[3]: 1AB8
tbrsv2[4]: 0
TCB #11 stack (176 bytes)
0x20456C 00 00 00 00 FF FB FF 00 00 19 CF 38 00 20 84 2A
0x20457C 00 20 45 B4 20 00 00 02 C4 D8 00 00 00 00 00 00
0x20458C C1 82 00 05 00 00 00 00 00 20 45 B0 00 00 00 22
0x20459C 00 00 00 01 00 02 E2 64 00 02 E2 66 01 03 01 00
0x2045AC 84 2A 00 20 00 00 20 00 00 20 04 20 DE AD BE EF
0x2045BC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2045CC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2045DC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2045EC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2045FC 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20460C 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #12
tbrsv1[0]: 201AB8
tbrsv1[1]: 202550
tbext: 0
tbpri: 41
tbid: 23 Make PCL message task
tbstat: 200
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 48000000
tbd4: 1
tbd5: FFFF0000
tba0: 2017B8
tba1: 2E29C
tba2: 2E29E
tba3: 2E298
tbssp: 205F54
tbusp: 0
tbstack: 205FB2
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1838
tbrsv2[2]: 20
tbrsv2[3]: 1738
tbrsv2[4]: 0
TCB #12 stack (176 bytes)
0x205F54 00 00 00 00 FF FB FF 00 00 02 E2 98 00 20 84 2A
0x205F64 00 20 5F AE 20 00 00 02 C5 9C 00 00 00 23 00 00
0x205F74 00 01 00 00 00 03 00 02 44 6E 00 01 00 00 00 00
0x205F84 48 00 00 00 00 01 00 20 5F A4 00 00 00 23 00 00
0x205F94 00 01 00 02 E2 9C 00 02 E2 9E 00 02 E2 98 E2 98
0x205FA4 00 20 84 2A 00 20 04 20 20 00 00 20 04 20 DE AD
0x205FB4 BE EF 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205FC4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205FD4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205FE4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x205FF4 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #13
tbrsv1[0]: 202662
tbrsv1[1]: 202662
tbext: 0
tbpri: 23
tbid: 28 Rung cache remote mod task
tbstat: 40
tbd0: 0
tbd1: 8
tbd2: 0
tbd3: 1
tbd4: 3
tbd5: FFFF0000
tba0: 20635E
tba1: 2C9BC
tba2: 2E2A6
tba3: 2E2A0
tbssp: 20632A
tbusp: 0
tbstack: 206368
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 17B8
tbrsv2[2]: 20
tbrsv2[3]: C9E
tbrsv2[4]: 0
TCB #13 stack (176 bytes)
0x20632A 00 00 00 00 FF FB FF 00 00 02 E2 A0 00 20 84 2A
0x20633A 00 20 63 64 20 00 00 02 C4 D8 00 00 00 28 00 01
0x20634A 91 AE 00 08 00 00 00 00 00 20 63 5E 00 02 E2 A4
0x20635A 00 20 84 2A 00 00 04 20 20 00 00 20 04 20 00 00
0x20636A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20637A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20638A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x20639A 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2063AA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2063BA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
0x2063CA 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Task Control Block entry #14
tbrsv1[0]: 201C38
tbrsv1[1]: 2017B8
tbext: 0
tbpri: 2F
tbid: 45 RIO IOT task
tbstat: 200
tbd0: 0
tbd1: 1
tbd2: 0
tbd3: 800000
tbd4: 0
tbd5: FFFF0000
tba0: 204968
tba1: 2C9BC
tba2: 2E26E
tba3: 2E268
tbssp: 204922
tbusp: 0
tbstack: 20496E
tbflags: 0
tbrsv2[0]: 20
tbrsv2[1]: 1B38
tbrsv2[2]: 20
tbrsv2[3]: 1A38
tbrsv2[4]: 0