PANEL VIEW 1000 :communication Driver fault

RSLinx, RSLogix, RSView, LogixPro ...
sotos37
Posts: 2
Joined: Mon Dec 05, 2011 10:23 pm

PANEL VIEW 1000 :communication Driver fault

Post by sotos37 »

The problems has started a couple weeks ago :
Randomly 2-3 times per shift an error appeared
communication driver fault 645
after pressing the touch screen another error appeared
communication driver fault 637
After restarting the device , the machine worked normally

But now after booting an alarm appears
MINOR FAULT 1007
COMMUNICATION FAULT 649 0,0

• The panel view is connected via CONTROLNET with a controlLogix (1756-PA72/B)
• The CPU (LOGIX5555) is on Run mode
• The controlNET card has two leds :
On: is flashing green
Channel A : is flashing red

On the controlNet display there is a message:
NET ERROR
%C07
Kp0V
nC00
nV00
A#01

• The panel view on the back on the right side has two leds
Both of them are off after booting

thanks
Ryzhij
Posts: 406
Joined: Mon Mar 31, 2008 11:29 am
Location: Ryazan, Russia

Re: PANEL VIEW 1000 :communication Driver fault

Post by Ryzhij »

Check the condition of the cable, connectors, a terminators.
Kirillij
Posts: 37
Joined: Wed Dec 15, 2010 8:49 pm

Re: PANEL VIEW 1000 :communication Driver fault

Post by Kirillij »

and no one changes the net configuration? can send data to the panel have a different length? and what about RSNetWorx for ControlNet?
sotos37
Posts: 2
Joined: Mon Dec 05, 2011 10:23 pm

Re: PANEL VIEW 1000 :communication Driver fault

Post by sotos37 »

no changes have been made to the net configuration
Also the cables and the terminal seems to be ok.
is it possible that the controlnet card is been defective?
Kirillij
Posts: 37
Joined: Wed Dec 15, 2010 8:49 pm

Re: PANEL VIEW 1000 :communication Driver fault

Post by Kirillij »

yes. its can be. use "RSNetWorx for ControlNet" for check net config and condition of the net-card.
repack connector cable is also good (if the system is not new).