Dear All
I have Siemens CPU 315-2DP and I want to use memory word variables I start from address MW 0,
I ask about the upper limit of MW variables addressing ?
i.e. can I use the address MW 300?
Thanks
[?]: Siemens CPU 315-2DP MW memory area
-
- Posts: 17
- Joined: Fri Sep 24, 2010 10:03 pm
Re: Siemens CPU 315-2DP
Hi,
The CPU 315-2 DP has 2 kB memory for flags. So you can use flag words from MW0 to MW2046. Mind the retentivity.
Greets
Lepes9
The CPU 315-2 DP has 2 kB memory for flags. So you can use flag words from MW0 to MW2046. Mind the retentivity.
Greets
Lepes9
-
- Posts: 65
- Joined: Thu Nov 01, 2007 9:41 pm
- Location: Belarus
Re: Siemens CPU 315-2DP
Find your CPU and see Technical Data
-
- Posts: 17
- Joined: Fri Sep 24, 2010 10:03 pm
Re: Siemens CPU 315-2DP
Here: https://eb.automation.siemens.com/mall/ ... atalogTree and select Product Information.
Greets
Lepes9
Greets
Lepes9
-
- Posts: 244
- Joined: Sat Oct 22, 2011 7:12 am
Re: [?]: Siemens CPU 315-2DP MW memory area
Thank you very much friends