CP1613A2 ISO and TCP simultaneously dont work

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
Triaton
Posts: 4
Joined: Thu Dec 01, 2011 10:43 am

CP1613A2 ISO and TCP simultaneously dont work

Post by Triaton »

Hi all. There is working system with H-station (2x414-4) and three operator workstations (InTouch), which communicated via ISO protocol.
Now i have to add three 3152PN/DP in this system for auxiliary aggregates control. I want to connect new controllers to the H-stations switch and communicate with InTouch via TCP. Problem in the following - after adding "Use TCP" on CP1613A2 properties i compile project in NetPro, then during downloading this station occours the message "CP1613 in station cannot be started". In the diag. buf. there are next messages:
The component is sending a negative response. TFservice: 28.
The component is sending a negative response. S7 error code: 8703
Component database invalid
Is anybody use such configuration (ISO and TCP on one board simultaneously)? What is wrong?

P.S. In HW Config cant find 6GK1161-3AA01, therefore 6GK1161-3AA00 used.

Thanks for the answers.

Sorry for my english
Triaton
Posts: 4
Joined: Thu Dec 01, 2011 10:43 am

Re: CP1613A2 ISO and TCP simultaneously dont work

Post by Triaton »

Sorry.
Problem was on uncorrect settings of IPs of NDIS and Network card. It was identical, and its wrong. Station was downloaded and started with ISO and TCP activated. But now i have a new problem. I can not download the CPU315 via TCP.

Sorry for my english.