Hi Linkinx64,
Could you help me step by step How to create Report with DataDirect?
Many Thanks
[?] 800xA DataDirect: Need Linkinx64's help
-
- Posts: 894
- Joined: Sun Apr 11, 2010 3:00 am
- Location: Russia
Re: [?] 800xA DataDirect: Need Linkinx64's help
Hi
Please specify the problem more details (with attached screenshots).
About those step-by-step you sent in PM:
1. Time difference occured because report creation time is different from the current system time. And the DataDirect templates are not provide autoupdate value by default. As well as the time stamp.
2. Sequence of generating report using Scheduling structure is right. I don't understand what's a problem can be...
Please specify the problem more details (with attached screenshots).
About those step-by-step you sent in PM:
1. Time difference occured because report creation time is different from the current system time. And the DataDirect templates are not provide autoupdate value by default. As well as the time stamp.
2. Sequence of generating report using Scheduling structure is right. I don't understand what's a problem can be...
-
- Posts: 125
- Joined: Wed Apr 11, 2007 7:53 am
Re: [?] 800xA DataDirect: Need Linkinx64's help
Hi,
Could you build a example to demonstration "How to create Shift-report automatically"?
Thanks.
Could you build a example to demonstration "How to create Shift-report automatically"?
Thanks.
-
- Posts: 125
- Joined: Wed Apr 11, 2007 7:53 am
Re: [?] 800xA DataDirect: Need Linkinx64's help
Hi Linkinx64,
I need your help for "How to create automatically report when alarms&events occurs by DataDirect tool?".
Could you explain the concept of alarms&events report?
Many thank,
Tuan.
I need your help for "How to create automatically report when alarms&events occurs by DataDirect tool?".
Could you explain the concept of alarms&events report?
Many thank,
Tuan.
-
- Posts: 125
- Joined: Wed Apr 11, 2007 7:53 am
Re: [?] 800xA DataDirect: Need Linkinx64's help
Hi Linkinx64,
I'm using DataDirect to create Shift Report. Some days ago, my report format as pic. below. The time sort oldest -> newest. (that's OK)
But today, my report automatic change sort time newest -> oldest. I don't what is changed. Time and date is wrong (2015???)
How to reconfig time sort oldest -> newest?
Thanks
I'm using DataDirect to create Shift Report. Some days ago, my report format as pic. below. The time sort oldest -> newest. (that's OK)
But today, my report automatic change sort time newest -> oldest. I don't what is changed. Time and date is wrong (2015???)
How to reconfig time sort oldest -> newest?
Thanks
-
- Posts: 894
- Joined: Sun Apr 11, 2010 3:00 am
- Location: Russia
Re: [?] 800xA DataDirect: Need Linkinx64's help
Upload your report template - I'll try to simulate time fault in my system.
-
- Posts: 125
- Joined: Wed Apr 11, 2007 7:53 am
Re: [?] 800xA DataDirect: Need Linkinx64's help
Check PM please.Linkinx64 wrote:Upload your report template - I'll try to simulate time fault in my system.
-
- Posts: 894
- Joined: Sun Apr 11, 2010 3:00 am
- Location: Russia
Re: [?] 800xA DataDirect: Need Linkinx64's help
Check carefully expressions for the ABBGETOPCHDA(...) function. It could be due to incorrect function arguments (e.g. start time and end time are conversed or not correct data type specified or something similar).
Unfortunately on the 2nd picture I do not see full expression for the ABBGETOPCHDA and which values it take.
Unfortunately on the 2nd picture I do not see full expression for the ABBGETOPCHDA and which values it take.
-
- Posts: 125
- Joined: Wed Apr 11, 2007 7:53 am
Re: [?] 800xA DataDirect: Need Linkinx64's help
1.
2.
3.
Check data in Log Configuration. It's look OK. Time&Date is correct.
Show
Use DataDirect
Show
Excell. Wrong time, wrong year... (some time is 2015)
Show
-
- Posts: 894
- Joined: Sun Apr 11, 2010 3:00 am
- Location: Russia
Re: [?] 800xA DataDirect: Need Linkinx64's help
Hi, Tuan
I am here but at the moment I still not found what can cause rearranging new->old issue.
I had tried to change time / disconnect from OPC server on my local system but it was not lead to rearranging date and shift it 2 years forward...
I am here but at the moment I still not found what can cause rearranging new->old issue.
I had tried to change time / disconnect from OPC server on my local system but it was not lead to rearranging date and shift it 2 years forward...
-
- Posts: 125
- Joined: Wed Apr 11, 2007 7:53 am
Re: [?] 800xA DataDirect: Need Linkinx64's help
I'm not lucky. I know my system is crazy.
Many thanks for your help.
-
- Posts: 125
- Joined: Wed Apr 11, 2007 7:53 am
Re: [?] 800xA DataDirect: Need Linkinx64's help
Hi Linkinx64,
Now my DataDirect report is wrong time & date again
Is this a bug of DataDirect?
I've used DataDirect ver5.1.5111.1110 in SV5.1 RevA FP1. Could I upgrade only DataDirect to ver 5.1.5812.0612 (in SV5.1.1 FP4) to fix my problem?
Thanks
Now my DataDirect report is wrong time & date again
Is this a bug of DataDirect?
I've used DataDirect ver5.1.5111.1110 in SV5.1 RevA FP1. Could I upgrade only DataDirect to ver 5.1.5812.0612 (in SV5.1.1 FP4) to fix my problem?
Thanks
-
- Posts: 894
- Joined: Sun Apr 11, 2010 3:00 am
- Location: Russia
Re: [?] 800xA DataDirect: Need Linkinx64's help
Partial update in 800xA is not supported - it can lead to unstable system behavior, failure, other unwanted consequences.tuangp wrote:I've used DataDirect ver5.1.5111.1110 in SV5.1 RevA FP1. Could I upgrade only DataDirect to ver 5.1.5812.0612 (in SV5.1.1 FP4) to fix my problem?
Exception: temporary correstions (TC) issuing by 800xA dev. team.
Therefore, there are 3 ways you need try now:
1. Check report template and OPC data consistency for the internal errors leading to the wrong date/time presentation.
2. (only if the 1st way is successfully commited) Request temporary corrections (TC) for DataDirect ver5.1.5111.1110 from ABB support center.
3. (if ABB support center was not able to identify problem) Update WHOLE system to v5.1.1.1 (FP4).