[?+]: Change address ET200S input module

SIMATIC S7-200/300/400, Step7, PCS7, CFC, SFC, PDM, PLCSIM,
SCL, Graph, SPS-VISU S5/S7, IBHsoftec, LOGO ...
igor62il
Posts: 7
Joined: Fri Sep 28, 2012 7:40 pm

[?+]: Change address ET200S input module

Post by igor62il »

Hi.How I can change a addresses of inputs modules of S7-300.
Now I have hardware with 2 inputs modules with not usable addresses from 00-0.3 and second from 1.0-1.3.
This modules installed together on the rack.
I want to change its to free IB13 for example.
What I need do for this?
Thanks.
Schtiel
Site Admin
Posts: 1122
Joined: Wed Sep 06, 2006 12:03 pm
Location: CIS

Re: Change address input module

Post by Schtiel »

Run HW Config, double click on your input module. Go to Addresses tab, uncheck System default checkbox. Then you can change addresses:
ET200M
Image
I did it,first ET200S module changed from 0.0-0.3 to 13.0-13.3,
but second show me possible only from address 14,not continius from 13.
ET200S > Pack Adress
Image
igor62il
Posts: 7
Joined: Fri Sep 28, 2012 7:40 pm

Re: Change address input module

Post by igor62il »

Can you explain,pleasy?
CoMod
Site Admin
Posts: 3992
Joined: Thu Feb 16, 2006 3:25 pm
Location: Russia

Re: Change address input module

Post by CoMod »

ScreenCopy of your HWConfig ?
Копию экрана HWConfig ?
igor62il
Posts: 7
Joined: Fri Sep 28, 2012 7:40 pm

Re: Change address input module

Post by igor62il »

I find solution: On a hardware chapter select required modules together and push "Pack Address" on the table.
Thats all,adresses will start from 0.0-03 and 0.4-0.7 for my case.
Thanks all for helping.