one plc S7300 or S5(x) requires annual maintenance
(except cleanup of dust or charge battery)
best regards
Carlos
[?]: requires annual maintenance for PLC ?
-
- Posts: 86
- Joined: Tue Aug 21, 2012 1:51 pm
- Location: Europe
Re: stupid questions or stupid boss
i think NO
Re: stupid questions or stupid boss
Thanks krank for replykrank wrote:i think NO
more opinions ?
-
- Posts: 24
- Joined: Thu Nov 08, 2007 6:46 pm
- Location: India
Re: [?]: requires annual maintenance for PLC ?
It is better not to do any maintenance on the PLCs other than blowering to remove the dust accumulated on the plc modules.
Please remember to switch off power to the racks before doing any maintenance.
From my personal experience, i will recommend that you SHOULD NOT remove/unplug the modules from the racks especially in case of S7-400 / S5 racks.
These racks are very sensitive to dust and the "maintenance" might result into unforeseen problems due to dust ingress.
Other than the above, checking tightness of mounting screws and a regular backup of online data always helps!
Cheers!
XMAS
Please remember to switch off power to the racks before doing any maintenance.
From my personal experience, i will recommend that you SHOULD NOT remove/unplug the modules from the racks especially in case of S7-400 / S5 racks.
These racks are very sensitive to dust and the "maintenance" might result into unforeseen problems due to dust ingress.
Other than the above, checking tightness of mounting screws and a regular backup of online data always helps!
Cheers!
XMAS
Re: [?]: requires annual maintenance for PLC ?
thanks XMAS for your reply, also grateful for the pm by CoMod.
can close the topic and once again grateful for the help
Carlos
can close the topic and once again grateful for the help
Carlos