Hello,
I need to configure PLC Connect (System 800xA) acting as a Modbus TCP Server/Slave.
I can configure it as a Modbus TCP/IP Client/Master.
A third party has to connect to my system and get some data using Modbus TCP and I don't know how to configure it.
Thank you in advance.
[?]: ABB 800xA (PLC Connect) Modbus TCP Server
-
- Posts: 8
- Joined: Wed Jan 30, 2013 4:56 pm
-
- Posts: 894
- Joined: Sun Apr 11, 2010 3:00 am
- Location: Russia
Re: [?]: ABB 800xA (PLC Connect) Modbus TCP Server
Hello,
Modbus trough PLC Connect connected with MB/TCPIP bridge device can act only as a master.
Modbus trough PLC Connect connected with MB/TCPIP bridge device can act only as a master.
-
- Posts: 8
- Joined: Wed Jan 30, 2013 4:56 pm
Re: [?]: ABB 800xA (PLC Connect) Modbus TCP Server
Thank you very much Linkinx64.
And there is any option with 800xA to act as a Modbus TCP slave/server? Please, no PLC Connect, no CI867 and no OPC third party. Could system 800xA be configured to act as Modbus TCP slave/server directly?
Thank you.
And there is any option with 800xA to act as a Modbus TCP slave/server? Please, no PLC Connect, no CI867 and no OPC third party. Could system 800xA be configured to act as Modbus TCP slave/server directly?
Thank you.
-
- Posts: 894
- Joined: Sun Apr 11, 2010 3:00 am
- Location: Russia
Re: [?]: ABB 800xA (PLC Connect) Modbus TCP Server
No, without third-parties it is not possible to make SCADA/DCS acts as a Modbus slave. Due to Modbus protocol specifics.
Also, what's a data PLC need query from SCADA/DCS? Usually SCADA/DCS query PLC for a process values, not vise versa...
Also, what's a data PLC need query from SCADA/DCS? Usually SCADA/DCS query PLC for a process values, not vise versa...
-
- Posts: 8
- Joined: Wed Jan 30, 2013 4:56 pm
Re: [?]: ABB 800xA (PLC Connect) Modbus TCP Server
Sorry, I think I have not explian very well. We are a part of the system and not the DCS. The DCS has to connect to us to get the data. Because of this, we have to be Modbus TCP Slave/Server and the DCS the client/Master.
Forget PLC Connect, is there any possiblity? And using OPC Client Connection? We also need an OPC Modbus TCP Server?
Thank you.
Forget PLC Connect, is there any possiblity? And using OPC Client Connection? We also need an OPC Modbus TCP Server?
Thank you.
-
- Posts: 894
- Joined: Sun Apr 11, 2010 3:00 am
- Location: Russia
Re: [?]: ABB 800xA (PLC Connect) Modbus TCP Server
Java_user wrote:And there is any option with 800xA to act as a Modbus TCP slave/server?
If we not DCS then who "we" are? Under DCS I assumed 800xA system. What kind of data? Why Modbus? There are another interfaces that can get data from the 800xA, ODA for example. Give more detail about your system configuration, incl. hardrware. It's hard to know how to establish connection with black boxes:Java_user wrote:We are a part of the system and not the DCS. The DCS has to connect to us to get the data. Because of this, we have to be Modbus TCP Slave/Server and the DCS the client/Master.
Java_user wrote:We are a part of the system and not the DCS.
-
- Posts: 7
- Joined: Sun Aug 11, 2013 4:06 am
Re: [?]: ABB 800xA (PLC Connect) Modbus TCP Server
800xA have built in OPC, the other DCS system can read the date from 800xA via OPC.Java_user wrote:Sorry, I think I have not explian very well. We are a part of the system and not the DCS. The DCS has to connect to us to get the data. Because of this, we have to be Modbus TCP Slave/Server and the DCS the client/Master.
Forget PLC Connect, is there any possiblity? And using OPC Client Connection? We also need an OPC Modbus TCP Server?
Thank you.
the modbus TCP is not really needed.