[?]: connect HMIGTO2300 to M340 PLC Schneider

Прочие SCADA: iFix, InTouch, Citect, ...
krank
Posts: 86
Joined: Tue Aug 21, 2012 1:51 pm
Location: Europe

[?]: connect HMIGTO2300 to M340 PLC Schneider

Post by krank »

Hi i want to find how to connect HMIGTO2300 and M340 plc

Modbus connexion M340 P341000
Modbus HMIGTO2300 COM2 RS485

CABLE OK but how to configure SerialPort in M340 ?
Kuzyma
Posts: 31
Joined: Tue May 12, 2009 8:32 am

Re: [?]: connect HMIGTO2300 to M340 PLC Schneider

Post by Kuzyma »

well, it's quite easy. The Magelis is going to Master in Modbus network, M340's serial port is going to be slave.
You need to configure identical line parameters (speed, parity, stop bits, etc.) in Unity Pro and Vijeo Designer and set up slave's address.
Basically that's all.
After you just create variables in Vijeo Designer with certain addresses (which correspond to ones in PLC).
There's also the option to connect Magelis and M340 by USB cable.