I am working on Quantum CPU 434 12 A, I am using Software Concept 2.6 and Proworx 32 to program it.
When I try to download configuration from concept it gives error that you need to update the EXEC
So, when I get this error I launch EXECLOADER utility and try to upgrade the firmware of my CPU 43412A
The currently running firmware if my CPU is 1.02
So I have downloaded latest firmware of year 2005 April and try to download it into my CPU its start transferring and after 1-2 mints its says link between CPU is broken
I have done the done the same procedure with ProworX 32 execloader and I get the same result, also ProworX 32 says the controller is in DIM AWARNESS state.
I have then contact Schneider Electric Support, They says that we will advise you to use Concept 2.2 SR2 with old CPU's , now I am unable to find download link for Concept version 2.2 SR2 .
If Any one of you can help me I shall be highly thankful to you.
Please advise how to overcome this error?
Quantum CPU 434 12 A
-
- Posts: 101
- Joined: Thu Aug 29, 2013 4:11 pm
Re: Quantum CPU 434 12 A
Hello, just look in your Concept installation folder, there you find the suitable firmware for your PLC and your concept version.genjua84 wrote:I am working on Quantum CPU 434 12 A, I am using Software Concept 2.6 and Proworx 32 to program it.
When I try to download configuration from concept it gives error that you need to update the EXEC
If not, just provide me hardware ID, Version number and Kernel number of your PLC (you see it in EXECLoader) and which firmware version you need.
BR
-
- Posts: 5
- Joined: Mon Jan 24, 2011 8:25 am
Re: Quantum CPU 434 12 A
Man Thanks for the prompt response
I don't know how to upload pictures into this post I have screenshot of it as well....
Please find the information below:
Hardware ID : (8) 0006
Version Number 1.02
Model Number : 140-CPU-x34-1x
Kernel Revision : 1.01
Crash Code: 0000
I need any firmware which works with my CPU434 12 A along with 06 Nos. of ACI 030 00 Cards.
Anything else you need to know?
Please be informed that I am using Concept 2.6 Version I do not have Concept 2.2 Version
Please share your email address with me, as I want to share some screenshots with you.
I don't know how to upload pictures/screen shots into this forum/post.
C:\Users\khan.genjua\Desktop\Case\Concept%20error%20for%20Exec%20uodates.JPG
After reading your reply, i have found *.bin files in concept folder (DAT Folder), My problem is that when i strat transferring Firmware into CPU its start and after 1-2 mints its stops and says that Link between CPU is broken,
The cable i am using is tested, as i have upload current running Firmware from CPU into computer by using same cable.
BR
I don't know how to upload pictures into this post I have screenshot of it as well....
Please find the information below:
Hardware ID : (8) 0006
Version Number 1.02
Model Number : 140-CPU-x34-1x
Kernel Revision : 1.01
Crash Code: 0000
I need any firmware which works with my CPU434 12 A along with 06 Nos. of ACI 030 00 Cards.
Anything else you need to know?
Please be informed that I am using Concept 2.6 Version I do not have Concept 2.2 Version
Please share your email address with me, as I want to share some screenshots with you.
I don't know how to upload pictures/screen shots into this forum/post.
C:\Users\khan.genjua\Desktop\Case\Concept%20error%20for%20Exec%20uodates.JPG
After reading your reply, i have found *.bin files in concept folder (DAT Folder), My problem is that when i strat transferring Firmware into CPU its start and after 1-2 mints its stops and says that Link between CPU is broken,
The cable i am using is tested, as i have upload current running Firmware from CPU into computer by using same cable.
BR
Last edited by genjua84 on Mon Sep 02, 2013 12:36 pm, edited 1 time in total.
-
- Posts: 101
- Joined: Thu Aug 29, 2013 4:11 pm
Re: Quantum CPU 434 12 A
Hello, pls. see Firmware 1.20 in attachment (from Concept 2.6).
Are you using Modbus or Modbus+? Which Adapter?
q5rv120E.bin
BR
Are you using Modbus or Modbus+? Which Adapter?
q5rv120E.bin
BR
-
- Posts: 5
- Joined: Mon Jan 24, 2011 8:25 am
Re: Quantum CPU 434 12 A
Dude I am Using Modbus!
I have told you that I have successfully fetched the installed Firmware from CPU 43412A this proves that the cable is good.
I have try the file which you have provided but still result is same
any suggestions???
I have told you that I have successfully fetched the installed Firmware from CPU 43412A this proves that the cable is good.
I have try the file which you have provided but still result is same
any suggestions???
-
- Posts: 101
- Joined: Thu Aug 29, 2013 4:11 pm
Re: Quantum CPU 434 12 A
1) install the neuest modbus driver
for USB/485 or USB/232: Windows7-32_64-bit.7z
2) if new driver doesn't help, then you need another Modbus Adapter - sometimes 5$ adapter working fine and 50$ adapter doesn't work at all. I'am using original TSXCUSB485 adapter.
for USB/485 or USB/232: Windows7-32_64-bit.7z
2) if new driver doesn't help, then you need another Modbus Adapter - sometimes 5$ adapter working fine and 50$ adapter doesn't work at all. I'am using original TSXCUSB485 adapter.
-
- Posts: 5
- Joined: Mon Jan 24, 2011 8:25 am
Re: Quantum CPU 434 12 A
Champ I have TSXCUSB485 in my hand, I am using Windows XP, when I can upload firmware from CPU by using the same cable why I could not download the firmware?
have you worked on Proworx 32 ever?
my CPU is in DIM AWARNESS Mode as well.....
Dude now I am using MODSOFT software for EXEC loading, I am getting same kind of error from MODSOFT as well.
It says while transferring "Waiting For Node To Rejoin The Link In Kernel Mode"
After some times it says "Mode Failed To Enter Kernel Mode"
Do you have now any idea about my problem?
have you worked on Proworx 32 ever?
my CPU is in DIM AWARNESS Mode as well.....
Dude now I am using MODSOFT software for EXEC loading, I am getting same kind of error from MODSOFT as well.
It says while transferring "Waiting For Node To Rejoin The Link In Kernel Mode"
After some times it says "Mode Failed To Enter Kernel Mode"
Do you have now any idea about my problem?
-
- Posts: 101
- Joined: Thu Aug 29, 2013 4:11 pm
Re: Quantum CPU 434 12 A
Dim awareness is the off-the-shelf state of Modicon processors. It means that there is no configuration or logic in the processor. This state will also reappear if you take the battery out and power down to clear the memory. It does not matter whether you're using Nxt, Modsoft, Proworx Plus, or Concept, the processor will be in dim awareness.genjua84 wrote:my CPU is in DIM AWARNESS Mode as well.....
Today in the Quantum range the term is "not Configured"
I had allready same troubles with Quantum 140CPU67160, with another PC it was possible to flash the PLC.genjua84 wrote: It says while transferring "Waiting For Node To Rejoin The Link In Kernel Mode"
After some times it says "Mode Failed To Enter Kernel Mode"
Which exec loader version do you have? How do you configurate the dip switches on front panel of PLC? Which LED are flashing on PLC?genjua84 wrote: After some times it says "Mode Failed To Enter Kernel Mode"
Do you have now any idea about my problem?
-
- Posts: 101
- Joined: Thu Aug 29, 2013 4:11 pm
Re: Quantum CPU 434 12 A
If Kernel LED is flashing and firmware update via Modbus doesn't work, you can still try use Modbus+. But I think you will have no success. In this case something wrong with the controller and cannot be field recovered. The unit can be sent in for repair exchange from the outfit you originally purchased the equipment from.
-
- Posts: 5
- Joined: Mon Jan 24, 2011 8:25 am
Re: Quantum CPU 434 12 A
Good Day Dude!
Thank you very much for being with me while I was in pain
I have solved the problem successfully, Basically I was going to EXEC update as Concept 2.6 was asking for it at the time when I try to download logic and configuration into it.
So I was using EXECLOADER utility for that and I was not able to upgrade firmware like I mentioned in the previous post.
So I thought came in my mind that leave EXEC and try to program PLC by using old software's e.g. Modsoft , Proworx 32
So finally I have successfully programmed my CPU 434 12 A along with 08 Nos. of ACI 030 00 cards and CPS 114 10, by using ProworX 32.
Thanks a lot for your support , really you provide me such a useful information as well as hints to solve my problem , I have also changed the Cable as per your advise
BR
Genjua
Thank you very much for being with me while I was in pain
I have solved the problem successfully, Basically I was going to EXEC update as Concept 2.6 was asking for it at the time when I try to download logic and configuration into it.
So I was using EXECLOADER utility for that and I was not able to upgrade firmware like I mentioned in the previous post.
So I thought came in my mind that leave EXEC and try to program PLC by using old software's e.g. Modsoft , Proworx 32
So finally I have successfully programmed my CPU 434 12 A along with 08 Nos. of ACI 030 00 cards and CPS 114 10, by using ProworX 32.
Thanks a lot for your support , really you provide me such a useful information as well as hints to solve my problem , I have also changed the Cable as per your advise
BR
Genjua