I have redundant system used 2 cpu's S7 400 (6ES7417-4HL04-0AB0) Version FW V4.0.4 ,
then one of them damaged
and I found cpu 417 but the FW version is V4.0.10
Can I use it instate of the damaged one??
How can I update FW???
Regards
[?]: Siemens s7 400 redundant with different firmware vers ?
-
- Posts: 244
- Joined: Sat Oct 22, 2011 7:12 am
-
- Site Admin
- Posts: 3992
- Joined: Thu Feb 16, 2006 3:25 pm
- Location: Russia
Re: [?]: Siemens s7 400 redundant with different firmware ve
hardware numbers 6ES7417-4HL04-0AB0
and firmware numbers must be identical
Recommended as Update firmware to V4.0.12 (19.04.2010)
http://support.automation.siemens.com/W ... en/6741018
and firmware numbers must be identical
Recommended as Update firmware to V4.0.12 (19.04.2010)
http://support.automation.siemens.com/W ... en/6741018
-