Hello,
I have a s7-200 PLC with a password protection for uploading. both communication ports of this PLC is used for communication with drives and HMI.
Can i add EM 277 PROFIBUS DP module for this PLC (s7-200)without chaning the program ??
thanks in advance
[?]: adding EM 277 PROFIBUS DP module to S7-200
-
- Posts: 10
- Joined: Tue Apr 09, 2013 10:42 pm
-
- Posts: 258
- Joined: Fri Apr 03, 2009 3:24 pm
- Location: Bosnia and Herzegovina
Re: [?]: adding EM 277 PROFIBUS DP module to S7-200
Basicaly, yes.
You can externaly (via DP master) set SMB200 to MSB249 to macth your needs.
But it is very hard to 'guess' data area where are variables you want to read/write, when you got a locked program.
And, if those variables are not in compast blocks (lenght of 64byte for I and Q), you are in big trouble.
You can externaly (via DP master) set SMB200 to MSB249 to macth your needs.
But it is very hard to 'guess' data area where are variables you want to read/write, when you got a locked program.
And, if those variables are not in compast blocks (lenght of 64byte for I and Q), you are in big trouble.
-
- Posts: 10
- Joined: Tue Apr 09, 2013 10:42 pm
Re: [?]: adding EM 277 PROFIBUS DP module to S7-200
can i use it as a PPI slave ?
-
- Posts: 258
- Joined: Fri Apr 03, 2009 3:24 pm
- Location: Bosnia and Herzegovina
Re: [?]: adding EM 277 PROFIBUS DP module to S7-200
No, just for Profibus slave. There are no system commands to apply PPI protocol through port on expansion module.