Hello,
i need some help!!
i connected both via rs-485 by lan cable.
HMI PLC
RJ-45 Mini Din 8 pin
pin4 A <---> pin1 A
pin5 B <---> pin2 B
pin8 SG <---> pin7 0V
PLC : I config in Twidosuite(Descrobe) to 19200 8 E 1 tried other baud rate too.
HMI : I config in IO Manager --> ModbusRTU01[Com2] to 19200 8 E 1 and ModbusEquipment1 to address 1(PLC)
but when i power on i get msg on HMI display "No reply from PLC within Timeout period. (ModbusEquipment01)"
i need config more? i missed something?
please help!!! or give some instruction.
Thank you.
Communication between Schneider HMIGTO2300 and TWDLCAA10DRF
-
- Posts: 1
- Joined: Mon Jan 13, 2014 5:51 pm
-
- Posts: 27
- Joined: Wed Mar 11, 2009 1:35 am
Re: Communication between Schneider HMIGTO2300 and TWDLCAA10
tewatute,
Herewith the configuration of Both..
PLC TWDLCAA10DRF
1. Using Twido Suite, at the Describe Toolbar, put by drag and drop PLC (Base->Compact->TWDLCAA10DRF) and HMI (Network Elements->Modbus Elements->Magelis)
2. Connected point to point PLC and Network Element
3. Configuration setting:
a.
Network Elements
Name = any
Type = Modbus
Address = Master
b.
Network
Type = No Change
Name = any
Baudrate = 19200
Data Bits = 8 (RTU)
Parity = none
Stop Bit = 1
Timeout = 10 x 100ms
Time between frames (ms) = 10 ms
c.
Twido PLC Port 1:
Type = No Change
Address = 1 (Should be same as the HMI)
HMI Vijeo Designer
IO Manager, selected:
a.
Manufacturer = Schneider Electric Industries SAS
Driver = Modbus (RTU)
COM Port = COM1
Serial Interface = no change
Flow Control = no change
Transmission Speed = 19200
Parity Bit = None
Stop Bit = 1
b.
Equipment Configuration = Modbus Equipment
Slave Equipment Address = 1
Comm. Optimization = Custom, 120 bytes
IEC61131 Syntax = "Check"
Addressing Mode = 0-based (Default)
Variables = Double Word word order (Low word first), ASCII Display byte order (Low byte first)
Cable Connection, RS-485
HMI [COM 1, RJ45], Twido MiniDIN 8 [PORT 1]
HMI [4] --------------------- [1] MiniDIN (+)
HMI [5] --------------------- [2] MiniDIN (-)
BR
Herewith the configuration of Both..
PLC TWDLCAA10DRF
1. Using Twido Suite, at the Describe Toolbar, put by drag and drop PLC (Base->Compact->TWDLCAA10DRF) and HMI (Network Elements->Modbus Elements->Magelis)
2. Connected point to point PLC and Network Element
3. Configuration setting:
a.
Network Elements
Name = any
Type = Modbus
Address = Master
b.
Network
Type = No Change
Name = any
Baudrate = 19200
Data Bits = 8 (RTU)
Parity = none
Stop Bit = 1
Timeout = 10 x 100ms
Time between frames (ms) = 10 ms
c.
Twido PLC Port 1:
Type = No Change
Address = 1 (Should be same as the HMI)
HMI Vijeo Designer
IO Manager, selected:
a.
Manufacturer = Schneider Electric Industries SAS
Driver = Modbus (RTU)
COM Port = COM1
Serial Interface = no change
Flow Control = no change
Transmission Speed = 19200
Parity Bit = None
Stop Bit = 1
b.
Equipment Configuration = Modbus Equipment
Slave Equipment Address = 1
Comm. Optimization = Custom, 120 bytes
IEC61131 Syntax = "Check"
Addressing Mode = 0-based (Default)
Variables = Double Word word order (Low word first), ASCII Display byte order (Low byte first)
Cable Connection, RS-485
HMI [COM 1, RJ45], Twido MiniDIN 8 [PORT 1]
HMI [4] --------------------- [1] MiniDIN (+)
HMI [5] --------------------- [2] MiniDIN (-)
BR