I need to set constant frequency preset value for manual mode (LI3 switch) - about 41.5 Hz.
Altivar will work in 2 modes: manual mode (LI3 on) without HMI panel and PLC auto mode (LI3 off) with control from PLC S7-300
Also there are 2 buttons: LI1-Stop button (NC contact) and LI2 - Start button (NO contact).
Separate mode is enabled.
Control 1 - comm. card (profibus)
Task 1 - comm. card (profibus)
Control 2 - terminal block (start and stop at the control panel)
In SET boundary frequency are 5 Hz and 48.5 Hz
I tried to set different options in Task 2, but by start button in local mode(LI3 on) motor runs at lower frequency - 5 Hz.
How should i set task 2 to the Start button in order to work in the local mode, the motor runs at a set speed, for example 41.5 Hz without PLC?
Where can i set this speed?
Thanks in advance.
Доброго времени суток. Может ли кто-нибудь помочь с настройкой altivar 61?
Суть такова: частотник работает в двух режимах - управление с плк (LI3 в '1') и в местном режиме (LI3 в '0'). Пуск в местном режиме - (LI1 НЗ контакт), стоп в местном режиме (LI2 НО контакт)
Включен раздельный режим:
управление 1 - комм. карта (profibus)
задание 1 - комм. карта (profibus)
управление 2 - клеммник
нижняя и верхняя частота - 5 Гц и 48.5 Гц.
Были испробованы различные варианты настройки задания 2, но в местном режиме привод либо крутится на нижней частоте 5 Гц, либо на максимальноq в 48.5 Гц. Как нужно настроить задание 2 или другие настройки чтобы в местном режиме частотник работал на некоторой заданной частоте, например, 41.5 Гц?
Заранее благодарю