Good day!
i have adapter LPT to rs232 and cable rs232/ppi.
i use this for connect to siemens simatic panel 177dp.
Can i use this cable to connect to controller s7-300/400?
[?]: LPT//rs232<>rs232/ppi for connection to S7-300/400
-
- Posts: 14
- Joined: Wed Oct 06, 2010 1:17 pm
-
- Posts: 24
- Joined: Tue Jan 31, 2012 8:14 am
Re: [?]: LPT//rs232<>rs232/ppi for connection to S7-300/400
Dear,
S7-300 and S7-400 series uses MPI or Profibus for communication on MPI/DP port. So Rs-232 to MPI cable should work not PPI.
Thanks
S7-300 and S7-400 series uses MPI or Profibus for communication on MPI/DP port. So Rs-232 to MPI cable should work not PPI.
Thanks