RSLINX 1747-PIC driver problem

RSLinx, RSLogix, RSView, LogixPro ...
hmohamed
Posts: 147
Joined: Sun Oct 18, 2009 8:19 am

RSLINX 1747-PIC driver problem

Post by hmohamed »

Hi Experts

i am using windows xp SP3 and installed RSLINX 2.54.00.11 CPR 9 SR1 and when i try to choose driver 1747-PIC a message with Fetal error appears and i can not swap this driver to Run Mode do any body has any solution or face this problem before

thanx in advance
mohdabshr
Posts: 180
Joined: Sat Jul 23, 2011 2:02 pm

Re: RSLINX 1747-PIC driver problem

Post by mohdabshr »

Dear
I face same problem, it is only occurred when your OS is XPsp3 if you change to OS XPsp2 it will work and other solution is to search in Google for AB PIC SP3Fix.
NowanH
Posts: 80
Joined: Wed Apr 30, 2014 6:16 pm

Re: RSLINX 1747-PIC driver problem

Post by NowanH »

This is a procedure I found. Not sure if it works.


1. Obtain "serenum.sys" from XP sp2. It lives in C:\Windows\System32\Drivers and can be identified from it's file version (it will be file version 5.1.2600.2280).
2. Back up your existing "serenum.sys" under sp3 (it will be file version 5.1.2600.55.12).
3. In RsLinx, delete any instance of drivers which use the serial port. Preferably, don't have RsLinx configured as a service.
4. Reboot your PC into safe mode.
5. Using explorer, locate the xp2 file version of "serenum.sys" and copy it.
6. Browse to C:\Windows\System32\Drivers ans paste the copied file overwriting the sp3 file.
7. Reboot your PC into normal mode.
8. Before doing anything else, run RsLinx.
9. Add the 147-PIC /AIC+ driver - make sure you tick the checkbox 'Reserve COM Port for Exclusive use by this driver'.
10. The new driver should be listed in Configured Drivers list as 'Running'. If not, repeat the procedure from step 3.

Note: While the sp2 driver is installed you will not be able to use the port as a standard COM port
hmohamed
Posts: 147
Joined: Sun Oct 18, 2009 8:19 am

Re: RSLINX 1747-PIC driver problem

Post by hmohamed »

Dear Friends,Mohdabshr,Badassplc,NowanH

thank you for reply i will follow your suggestions and give you my feedbacks
hmohamed
Posts: 147
Joined: Sun Oct 18, 2009 8:19 am

Re: RSLINX 1747-PIC driver problem

Post by hmohamed »

Dear Friends
it works and problem solved
thank you
keremsafa
Posts: 1
Joined: Sat Apr 17, 2021 5:52 am

Re: RSLINX 1747-PIC driver problem

Post by keremsafa »

NowanH wrote: Fri Jan 30, 2015 3:08 pm This is a procedure I found. Not sure if it works.


1. Obtain "serenum.sys" from XP sp2. It lives in C:\Windows\System32\Drivers and can be identified from it's file version (it will be file version 5.1.2600.2280).
2. Back up your existing "serenum.sys" under sp3 (it will be file version 5.1.2600.55.12).
3. In RsLinx, delete any instance of drivers which use the serial port. Preferably, don't have RsLinx configured as a service.
4. Reboot your PC into safe mode.
5. Using explorer, locate the xp2 file version of "serenum.sys" and copy it.
6. Browse to C:\Windows\System32\Drivers ans paste the copied file overwriting the sp3 file.
7. Reboot your PC into normal mode.
8. Before doing anything else, run RsLinx.
9. Add the 147-PIC /AIC+ driver - make sure you tick the checkbox 'Reserve COM Port for Exclusive use by this driver'.
10. The new driver should be listed in Configured Drivers list as 'Running'. If not, repeat the procedure from step 3.

Note: While the sp2 driver is installed you will not be able to use the port as a standard COM port
Thank you NowanH
I solved my problem. i copied serenum.sys to Windows 7 and its working. U need real pyhsical Com Port guys. Not Converter.